    Why did wind sensor canot received the data via modbus serial port.
    26 Posts 4 Posters 24.4k Views 1 Watching
    • E Offline
      edmond
      yes.I am sure now the wind sensor mode is modbus mode. and I can received the data from modbus scan software. But mango is not ok.
      • jeremyhJ Offline
        jeremyh
        Show me where you are receiving the modbus data over serial using Modscan?
        @jeremyh said:
        @edmond said:
        and can received data use modscan32 software.
        Modscan doesn't receive any data..
        Your equipment is not set up correctly
        • E Offline
          edmond
          as show in the attachment . I use other device via modbus ip to received data .
          and display mango and modbus scan software as below.
          • E Offline
            edmond
            now I modify the connection to rs 485 .
            and I test again
            display "argument type mismatch"
            many data 32 bit float.and mango have no this option.
            • jeremyhJ Offline
              jeremyh
              32 bit = 4 byte
              and I test again
              What did you expect? That your RS232 adapter would turn into a RS485 adapter? :shock:
              • E Offline
                edmond
                in wind sensor side ,have two type:rs422 or rs485,
                before the connection always is rs 422, and I change a adapter to rs485 to test to see have any changing.
                • E Offline
                  edmond
                  and I test serval times.
                  and display"Exception from modbus master:CRC mismatch:given=1536,calc=8432"
                  • hussamH Offline
                    hussam
                    as your attachment, the modscan32 don't receive any value?don't you know what's mean valid slave responses:0?
                    • E Offline
                      edmond
                      if in mango,
                      What do this mean "nd I test serval times.
                        This means that you got a response but the CRC did not match so the message was discarded.
                        A CRC of 1536 was given but the calculated CRC was 8432. This indicated that the message might have been corrupted.
                        If you don't know what a CRC is then you should do some research on the Modbus spec and will probably clear that up.
                        • E Offline
                          edmond
                          yes,I change to wind sensor adapter from rs 422 to rs485 adapter,and display above the message."exception from modbus master:CRC mismatch:given=1536,calc=8432"
                          • E Offline
                            edmond
                            How to setting can display normal value.
                            will not display"Exception from modbus master:CRC mismatch:given=1536,calc=8432"
                            BR
                              I don't think that's a question that anyone here can answer. It could be noise on your network or something else.