Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
Why did wind sensor canot received the data via modbus serial port.
-
In one of your other threads (good luck finding it) I pointed out that you need to actually change the weather station to Modbus mode before you can read data using Modbus. Have you definitely done that?
-
yes.I am sure now the wind sensor mode is modbus mode. and I can received the data from modbus scan software. But mango is not ok.
-
@edmond said:
I can received the data from modbus scan software. But mango is not ok.
Show me where you are receiving the modbus data over serial using Modscan?
@jeremyh said:
@edmond said:
and can received data use modscan32 software.
Modscan doesn't receive any data..
Your equipment is not set up correctly -
as show in the attachment . I use other device via modbus ip to received data .
and display mango and modbus scan software as below.
Attachment: download link
-
now I modify the connection to rs 485 .
and I test againdisplay "argument type mismatch"
many data 32 bit float.and mango have no this option.
Attachment: download link
-
-
in wind sensor side ,have two type:rs422 or rs485,
before the connection always is rs 422, and I change a adapter to rs485 to test to see have any changing.
-
and I test serval times.
and display"Exception from modbus master:CRC mismatch:given=1536,calc=8432"
Attachment: download link
-
as your attachment, the modscan32 don't receive any value?don't you know what's mean valid slave responses:0?
-
if in mango,
What do this mean "nd I test serval times.and display"Exception from modbus master:CRC mismatch:given=1536,calc=8432"
" -
This means that you got a response but the CRC did not match so the message was discarded.
A CRC of 1536 was given but the calculated CRC was 8432. This indicated that the message might have been corrupted.
If you don't know what a CRC is then you should do some research on the Modbus spec and will probably clear that up.
Joel.
-
yes,I change to wind sensor adapter from rs 422 to rs485 adapter,and display above the message."exception from modbus master:CRC mismatch:given=1536,calc=8432"
-
How to setting can display normal value.
will not display"Exception from modbus master:CRC mismatch:given=1536,calc=8432"
BR
Attachment: download link
-
I don't think that's a question that anyone here can answer. It could be noise on your network or something else.
Joel.