    Mango Persistent TCP publisher constantly resets connection
    26 Posts 5 Posters 15.4k Views 4 Watching
      MaP
      Hi Guys,
      Thanks for the speedy replies - much appreciated. I have disabled the publisher while i try to solve the issue as i don't want to clog up the events.
      I have attached some screenshots.
      0_1477463177407_upload-4e947aa6-1513-46f2-beeb-18c7c1566043
      0_1477463318283_upload-c75ebb97-333e-4c10-bc3c-85f79e92159f
        @mihairosu Right you are. I have made an issue for this; https://github.com/infiniteautomation/ma-core-public/issues/855
        @MaP Can you give us a description of what happens when you enable it? If you press the "Get Status" button every few seconds after enabling it, do you see it finish connecting the points? Judging from the image in your first post, where the connection is resetting every three seconds, I am guessing Terry's suggestion is pretty good: it could be an issue with the point configurations.
        Consider changing the XID prefix and seeing if you get new points created on the receiver. If so, it could be a problem with the configuration of a point, as Terry suggested.
        If the points do finish connecting and begin to publish or sync, then the connection resets, I would consider trying to turn down the point values to send per packet.
          MaP
          No points have been created by the receiver when you press get status it says 0 points, connected for 284ms, 1 packet received, 0 timeouts if you press get status a second time it will say no connection. It toggles between these two states..
          No points have been created by the receiver at all yet just lots of connection reset errors on the sending side and the data points tab on the receiver side are blank.
            Is it possible you have two different versions of the module? Regardless from your screen shot I can see you have an older version so I would recommend doing an update.
              MaP
              I have upgraded the local mango to the latest persistent module but we still see the same connection reset behavior.
                MaP
                I enabled the Debug log for a while and received the following logs (only put about a third here):
                INFO 2016-10-27 15:00:50,050 (com.serotonin.m2m2.persistent.pub.PersistentSenderRT.initialize:228) - Initializing
                INFO 2016-10-27 15:00:50,101 (com.serotonin.m2m2.persistent.pub.PersistentSenderRT.initialize:242) - Initialized
                WARN 2016-10-27 15:00:51,127 (com.serotonin.m2m2.persistent.pub.PersistentSendThread.runImpl:182) - Connection reset
                java.net.SocketException: Connection reset
                at java.net.SocketInputStream.read(SocketInputStream.java:189)
                at java.net.SocketInputStream.read(SocketInputStream.java:121)
                at java.net.SocketInputStream.read(SocketInputStream.java:203)
                at com.serotonin.m2m2.persistent.common.Packet.readPacket(Packet.java:93)
                at com.serotonin.m2m2.persistent.pub.PersistentSendThread.getPointReceipt(PersistentSendThread.java:617)
                at com.serotonin.m2m2.persistent.pub.PersistentSendThread.openConnection(PersistentSendThread.java:599)
                at com.serotonin.m2m2.persistent.pub.PersistentSendThread.runImpl(PersistentSendThread.java:179)
                at com.serotonin.m2m2.rt.publish.SendThread.run(SendThread.java:56)
                WARN 2016-10-27 15:00:54,074 (com.serotonin.m2m2.persistent.pub.PersistentSendThread.runImpl:182) - Connection reset
                WARN 2016-10-27 15:00:57,354 (com.serotonin.m2m2.persistent.pub.PersistentSendThread.runImpl:182) - Connection reset
                WARN 2016-10-27 15:01:00,324 (com.serotonin.m2m2.persistent.pub.PersistentSendThread.runImpl:182) - Connection reset
                WARN 2016-10-27 15:01:03,604 (com.serotonin.m2m2.persistent.pub.PersistentSendThread.runImpl:182) - Connection reset
                WARN 2016-10-27 15:01:06,564 (com.serotonin.m2m2.persistent.pub.PersistentSendThread.runImpl:182) - Connection reset
                Any assistance would be appreciated.
                  Is this to imply there was no debug output on the receiver's end? You can set the level even lower, at Trace. When I asked about the status button, I was wondering about from the Publisher's side as well.
                  I would try to assess whether it was a configuration issue or a network issue. To do that I would export your Publisher's configuration, remove all the items in the "points" list, change the host to localhost and import it on your receiver's Mango. Create some virtual points, and see if you can publish them to the localhost receiver. If so, and both Mangos are running on the same versions of the module, you can be sure it's a network problem.
                  Another thought is to remove the data points from the publisher, and see if the connection is stable.
                    MaP
                    I have some screenshots of the receiver side Trace Logs here:
                    Constraint A foreign key constrant fails - DataSourceId References DataSources_Old
                    Any ideas how to solve this?
                    0_1477626888402_upload-450be2da-545a-47d8-ae31-a4216716418d
                    0_1477626900084_upload-6ffb83db-fe75-41dd-8337-bfd20036dd14
                      MaP
                      This post is deleted!
                        MaP
                        Also encountering the below error while trying to construct a new publisher using only mango data source points like CPU temp.
                        The published data points section just hangs with a loading image after seeing this error
                        0_1477627920182_upload-49e1e9c1-9632-4377-8e3f-7aaf24e4253b
                          dataSources_old? You were playing around in your database schema! I assume you created a table dataSources_new like dataSources, then renamed dataSources to dataSources_old and moved dataSources_new to dataSources. Is there a reason you would try this?
                          If there isn't data that matters, I would fix it by exporting your configuration, going into the mysql command line, creating a database "mango2" and redirecting the connection string in your env.properties to this new database, and then importing your configuration again after Mango boots.
                          If there is data that matters, you can update the foreign key constraints to reference the right table (grumble grumble) by running some SQL:
                          ALTER TABLE dataPoints DROP FOREIGN KEY dataPointsFk1;
                          ALTER TABLE dataPoints ADD CONSTRAINT dataPointsFk1 FOREIGN KEY (dataSourceId) REFERENCES dataSources(id);
                            MaP
                            Hi Phil,
                            I just imported another sites data sources config into the mango and did a find replace to ensure unique XIDs. I was pretty sure this was a brand-new mango but I cant be sure that it hasnt been toyed with.
                            Is there a way to do a factory reset and clear all previous data/config from a mango?
                              MaP
                              Hi Phil,
                              I entered the SQL queries listed in your last post and received the following errors:
                              0_1477887143953_upload-96a5675c-75e6-4842-b086-afb6f1c0c9b5
                                MaP
                                0_1477893574186_upload-b2dd7f5b-b362-4810-bbd4-fb23d33e5c86
                                  That's okay, the foreign key was the bigger problem. I'm going to remove the index recommendation from that post. But, it also looks like you're using the H2 web console now, but from your SQL error I think you're using MySQL? If so, running those commands in the H2 console won't help, you would have to run them in your MySQL database.
                                  Using H2, you can cause a new Mango instance by renaming your Mango/databases directory while Mango is off. if using MySQL, you should create another database via CREATE DATABASE newMangoDatabaseName and then modify the connection string to point to this database. You would also need to rename the Mango/databases directory to set the old data aside, if you are using the NoSQL module.
                                    MaP
                                    0_1477982343865_upload-3db30b84-56f7-49c9-b436-daffa43837ce
                                    Do you mean using the inbuilt SQL console on the Mango web interface to try the queries in the previous post?
                                    0_1477982415138_upload-e76d2fba-dc92-4922-85a5-98e90ae41e3c
                                      The error you posted relating to dataSources_old is a com.mysql.jdbc.exceptions.jdbc4.MySQLIntegrityConstraintViolationException so I'm pretty certain you were using MySQL. Is there a chance you overwrote your env.properties file?
                                        MaP
                                        I dont think so -
                                        #    Copyright (C) 2014 Infinite Automation Systems Inc. All rights reserved.
                                        #    @author Matthew Lohbihler
                                        # TO OVERRIDE VALUES IN THIS FILE...
                                        # Do not change the values in this file, because when you upgrade your core
                                        # your changes will be overwritten. Instead, create a new file called
                                        # <MA_HOME>/overrides/properties/env.properties and override properties
                                        # there. The overrides directory will never be overwritten by an upgrade, so
                                        # your customizations will be safe.
                                        # The port at which Mango Automation will listen for browser connections
                                        web.port=80
                                        # The host interface to which Mango Automation will bind and listen for new connections
                                        #  0.0.0.0 is the special interface that will force a bind to all available interfaces
                                        web.host=0.0.0.0
                                        # Should Mango Automation open (if possible) a browser window when it starts up?
                                        web.openBrowserOnStartup=true
                                        # Default database settings, NOTE that on windows this must be an absolute path
                                        db.type=h2
                                        db.url=jdbc:h2:${ma.home}/databases/mah2
                                        db.location=${ma.home}/databases/mah2
                                        db.port=8081
                                        db.username=
                                        db.password=
                                        #For web console
                                        db.web.start=false
                                        db.web.port=8091
                                        #db.type=derby
                                        #db.url=${ma.home}/databases/madb
                                        #db.username=
                                        #db.password=
                                        #General Database Settings
                                        db.pool.maxActive=100
                                        db.pool.maxIdle=10
                                        db.update.log.dir=${ma.home}/logs/
                                        # setting to show query times in the logs as INFO
                                        db.useMetrics=false
                                        # MySQL database settings. Your MySQL instance must already be running and configured before this can be used.
                                        #db.type=mysql
                                        #db.url=jdbc:mysql://localhost/<your mysql schema name>
                                        #db.username=<your mysql username>
                                        #db.password=<your mysql password>
                                        # Database settings for conversion. If the db.* settings point to a new database instance, and the convert type setting
                                        # is set, Mango Automation will attempt to convert from the convert.db.* settings to the db.* settings
                                        # Note that database conversions should not be performed in the same step as an upgrade. First upgrade, then convert.
                                        convert.db.type=
                                        convert.db.url=${convert.db.url}
                                        convert.db.username=${convert.db.username}
                                        convert.db.password=${convert.db.password}
                                        # The location of the Mango Automation store from which to get license files.
                                        store.url=http://store.infiniteautomation.com
                                        # SSL control
                                        ssl.on=false
                                        ssl.port=8443
                                        ssl.keystore.location=/location/to/keystore/file.jks
                                        ssl.keystore.password=freetextpassword
                                        # System time zone. Leave blank to use default VM time zone.
                                        timezone=
                                        #Rest API Configuration
                                        rest.enabled=true
                                        #For using other than timestamp
                                        rest.customDateOutputFormat=YYYY-MM-dd HH:mm:ss.SSS Z
                                        rest.customDateInputFormat=YYYY-MM-dd HH:mm:ss.SSS Z
                                        #For rest API Documentation at /swagger/index.html
                                        swagger.enabled=false
                                        swagger.mangoApiVersion=v1
                                        #Distributor Settings
                                        distributor=IA
                                        #Jetty Thread Pool Tuning
                                        web.threads.msIdleTimeout=10000
                                        web.threads.minimum=10
                                        web.threads.maximum=200
                                        web.websocket.pingTimeoutMs=10000
                                        #Jetty JSP Configuration
                                        # See here for options: http://www.eclipse.org/jetty/documentation/9.2.10.v20150310/configuring-jsp.html
                                        web.jsp.development=true
                                        web.jsp.genStringsAsCharArray=true
                                        web.jsp.trimSpaces=false
                                        web.jsp.classdebuginfo=false
                                        web.jsp.supressSmap=true
                                        web.jsp.compilerClassName=org.apache.jasper.compiler.JDTCompiler
                                        web.jsp.compiler=modern
                                        web.jsp.fork=false
                                        web.jsp.keepgenerated=true
                                        #Regex used to match serial ports so they show up in the menu
                                        serial.port.linux.regex=((ttymUSB)[0-9]{1,3}|rs(485)-[0-9])
                                        serial.port.linux.path=/dev/
                                        serial.port.windows.regex=
                                        serial.port.windows.path=
                                        serial.port.osx.path=/dev/
                                        serial.port.osx.regex=(cu|tty)..*
                                          MaP
                                          The persistent TCP receiver is using MySQL while the local mango is using H2 i believe. Will this cause the issue?
                                            No, the TCP receiver will be using the database of the instance it is running on, and the database of the receiver and the publisher do not need to be the same. Have you been re-evaluating if your problem was solved? We have covered multiple paths to resolution, for each database.
                                            If your receiver is the one with the SQL error, and it is on MySQL, that is where i was advising to fix the foreign key problem.