    No restart flag found, not restarting MA
    10 Posts 3 Posters 1.8k Views 3 Watching
      PSpivey
      Hi Guys,
      Having a bit of trouble with a mango of mine at a remote site. Noticed the web server wasn't working so i ssh'd into it to restart it but i keep on getting an error when i attempt to do that.
      I have tried rebooting the mango and clearing space on it which didn't work and can't quite think of anything else to try. Any help would be appreciated.
      Thank you!
        What version of Mango are you trying to start. That error looks like a hardware/os problem but knowing the version will help us find the right version of the startup script and from that the command on line 142.
          PSpivey
          I believe it's a V3 mango. I don't know what version of the core is being used. Is there a way to find out that from the back end?
            Look at the name of the mango-[version].jar file in MA_HOME/lib. All recent versions of Mango include the version in that filename.
              I took a look at the source for ma-start.sh and it looks like it is trying to execute one of your extension from MA_HOME/bin/ext-enabled
              Perhaps that folder is missing, or has a corrupt file in it?
                PSpivey
                The MangoES is using core version 2.7.10 according to MA_HOME/lib.
                The folder MA_HOME/bin/ext-enabled is not missing and contains one script posted below.
                Any help?
                  can you paste your ma.log file and ma-script.log files here in a code element after you have tried to restart it.
                  Also, can you make sure that your memory-small,sh is executable?
                    PSpivey
                    It seems like my memory-small.sh is executable, didn't come up with a error at least when i tried to execute it.
                    Below is my ma-script.log
                    Fri Feb 5 15:53:54 UTC 2016 ma-start: running init extensions...
                    Fri Feb 5 15:53:54 UTC 2016 ma-start: running start extensions...
                    Fri Feb 5 15:53:54 UTC 2016 ma-start: starting MA
                    Fri Feb 5 15:53:54 UTC 2016 ma-start: MA started with Process ID 523
                    Fri Feb 5 18:15:14 UTC 2016 ma-start: running stop extensions...
                    Fri Feb 5 18:15:14 UTC 2016 ma.stop: stop initiated...
                    Fri Feb 5 18:15:22 UTC 2016 ma-start: MA explicitly stopped. Exiting restart loop
                    Fri Feb 5 18:15:22 UTC 2016 ma-start: MA done
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: running init extensions...
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: running start extensions...
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: starting MA
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 520
                    Mon Feb 8 22:18:34 UTC 2016 ma-start: running stop extensions...
                    Mon Feb 8 22:18:34 UTC 2016 ma.stop: stop initiated...
                    Tue Jan 1 00:08:54 UTC 2013 ma-start: running init extensions...
                    Tue Jan 1 00:08:54 UTC 2013 ma-start: running start extensions...
                    Tue Jan 1 00:08:54 UTC 2013 ma-start: MA removing pid file for dead pid: 520
                    Tue Jan 1 00:08:54 UTC 2013 ma-start: starting MA
                    Tue Jan 1 00:08:54 UTC 2013 ma-start: MA started with Process ID 534
                    Tue Jan 1 00:00:08 UTC 2013 ma-start: running init extensions...
                    Tue Jan 1 00:00:08 UTC 2013 ma-start: running start extensions...
                    Tue Jan 1 00:00:08 UTC 2013 ma-start: MA removing pid file for dead pid: 534
                    Tue Jan 1 00:00:08 UTC 2013 ma-start: starting MA
                    Tue Jan 1 00:00:08 UTC 2013 ma-start: MA started with Process ID 533
                    Mon Feb 22 21:11:55 UTC 2016 ma-start: running stop extensions...
                    Mon Feb 22 21:11:55 UTC 2016 ma.stop: stop initiated...
                    Mon Feb 22 21:12:05 UTC 2016 ma-start: MA explicitly stopped. Exiting restart loop
                    Mon Feb 22 21:12:05 UTC 2016 ma-start: MA done
                    Mon Feb 22 21:15:07 UTC 2016 ma-start: running init extensions...
                    Mon Feb 22 21:15:07 UTC 2016 ma-start: upgrading core...
                    Mon Feb 22 21:15:25 UTC 2016 ma-start: running init extensions...
                    Mon Feb 22 21:15:25 UTC 2016 ma-start: running start extensions...
                    Mon Feb 22 21:15:25 UTC 2016 ma-start: starting MA
                    Mon Feb 22 21:15:25 UTC 2016 ma-start: MA started with Process ID 3097
                    Mon Feb 22 21:18:27 UTC 2016 ma-restart: restart initiated...
                    Mon Feb 22 21:18:37 UTC 2016 ma-start: running restart extentions
                    Mon Feb 22 21:18:37 UTC 2016 ma-start: running start extensions...
                    Mon Feb 22 21:18:37 UTC 2016 ma-start: starting MA
                    Mon Feb 22 21:18:37 UTC 2016 ma-start: MA started with Process ID 4503
                    Mon Feb 22 21:20:51 UTC 2016 ma-start: running stop extensions...
                    Mon Feb 22 21:20:51 UTC 2016 ma.stop: stop initiated...
                    Mon Feb 22 21:21:02 UTC 2016 ma-start: MA explicitly stopped. Exiting restart loop
                    Mon Feb 22 21:21:02 UTC 2016 ma-start: MA done
                    Mon Feb 22 21:21:22 UTC 2016 ma-start: running stop extensions...
                    Mon Feb 22 21:21:22 UTC 2016 ma.stop: No PID file found. Java process not stopped...
                    Tue Mar 22 17:47:19 UTC 2016 ma-start: running init extensions...
                    Tue Mar 22 17:47:19 UTC 2016 ma-start: running start extensions...
                    Tue Mar 22 17:47:19 UTC 2016 ma-start: starting MA
                    Tue Mar 22 17:47:19 UTC 2016 ma-start: MA started with Process ID 516
                    Tue Mar 22 17:57:21 UTC 2016 ma-start: running restart extentions
                    Tue Mar 22 17:57:21 UTC 2016 ma-start: upgrading core...
                    Tue Mar 22 17:57:41 UTC 2016 ma-start: running init extensions...
                    Tue Mar 22 17:57:41 UTC 2016 ma-start: running start extensions...
                    Tue Mar 22 17:57:41 UTC 2016 ma-start: starting MA
                    Tue Mar 22 17:57:41 UTC 2016 ma-start: MA started with Process ID 5160
                    Tue Mar 22 17:58:39 UTC 2016 ma-start: running stop extensions...
                    Tue Mar 22 17:58:39 UTC 2016 ma.stop: stop initiated...
                    Tue Mar 22 17:58:48 UTC 2016 ma-start: MA explicitly stopped. Exiting restart loop
                    Tue Mar 22 17:58:48 UTC 2016 ma-start: MA done
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 532
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: MA removing pid file for dead pid:
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 541
                    Wed Mar 30 20:44:13 UTC 2016 ma-start: running restart extentions
                    Wed Mar 30 20:44:13 UTC 2016 ma-start: running start extensions...
                    Wed Mar 30 20:44:13 UTC 2016 ma-start: starting MA
                    Wed Mar 30 20:44:13 UTC 2016 ma-start: MA started with Process ID 2108
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: MA removing pid file for dead pid: 2108
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 556
                    Tue Jan 1 00:00:08 UTC 2013 ma-start: MA removing pid file for dead pid: 556
                    Tue Jan 1 00:00:08 UTC 2013 ma-start: MA started with Process ID 563
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: MA removing pid file for dead pid: 563
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 578
                    Tue Jan 1 00:00:10 UTC 2013 ma-start: running init extensions...
                    Tue Jan 1 00:00:10 UTC 2013 ma-start: running start extensions...
                    Tue Jan 1 00:00:10 UTC 2013 ma-start: MA removing pid file for dead pid: 578
                    Tue Jan 1 00:00:10 UTC 2013 ma-start: starting MA
                    Tue Jan 1 00:00:10 UTC 2013 ma-start: MA started with Process ID 560
                    Tue Jan 1 00:00:08 UTC 2013 ma-start: MA removing pid file for dead pid: 560
                    Tue Jan 1 00:00:08 UTC 2013 ma-start: MA started with Process ID 565
                    Tue Jan 1 00:00:08 UTC 2013 ma-start: MA removing pid file for dead pid: 565
                    Tue Jan 1 00:00:08 UTC 2013 ma-start: MA started with Process ID 562
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: MA removing pid file for dead pid: 562
                    Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 620
                    Mon May 30 02:18:04 UTC 2016 ma-start: no restart flag found, not restarting MA
                    Mon May 30 02:18:04 UTC 2016 ma-start: MA done
                    Mon May 30 02:25:01 UTC 2016 ma-start: running stop extensions...
                    Mon May 30 02:25:01 UTC 2016 ma.stop: No PID file found. Java process not stopped...
                    Mon May 30 02:25:27 UTC 2016 ma-start: running init extensions...
                    Mon May 30 02:25:27 UTC 2016 ma-start: running start extensions...
                    Mon May 30 02:25:27 UTC 2016 ma-start: starting MA
                    Mon May 30 02:25:27 UTC 2016 ma-start: MA started with Process ID 576
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions...
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions...
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 576
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 606
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 606
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 612
                    Tue Jan 1 08:00:08 AWST 2013 ma-start: running init extensions...
                    Tue Jan 1 08:00:08 AWST 2013 ma-start: running start extensions...
                    Tue Jan 1 08:00:08 AWST 2013 ma-start: MA removing pid file for dead pid: 612
                    Tue Jan 1 08:00:08 AWST 2013 ma-start: starting MA
                    Tue Jan 1 08:00:08 AWST 2013 ma-start: MA started with Process ID 605
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: running init extensions...
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: running start extensions...
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 605
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: starting MA
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 601
                    Tue Jan 1 08:00:08 AWST 2013 ma-start: MA removing pid file for dead pid: 601
                    Tue Jan 1 08:00:08 AWST 2013 ma-start: MA started with Process ID 600
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 600
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 601
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 601
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 614
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 614
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 610
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 610
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 601
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 605
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 605
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 611
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 611
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 605
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 596
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 596
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 603
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 603
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 622
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 622
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 613
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 613
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 598
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 598
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 602
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 602
                    Tue Jan 1 08:00:08 AWST 2013 ma-start: MA started with Process ID 617
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 617
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 607
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 607
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 599
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 599
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 612
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 603
                    Fri Jun 23 13:06:14 AWST 2017 ma-start: running restart extentions
                    Fri Jun 23 13:06:14 AWST 2017 ma-start: running start extensions...
                    Fri Jun 23 13:06:14 AWST 2017 ma-start: starting MA
                    Fri Jun 23 13:06:14 AWST 2017 ma-start: MA started with Process ID 11320
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 11320
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 600
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 609
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 595
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 595
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 609
                    Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 609
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 598
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 620
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 620
                    Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 599
                    Tue Jan 29 16:03:42 AWST 2019 ma-start: running stop extensions...
                    Tue Jan 29 16:03:42 AWST 2019 ma.stop: stop initiated...
                    Tue Jan 29 16:03:48 AWST 2019 ma-start: MA explicitly stopped. Exiting restart loop
                    Tue Jan 29 16:03:48 AWST 2019 ma-start: MA done
                    Tue Jan 29 16:03:49 AWST 2019 ma-start: running init extensions...
                    Tue Jan 29 16:03:49 AWST 2019 ma-start: running start extensions...
                    Tue Jan 29 16:03:49 AWST 2019 ma-start: starting MA
                    Tue Jan 29 16:03:49 AWST 2019 ma-start: MA started with Process ID 6735
                    Tue Jan 1 08:00:11 AWST 2013 ma-start: running init extensions...
                    Tue Jan 1 08:00:11 AWST 2013 ma-start: running start extensions...
                    Tue Jan 1 08:00:11 AWST 2013 ma-start: MA removing pid file for dead pid: 6735
                    Tue Jan 1 08:00:11 AWST 2013 ma-start: starting MA
                    Tue Jan 1 08:00:11 AWST 2013 ma-start: MA started with Process ID 605
                    Tue Jan 1 08:00:15 AWST 2013 ma-start: no restart flag found, not restarting MA
                    Tue Jan 1 08:00:15 AWST 2013 ma-start: MA done
                    Fri May 10 10:35:19 AWST 2019 ma-start: running init extensions...
                    Fri May 10 10:35:19 AWST 2019 ma-start: running start extensions...
                    Fri May 10 10:35:19 AWST 2019 ma-start: starting MA
                    Fri May 10 10:35:19 AWST 2019 ma-start: MA started with Process ID 1945
                    Fri May 10 10:35:22 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 10:35:22 AWST 2019 ma-start: MA done
                    Fri May 10 10:35:49 AWST 2019 ma-start: running stop extensions...
                    Fri May 10 10:35:49 AWST 2019 ma.stop: No PID file found. Java process not stopped...
                    Fri May 10 10:35:55 AWST 2019 ma-start: running init extensions...
                    Fri May 10 10:35:55 AWST 2019 ma-start: running start extensions...
                    Fri May 10 10:35:55 AWST 2019 ma-start: starting MA
                    Fri May 10 10:35:55 AWST 2019 ma-start: MA started with Process ID 2200
                    Fri May 10 10:35:58 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 10:35:58 AWST 2019 ma-start: MA done
                    Fri May 10 10:42:27 AWST 2019 ma-start: running init extensions...
                    Fri May 10 10:42:27 AWST 2019 ma-start: running start extensions...
                    Fri May 10 10:42:27 AWST 2019 ma-start: starting MA
                    Fri May 10 10:42:27 AWST 2019 ma-start: MA started with Process ID 4508
                    Fri May 10 10:42:30 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 10:42:30 AWST 2019 ma-start: MA done
                    Fri May 10 10:42:39 AWST 2019 ma-start: running stop extensions...
                    Fri May 10 10:42:39 AWST 2019 ma.stop: No PID file found. Java process not stopped...
                    Fri May 10 10:43:07 AWST 2019 ma-start: running init extensions...
                    Fri May 10 10:43:07 AWST 2019 ma-start: running start extensions...
                    Fri May 10 10:43:07 AWST 2019 ma-start: starting MA
                    Fri May 10 10:43:07 AWST 2019 ma-start: MA started with Process ID 603
                    Fri May 10 10:43:10 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 10:43:10 AWST 2019 ma-start: MA done
                    Fri May 10 10:44:15 AWST 2019 ma-start: running stop extensions...
                    Fri May 10 10:44:15 AWST 2019 ma.stop: No PID file found. Java process not stopped...
                    Fri May 10 10:44:43 AWST 2019 ma-start: running init extensions...
                    Fri May 10 10:44:43 AWST 2019 ma-start: running start extensions...
                    Fri May 10 10:44:43 AWST 2019 ma-start: starting MA
                    Fri May 10 10:44:43 AWST 2019 ma-start: MA started with Process ID 1624
                    Fri May 10 10:44:46 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 10:44:46 AWST 2019 ma-start: MA done
                    Fri May 10 10:44:58 AWST 2019 ma-start: running init extensions...
                    Fri May 10 10:44:58 AWST 2019 ma-start: running start extensions...
                    Fri May 10 10:44:58 AWST 2019 ma-start: starting MA
                    Fri May 10 10:44:58 AWST 2019 ma-start: MA started with Process ID 1699
                    Fri May 10 10:45:01 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 10:45:01 AWST 2019 ma-start: MA done
                    Fri May 10 10:45:14 AWST 2019 ma-start: running init extensions...
                    Fri May 10 10:45:14 AWST 2019 ma-start: running start extensions...
                    Fri May 10 10:45:14 AWST 2019 ma-start: starting MA
                    Fri May 10 10:45:14 AWST 2019 ma-start: MA started with Process ID 1894
                    Fri May 10 10:45:17 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 10:45:17 AWST 2019 ma-start: MA done
                    Fri May 10 10:45:20 AWST 2019 ma-start: running init extensions...
                    Fri May 10 10:45:20 AWST 2019 ma-start: running start extensions...
                    Fri May 10 10:45:20 AWST 2019 ma-start: starting MA
                    Fri May 10 10:45:20 AWST 2019 ma-start: MA started with Process ID 1945
                    Fri May 10 10:45:23 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 10:45:23 AWST 2019 ma-start: MA done
                    Fri May 10 10:46:27 AWST 2019 ma-start: running init extensions...
                    Fri May 10 10:46:27 AWST 2019 ma-start: running start extensions...
                    Fri May 10 10:46:27 AWST 2019 ma-start: starting MA
                    Fri May 10 10:46:27 AWST 2019 ma-start: MA started with Process ID 2401
                    Fri May 10 10:46:30 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 10:46:30 AWST 2019 ma-start: MA done
                    Fri May 10 10:47:53 AWST 2019 ma-start: running stop extensions...
                    Fri May 10 10:47:53 AWST 2019 ma.stop: No PID file found. Java process not stopped...
                    Fri May 10 10:48:19 AWST 2019 ma-start: running init extensions...
                    Fri May 10 10:48:19 AWST 2019 ma-start: running start extensions...
                    Fri May 10 10:48:19 AWST 2019 ma-start: starting MA
                    Fri May 10 10:48:19 AWST 2019 ma-start: MA started with Process ID 612
                    Fri May 10 10:48:22 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 10:48:22 AWST 2019 ma-start: MA done
                    Fri May 10 10:51:32 AWST 2019 ma-start: running init extensions...
                    Fri May 10 10:51:32 AWST 2019 ma-start: running start extensions...
                    Fri May 10 10:51:32 AWST 2019 ma-start: starting MA
                    Fri May 10 10:51:32 AWST 2019 ma-start: MA started with Process ID 2112
                    Fri May 10 10:51:36 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 10:51:36 AWST 2019 ma-start: MA done
                    Fri May 10 11:55:50 AWST 2019 ma-start: running init extensions...
                    Fri May 10 11:55:50 AWST 2019 ma-start: running start extensions...
                    Fri May 10 11:55:50 AWST 2019 ma-start: starting MA
                    Fri May 10 11:55:50 AWST 2019 ma-start: MA started with Process ID 23778
                    Fri May 10 11:55:53 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Fri May 10 11:55:53 AWST 2019 ma-start: MA done
                    Mon May 13 14:27:20 AWST 2019 ma-start: running init extensions...
                    Mon May 13 14:27:20 AWST 2019 ma-start: running start extensions...
                    Mon May 13 14:27:20 AWST 2019 ma-start: starting MA
                    Mon May 13 14:27:20 AWST 2019 ma-start: MA started with Process ID 18871
                    Mon May 13 14:27:23 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Mon May 13 14:27:23 AWST 2019 ma-start: MA done
                    Mon May 13 16:25:25 AWST 2019 ma-start: running stop extensions...
                    Mon May 13 16:25:25 AWST 2019 ma.stop: No PID file found. Java process not stopped...
                    Mon May 13 16:25:29 AWST 2019 ma-start: running init extensions...
                    Mon May 13 16:25:29 AWST 2019 ma-start: running start extensions...
                    Mon May 13 16:25:29 AWST 2019 ma-start: starting MA
                    Mon May 13 16:25:29 AWST 2019 ma-start: MA started with Process ID 25895
                    Mon May 13 16:25:32 AWST 2019 ma-start: no restart flag found, not restarting MA
                    Mon May 13 16:25:32 AWST 2019 ma-start: MA done
                    My ma.log is very sizable. 1400kB to be exact which makes it too large to put in this post. Did you want me to try and cut it down to a more manageable size?
                      You could mail it to support@infiniteautomation.com
                        In your first post you provided the output from the command line. It looks like you got a 2112 Bus error when it was executing ma-start.sh at line 142. That leads me to believe there is a hardware problem. I thought perhaps the files in the ext-enabled folder were corrupt or on a bad sector of the HD but that is just a guess.