No restart flag found, not restarting MA
Hi Guys,
Having a bit of trouble with a mango of mine at a remote site. Noticed the web server wasn't working so i ssh'd into it to restart it but i keep on getting an error when i attempt to do that.
I have tried rebooting the mango and clearing space on it which didn't work and can't quite think of anything else to try. Any help would be appreciated.
Thank you!
What version of Mango are you trying to start. That error looks like a hardware/os problem but knowing the version will help us find the right version of the startup script and from that the command on line 142.
I believe it's a V3 mango. I don't know what version of the core is being used. Is there a way to find out that from the back end?
Look at the name of the mango-[version].jar file in MA_HOME/lib. All recent versions of Mango include the version in that filename.
I took a look at the source for ma-start.sh and it looks like it is trying to execute one of your extension from MA_HOME/bin/ext-enabled
Perhaps that folder is missing, or has a corrupt file in it?
The MangoES is using core version 2.7.10 according to MA_HOME/lib.
The folder MA_HOME/bin/ext-enabled is not missing and contains one script posted below.
Any help? -
can you paste your ma.log file and ma-script.log files here in a
code
element after you have tried to restart it.Also, can you make sure that your memory-small,sh is executable?
It seems like my memory-small.sh is executable, didn't come up with a error at least when i tried to execute it.
Below is my ma-script.log
Fri Feb 5 15:53:54 UTC 2016 ma-start: running init extensions... Fri Feb 5 15:53:54 UTC 2016 ma-start: running start extensions... Fri Feb 5 15:53:54 UTC 2016 ma-start: starting MA Fri Feb 5 15:53:54 UTC 2016 ma-start: MA started with Process ID 523 Fri Feb 5 18:15:14 UTC 2016 ma-start: running stop extensions... Fri Feb 5 18:15:14 UTC 2016 ma.stop: stop initiated... Fri Feb 5 18:15:22 UTC 2016 ma-start: MA explicitly stopped. Exiting restart loop Fri Feb 5 18:15:22 UTC 2016 ma-start: MA done Tue Jan 1 00:00:09 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: starting MA Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 520 Mon Feb 8 22:18:34 UTC 2016 ma-start: running stop extensions... Mon Feb 8 22:18:34 UTC 2016 ma.stop: stop initiated... Tue Jan 1 00:08:54 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:08:54 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:08:54 UTC 2013 ma-start: MA removing pid file for dead pid: 520 Tue Jan 1 00:08:54 UTC 2013 ma-start: starting MA Tue Jan 1 00:08:54 UTC 2013 ma-start: MA started with Process ID 534 Tue Jan 1 00:00:08 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:00:08 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:00:08 UTC 2013 ma-start: MA removing pid file for dead pid: 534 Tue Jan 1 00:00:08 UTC 2013 ma-start: starting MA Tue Jan 1 00:00:08 UTC 2013 ma-start: MA started with Process ID 533 Mon Feb 22 21:11:55 UTC 2016 ma-start: running stop extensions... Mon Feb 22 21:11:55 UTC 2016 ma.stop: stop initiated... Mon Feb 22 21:12:05 UTC 2016 ma-start: MA explicitly stopped. Exiting restart loop Mon Feb 22 21:12:05 UTC 2016 ma-start: MA done Mon Feb 22 21:15:07 UTC 2016 ma-start: running init extensions... Mon Feb 22 21:15:07 UTC 2016 ma-start: upgrading core... Mon Feb 22 21:15:25 UTC 2016 ma-start: running init extensions... Mon Feb 22 21:15:25 UTC 2016 ma-start: running start extensions... Mon Feb 22 21:15:25 UTC 2016 ma-start: starting MA Mon Feb 22 21:15:25 UTC 2016 ma-start: MA started with Process ID 3097 Mon Feb 22 21:18:27 UTC 2016 ma-restart: restart initiated... Mon Feb 22 21:18:37 UTC 2016 ma-start: running restart extentions Mon Feb 22 21:18:37 UTC 2016 ma-start: running start extensions... Mon Feb 22 21:18:37 UTC 2016 ma-start: starting MA Mon Feb 22 21:18:37 UTC 2016 ma-start: MA started with Process ID 4503 Mon Feb 22 21:20:51 UTC 2016 ma-start: running stop extensions... Mon Feb 22 21:20:51 UTC 2016 ma.stop: stop initiated... Mon Feb 22 21:21:02 UTC 2016 ma-start: MA explicitly stopped. Exiting restart loop Mon Feb 22 21:21:02 UTC 2016 ma-start: MA done Mon Feb 22 21:21:22 UTC 2016 ma-start: running stop extensions... Mon Feb 22 21:21:22 UTC 2016 ma.stop: No PID file found. Java process not stopped... Tue Mar 22 17:47:19 UTC 2016 ma-start: running init extensions... Tue Mar 22 17:47:19 UTC 2016 ma-start: running start extensions... Tue Mar 22 17:47:19 UTC 2016 ma-start: starting MA Tue Mar 22 17:47:19 UTC 2016 ma-start: MA started with Process ID 516 Tue Mar 22 17:57:21 UTC 2016 ma-start: running restart extentions Tue Mar 22 17:57:21 UTC 2016 ma-start: upgrading core... Tue Mar 22 17:57:41 UTC 2016 ma-start: running init extensions... Tue Mar 22 17:57:41 UTC 2016 ma-start: running start extensions... Tue Mar 22 17:57:41 UTC 2016 ma-start: starting MA Tue Mar 22 17:57:41 UTC 2016 ma-start: MA started with Process ID 5160 Tue Mar 22 17:58:39 UTC 2016 ma-start: running stop extensions... Tue Mar 22 17:58:39 UTC 2016 ma.stop: stop initiated... Tue Mar 22 17:58:48 UTC 2016 ma-start: MA explicitly stopped. Exiting restart loop Tue Mar 22 17:58:48 UTC 2016 ma-start: MA done Tue Jan 1 00:00:08 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: starting MA Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 532 Tue Jan 1 00:00:09 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: MA removing pid file for dead pid: Tue Jan 1 00:00:09 UTC 2013 ma-start: starting MA Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 541 Wed Mar 30 20:44:13 UTC 2016 ma-start: running restart extentions Wed Mar 30 20:44:13 UTC 2016 ma-start: running start extensions... Wed Mar 30 20:44:13 UTC 2016 ma-start: starting MA Wed Mar 30 20:44:13 UTC 2016 ma-start: MA started with Process ID 2108 Tue Jan 1 00:00:09 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: MA removing pid file for dead pid: 2108 Tue Jan 1 00:00:09 UTC 2013 ma-start: starting MA Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 556 Tue Jan 1 00:00:08 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:00:08 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:00:08 UTC 2013 ma-start: MA removing pid file for dead pid: 556 Tue Jan 1 00:00:08 UTC 2013 ma-start: starting MA Tue Jan 1 00:00:08 UTC 2013 ma-start: MA started with Process ID 563 Tue Jan 1 00:00:09 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: MA removing pid file for dead pid: 563 Tue Jan 1 00:00:09 UTC 2013 ma-start: starting MA Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 578 Tue Jan 1 00:00:10 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:00:10 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:00:10 UTC 2013 ma-start: MA removing pid file for dead pid: 578 Tue Jan 1 00:00:10 UTC 2013 ma-start: starting MA Tue Jan 1 00:00:10 UTC 2013 ma-start: MA started with Process ID 560 Tue Jan 1 00:00:08 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:00:08 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:00:08 UTC 2013 ma-start: MA removing pid file for dead pid: 560 Tue Jan 1 00:00:08 UTC 2013 ma-start: starting MA Tue Jan 1 00:00:08 UTC 2013 ma-start: MA started with Process ID 565 Tue Jan 1 00:00:08 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:00:08 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:00:08 UTC 2013 ma-start: MA removing pid file for dead pid: 565 Tue Jan 1 00:00:08 UTC 2013 ma-start: starting MA Tue Jan 1 00:00:08 UTC 2013 ma-start: MA started with Process ID 562 Tue Jan 1 00:00:09 UTC 2013 ma-start: running init extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: running start extensions... Tue Jan 1 00:00:09 UTC 2013 ma-start: MA removing pid file for dead pid: 562 Tue Jan 1 00:00:09 UTC 2013 ma-start: starting MA Tue Jan 1 00:00:09 UTC 2013 ma-start: MA started with Process ID 620 Mon May 30 02:18:04 UTC 2016 ma-start: no restart flag found, not restarting MA Mon May 30 02:18:04 UTC 2016 ma-start: MA done Mon May 30 02:25:01 UTC 2016 ma-start: running stop extensions... Mon May 30 02:25:01 UTC 2016 ma.stop: No PID file found. Java process not stopped... Mon May 30 02:25:27 UTC 2016 ma-start: running init extensions... Mon May 30 02:25:27 UTC 2016 ma-start: running start extensions... Mon May 30 02:25:27 UTC 2016 ma-start: starting MA Mon May 30 02:25:27 UTC 2016 ma-start: MA started with Process ID 576 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 576 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 606 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 606 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 612 Tue Jan 1 08:00:08 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:08 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:08 AWST 2013 ma-start: MA removing pid file for dead pid: 612 Tue Jan 1 08:00:08 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:08 AWST 2013 ma-start: MA started with Process ID 605 Tue Jan 1 08:00:10 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 605 Tue Jan 1 08:00:10 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 601 Tue Jan 1 08:00:08 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:08 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:08 AWST 2013 ma-start: MA removing pid file for dead pid: 601 Tue Jan 1 08:00:08 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:08 AWST 2013 ma-start: MA started with Process ID 600 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 600 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 601 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 601 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 614 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 614 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 610 Tue Jan 1 08:00:10 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 610 Tue Jan 1 08:00:10 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 601 Tue Jan 1 08:00:10 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 601 Tue Jan 1 08:00:10 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 605 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 605 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 611 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 611 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 605 Tue Jan 1 08:00:08 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 596 Tue Jan 1 08:00:10 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 596 Tue Jan 1 08:00:10 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 603 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 603 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 622 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 622 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 613 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 613 Tue Jan 1 08:00:10 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 598 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 598 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 602 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 602 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 601 Tue Jan 1 08:00:08 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:08 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:08 AWST 2013 ma-start: MA removing pid file for dead pid: 601 Tue Jan 1 08:00:08 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:08 AWST 2013 ma-start: MA started with Process ID 617 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 617 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 607 Tue Jan 1 08:00:10 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 607 Tue Jan 1 08:00:10 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 599 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 599 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 612 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 612 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 603 Fri Jun 23 13:06:14 AWST 2017 ma-start: running restart extentions Fri Jun 23 13:06:14 AWST 2017 ma-start: running start extensions... Fri Jun 23 13:06:14 AWST 2017 ma-start: starting MA Fri Jun 23 13:06:14 AWST 2017 ma-start: MA started with Process ID 11320 Tue Jan 1 08:00:10 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 11320 Tue Jan 1 08:00:10 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 600 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 600 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 609 Tue Jan 1 08:00:10 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: Tue Jan 1 08:00:10 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 595 Tue Jan 1 08:00:10 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 595 Tue Jan 1 08:00:10 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 609 Tue Jan 1 08:00:10 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:10 AWST 2013 ma-start: MA removing pid file for dead pid: 609 Tue Jan 1 08:00:10 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:10 AWST 2013 ma-start: MA started with Process ID 599 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 599 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 598 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 598 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 620 Tue Jan 1 08:00:09 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:09 AWST 2013 ma-start: MA removing pid file for dead pid: 620 Tue Jan 1 08:00:09 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:09 AWST 2013 ma-start: MA started with Process ID 599 Tue Jan 29 16:03:42 AWST 2019 ma-start: running stop extensions... Tue Jan 29 16:03:42 AWST 2019 ma.stop: stop initiated... Tue Jan 29 16:03:48 AWST 2019 ma-start: MA explicitly stopped. Exiting restart loop Tue Jan 29 16:03:48 AWST 2019 ma-start: MA done Tue Jan 29 16:03:49 AWST 2019 ma-start: running init extensions... Tue Jan 29 16:03:49 AWST 2019 ma-start: running start extensions... Tue Jan 29 16:03:49 AWST 2019 ma-start: starting MA Tue Jan 29 16:03:49 AWST 2019 ma-start: MA started with Process ID 6735 Tue Jan 1 08:00:11 AWST 2013 ma-start: running init extensions... Tue Jan 1 08:00:11 AWST 2013 ma-start: running start extensions... Tue Jan 1 08:00:11 AWST 2013 ma-start: MA removing pid file for dead pid: 6735 Tue Jan 1 08:00:11 AWST 2013 ma-start: starting MA Tue Jan 1 08:00:11 AWST 2013 ma-start: MA started with Process ID 605 Tue Jan 1 08:00:15 AWST 2013 ma-start: no restart flag found, not restarting MA Tue Jan 1 08:00:15 AWST 2013 ma-start: MA done Fri May 10 10:35:19 AWST 2019 ma-start: running init extensions... Fri May 10 10:35:19 AWST 2019 ma-start: running start extensions... Fri May 10 10:35:19 AWST 2019 ma-start: starting MA Fri May 10 10:35:19 AWST 2019 ma-start: MA started with Process ID 1945 Fri May 10 10:35:22 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 10:35:22 AWST 2019 ma-start: MA done Fri May 10 10:35:49 AWST 2019 ma-start: running stop extensions... Fri May 10 10:35:49 AWST 2019 ma.stop: No PID file found. Java process not stopped... Fri May 10 10:35:55 AWST 2019 ma-start: running init extensions... Fri May 10 10:35:55 AWST 2019 ma-start: running start extensions... Fri May 10 10:35:55 AWST 2019 ma-start: starting MA Fri May 10 10:35:55 AWST 2019 ma-start: MA started with Process ID 2200 Fri May 10 10:35:58 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 10:35:58 AWST 2019 ma-start: MA done Fri May 10 10:42:27 AWST 2019 ma-start: running init extensions... Fri May 10 10:42:27 AWST 2019 ma-start: running start extensions... Fri May 10 10:42:27 AWST 2019 ma-start: starting MA Fri May 10 10:42:27 AWST 2019 ma-start: MA started with Process ID 4508 Fri May 10 10:42:30 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 10:42:30 AWST 2019 ma-start: MA done Fri May 10 10:42:39 AWST 2019 ma-start: running stop extensions... Fri May 10 10:42:39 AWST 2019 ma.stop: No PID file found. Java process not stopped... Fri May 10 10:43:07 AWST 2019 ma-start: running init extensions... Fri May 10 10:43:07 AWST 2019 ma-start: running start extensions... Fri May 10 10:43:07 AWST 2019 ma-start: starting MA Fri May 10 10:43:07 AWST 2019 ma-start: MA started with Process ID 603 Fri May 10 10:43:10 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 10:43:10 AWST 2019 ma-start: MA done Fri May 10 10:44:15 AWST 2019 ma-start: running stop extensions... Fri May 10 10:44:15 AWST 2019 ma.stop: No PID file found. Java process not stopped... Fri May 10 10:44:43 AWST 2019 ma-start: running init extensions... Fri May 10 10:44:43 AWST 2019 ma-start: running start extensions... Fri May 10 10:44:43 AWST 2019 ma-start: starting MA Fri May 10 10:44:43 AWST 2019 ma-start: MA started with Process ID 1624 Fri May 10 10:44:46 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 10:44:46 AWST 2019 ma-start: MA done Fri May 10 10:44:58 AWST 2019 ma-start: running init extensions... Fri May 10 10:44:58 AWST 2019 ma-start: running start extensions... Fri May 10 10:44:58 AWST 2019 ma-start: starting MA Fri May 10 10:44:58 AWST 2019 ma-start: MA started with Process ID 1699 Fri May 10 10:45:01 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 10:45:01 AWST 2019 ma-start: MA done Fri May 10 10:45:14 AWST 2019 ma-start: running init extensions... Fri May 10 10:45:14 AWST 2019 ma-start: running start extensions... Fri May 10 10:45:14 AWST 2019 ma-start: starting MA Fri May 10 10:45:14 AWST 2019 ma-start: MA started with Process ID 1894 Fri May 10 10:45:17 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 10:45:17 AWST 2019 ma-start: MA done Fri May 10 10:45:20 AWST 2019 ma-start: running init extensions... Fri May 10 10:45:20 AWST 2019 ma-start: running start extensions... Fri May 10 10:45:20 AWST 2019 ma-start: starting MA Fri May 10 10:45:20 AWST 2019 ma-start: MA started with Process ID 1945 Fri May 10 10:45:23 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 10:45:23 AWST 2019 ma-start: MA done Fri May 10 10:46:27 AWST 2019 ma-start: running init extensions... Fri May 10 10:46:27 AWST 2019 ma-start: running start extensions... Fri May 10 10:46:27 AWST 2019 ma-start: starting MA Fri May 10 10:46:27 AWST 2019 ma-start: MA started with Process ID 2401 Fri May 10 10:46:30 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 10:46:30 AWST 2019 ma-start: MA done Fri May 10 10:47:53 AWST 2019 ma-start: running stop extensions... Fri May 10 10:47:53 AWST 2019 ma.stop: No PID file found. Java process not stopped... Fri May 10 10:48:19 AWST 2019 ma-start: running init extensions... Fri May 10 10:48:19 AWST 2019 ma-start: running start extensions... Fri May 10 10:48:19 AWST 2019 ma-start: starting MA Fri May 10 10:48:19 AWST 2019 ma-start: MA started with Process ID 612 Fri May 10 10:48:22 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 10:48:22 AWST 2019 ma-start: MA done Fri May 10 10:51:32 AWST 2019 ma-start: running init extensions... Fri May 10 10:51:32 AWST 2019 ma-start: running start extensions... Fri May 10 10:51:32 AWST 2019 ma-start: starting MA Fri May 10 10:51:32 AWST 2019 ma-start: MA started with Process ID 2112 Fri May 10 10:51:36 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 10:51:36 AWST 2019 ma-start: MA done Fri May 10 11:55:50 AWST 2019 ma-start: running init extensions... Fri May 10 11:55:50 AWST 2019 ma-start: running start extensions... Fri May 10 11:55:50 AWST 2019 ma-start: starting MA Fri May 10 11:55:50 AWST 2019 ma-start: MA started with Process ID 23778 Fri May 10 11:55:53 AWST 2019 ma-start: no restart flag found, not restarting MA Fri May 10 11:55:53 AWST 2019 ma-start: MA done Mon May 13 14:27:20 AWST 2019 ma-start: running init extensions... Mon May 13 14:27:20 AWST 2019 ma-start: running start extensions... Mon May 13 14:27:20 AWST 2019 ma-start: starting MA Mon May 13 14:27:20 AWST 2019 ma-start: MA started with Process ID 18871 Mon May 13 14:27:23 AWST 2019 ma-start: no restart flag found, not restarting MA Mon May 13 14:27:23 AWST 2019 ma-start: MA done Mon May 13 16:25:25 AWST 2019 ma-start: running stop extensions... Mon May 13 16:25:25 AWST 2019 ma.stop: No PID file found. Java process not stopped... Mon May 13 16:25:29 AWST 2019 ma-start: running init extensions... Mon May 13 16:25:29 AWST 2019 ma-start: running start extensions... Mon May 13 16:25:29 AWST 2019 ma-start: starting MA Mon May 13 16:25:29 AWST 2019 ma-start: MA started with Process ID 25895 Mon May 13 16:25:32 AWST 2019 ma-start: no restart flag found, not restarting MA Mon May 13 16:25:32 AWST 2019 ma-start: MA done
My ma.log is very sizable. 1400kB to be exact which makes it too large to put in this post. Did you want me to try and cut it down to a more manageable size?
You could mail it to support@infiniteautomation.com
In your first post you provided the output from the command line. It looks like you got a
2112 Bus error
when it was executing ma-start.sh at line 142. That leads me to believe there is a hardware problem. I thought perhaps the files in the ext-enabled folder were corrupt or on a bad sector of the HD but that is just a guess.