Calculating power use
Hi! I have amps and volts (3 phase) that I'm reading. I want to calculate kWh. I assume the easiest method would be to setup a meta data point but I'm a novice. any thoughts? I will also want to move this data to a chart and gauge.
Cheers,
Rick
Hi Rowen
Kind of hard to see what your actual question is. Yes, a meta point will be the best option to calculate the power consumption, The meta-point can then be used in a dashboard with a <ma-get-point-value> component. Go through these documents and if you get stuck let us know what you have done so far and where exactly you are getting stuck,
https://help.infiniteautomation.com/meta-data-source -
Hi Rowen,
I assume the amperage and voltage measurements are on the same device that you're polling? I would simply add both points into the context of the meta point, have only one of them update the context, and have a 1 second execution delay on the meta point (provided you are sampling less than once per few seconds, otherwise I would have a
RuntimeManager.sleep(100);as the first thing (not for history generation though!)).It should also be said that if you require a high degree of precision you should use an energy meter instead of extrapolating from sampled data.
Hi Rowen,
Hope this helps to get started.I am only monitoring current on one of the 3 phases on a small job, and I've used:
return (1.732 * 0.7 * p217.value * p218.value)/1000;1.732 = Square Root of 3
0.7 = power factor I measured onsite once
p217 = Amps
p218 = VoltageIt's not going to be as good as a power meter, but gets me trending which is all I am after and it's fairly close.
@pikey4 Hey! Sorry I didn't reply sooner but your info helped me out. Thx.
R