    Calculating power use
    5 Posts 4 Posters 2.2k Views 4 Watching
      Rowen
      Hi! I have amps and volts (3 phase) that I'm reading. I want to calculate kWh. I assume the easiest method would be to setup a meta data point but I'm a novice. any thoughts? I will also want to move this data to a chart and gauge.
      Cheers,
      Rick
        Hi Rowen
        Kind of hard to see what your actual question is. Yes, a meta point will be the best option to calculate the power consumption, The meta-point can then be used in a dashboard with a <ma-get-point-value> component. Go through these documents and if you get stuck let us know what you have done so far and where exactly you are getting stuck,
        https://help.infiniteautomation.com/meta-data-source
          Hi Rowen,
          I assume the amperage and voltage measurements are on the same device that you're polling? I would simply add both points into the context of the meta point, have only one of them update the context, and have a 1 second execution delay on the meta point (provided you are sampling less than once per few seconds, otherwise I would have a RuntimeManager.sleep(100); as the first thing (not for history generation though!)).
          It should also be said that if you require a high degree of precision you should use an energy meter instead of extrapolating from sampled data.
            Pikey4
            Hi Rowen,
            Hope this helps to get started.
            I am only monitoring current on one of the 3 phases on a small job, and I've used:
            return (1.732 * 0.7 * p217.value * p218.value)/1000;
            1.732 = Square Root of 3
            0.7 = power factor I measured onsite once
            p217 = Amps
            p218 = Voltage
            It's not going to be as good as a power meter, but gets me trending which is all I am after and it's fairly close.
            Mango Core version: 3.5.6
            Mango API module version: 3.5.2
            MangoUi module version: 3.5.5
            Platform: 10.14 MacOS Mojave
            Chrome: Version 70.0.3538.110 (64-bit)
            R 1 Reply Last reply Reply Quote 1
              Rowen @Pikey4
              @pikey4 Hey! Sorry I didn't reply sooner but your info helped me out. Thx.
              R
