    Mango on Ubuntu 14.04
    21 Posts 4 Posters 31.3k Views 2 Watching
    • D Offline
      dmsmith
      Hi Joel, and "support",
      Been having a lot of trouble getting Mango to start on Ubuntu 14.04. When it was first installed it would start and run if invoked by a non-privileged user, invoking with sudo (or as root) would typically fail. Now every time I attempt to start it as a non-privileged user I get the following:
      /opt/mango/bin$ ./ma.sh start
      MA_HOME is /opt/mango
      ml350g5@HPS350G5:/opt/mango/bin$ ma-start: MA started with Process ID: 2073
      INFO 2016-01-18 15:47:59,821 (com.serotonin.m2m2.Main.main:82) - Starting Mango 2.7.2 with Schema Version: 11
      INFO 2016-01-18 15:48:02,349 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'egauge', v1.1.1 by Infinite Automation
      INFO 2016-01-18 15:48:02,424 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'dnp3', v1.6.1 by Infinite Automation Software
      INFO 2016-01-18 15:48:02,445 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'mangoNoSqlDatabase', v1.2.1 by Infinite Automation Software
      INFO 2016-01-18 15:48:02,467 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'asciiFile', v1.2.1 by Infinite Automation
      INFO 2016-01-18 15:48:02,489 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'loggingConsole', v1.1.1 by Infinite Automation
      INFO 2016-01-18 15:48:02,505 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'pointLinks', v1.5.2 by Infinite Automation Software
      INFO 2016-01-18 15:48:02,525 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'TCPIP', v1.1.3 by Infinite Automation
      INFO 2016-01-18 15:48:02,546 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'dataImport', v1.4.1 by Infinite Automation Software
      INFO 2016-01-18 15:48:02,565 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'pachube', v1.5.1 by Infinite Automation Software
      INFO 2016-01-18 15:48:02,583 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'ssh', v1.1.1 by Infinite Automation
      INFO 2016-01-18 15:48:02,601 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'mangoApi', v1.1.3 by Infinite Automation Systems Inc.
      INFO 2016-01-18 15:48:02,621 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'watchlists', v1.7.4 by Infinite Automation Systems Inc.
      Exception in thread "main" java.io.IOException: Unable to delete file: /opt/mango/web/WEB-INF/tags/watchlists/mobilePage.tag
      at org.apache.commons.io.FileUtils.forceDelete(FileUtils.java:1919)
      at org.apache.commons.io.FileUtils.cleanDirectory(FileUtils.java:1399)
      at org.apache.commons.io.FileUtils.deleteDirectory(FileUtils.java:1331)
      at com.serotonin.m2m2.Main.deleteDir(Main.java:757)
      at com.serotonin.m2m2.Main.loadModules(Main.java:499)
      at com.serotonin.m2m2.Main.main(Main.java:99)
      ma-start: no restart flag found, not restarting MA
      ma-start: MA done
      With sudo the following is what happens (this behaviour is unchanged):
      /opt/mango/bin$ sudo ./ma.sh start
      [sudo] password for ml350g5:
      ml350g5@HPS350G5:/opt/mango/bin$ /opt/mango/bin/ma-start.sh: line 94: java: command not found
      ma-start: MA started with Process ID: 2114
      ma-start: MA done
      Java version details:
      /opt/mango/bin$ java -version
      java version "1.8.0_66"
      Java(TM) SE Runtime Environment (build 1.8.0_66-b17)
      Java HotSpot(TM) 64-Bit Server VM (build 25.66-b17, mixed mode)
      Have tried simply creating an empty RESTART file but that results in the start script entering an infinite loop that required a SIGKILL to terminate.
      Is this something you have seen before? Are you able to point me in the right direction? Thanks.
      Regards,
      David
        Hi David,
        Mango requires to be run with root or elevated privileges so doing sudo ./ma.sh start is one valid way to go. The problem that you're having is that your environment "PATH" variable has been set in such a way that it is not global, or perhaps is not set until a user logs in (like in a .bashrc file).
        To fix, you can do either of two things, you can define JAVA_HOME as an environment variable, which would point to your JDK (such that JAVA_HOME/bin/java exists or you can make sure your JAVA_HOME/bin/ directory is one of the folders specified in the variable PATH. To see what your PATH is, use "echo $PATH;" To set JAVA_HOME, add it as it's own line in the file /etc/environment and set it to the absolute path to your JDK. You can also edit the paths described in the PATH variable in /etc/environment to set persistent, global settings, in which can you need to have JAVA_HOME/bin/
        • D Offline
          dmsmith
          Thanks Phil, however as root:
          root@HPS350G5:/opt/mango/bin# echo $PATH
          /usr/local/sbin:/usr/local/bin:/usr/sbin:/usr/bin:/sbin:/bin:/usr/games:/usr/local/games:/usr/lib/jvm/oracle_jdk8/bin:/usr/lib/jvm/oracle_jdk8/db/bin:/usr/lib/jvm/oracle_jdk8/jre/bin
          root@HPS350G5:/opt/mango/bin# echo $JAVA_HOME
          root@HPS350G5:/home/ml350g5# java -version
          root@HPS350G5:/home/ml350g5# cd /opt/mango/bin
          root@HPS350G5:/opt/mango/bin# ./ma.sh start
          root@HPS350G5:/opt/mango/bin# ma-start: MA started with Process ID: 12420
          INFO 2016-01-19 09:09:30,113 (com.serotonin.m2m2.Main.main:82) - Starting Mango 2.7.2 with Schema Version: 11
          INFO 2016-01-19 09:09:30,971 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'egauge', v1.1.1 by Infinite Automation
          INFO 2016-01-19 09:09:31,010 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'dnp3', v1.6.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,020 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'mangoNoSqlDatabase', v1.2.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,029 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'asciiFile', v1.2.1 by Infinite Automation
          INFO 2016-01-19 09:09:31,036 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'loggingConsole', v1.1.1 by Infinite Automation
          INFO 2016-01-19 09:09:31,044 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'pointLinks', v1.5.2 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,050 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'TCPIP', v1.1.3 by Infinite Automation
          INFO 2016-01-19 09:09:31,055 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'dataImport', v1.4.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,060 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'pachube', v1.5.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,065 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'ssh', v1.1.1 by Infinite Automation
          INFO 2016-01-19 09:09:31,070 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'mangoApi', v1.1.3 by Infinite Automation Systems Inc.
          INFO 2016-01-19 09:09:31,075 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'watchlists', v1.7.4 by Infinite Automation Systems Inc.
          INFO 2016-01-19 09:09:31,181 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'sqlds', v1.6.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,207 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'sstTheme', v1.1.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,219 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'scheduledEvents', v1.5.1 by (unknown vendor)
          INFO 2016-01-19 09:09:31,250 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'dashboards', v1.1.2 by Infinite Automation
          INFO 2016-01-19 09:09:31,309 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'scripting', v1.1.2 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,327 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'jspViews', v2.1.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,364 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'twilio', v1.1.2 by (unknown vendor)
          INFO 2016-01-19 09:09:31,390 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'controlcore', v1.1.1 by Infinite Automation
          INFO 2016-01-19 09:09:31,398 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'graphicalViews', v1.6.3 by Infinite Automation Systems Inc.
          INFO 2016-01-19 09:09:31,434 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'opcda', v1.6.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,446 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'sstGlobalScripts', v1.5.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,461 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'dataPointDetailsView', v1.0.3 by Infinite Automation
          INFO 2016-01-19 09:09:31,472 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'modbus', v1.6.3 by Infinite Automation Systems Inc.
          INFO 2016-01-19 09:09:31,487 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'sstGraphics', v1.1.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,533 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'BACnet', v2.2.3 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,548 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'galil', v1.5.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,566 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'pop3', v1.5.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,581 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'onewire', v1.5.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,605 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'virtualDS', v1.5.2 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,625 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'vmstat', v1.5.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,643 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'meta', v2.2.3 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,658 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'jmxds', v1.5.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,677 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'dglux', v1.3.2 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,968 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'log4jDS', v1.1.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:31,997 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'internal', v1.5.3 by Infinite Automation Software
          INFO 2016-01-19 09:09:32,015 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'templateConfig', v1.0.8 by Infinite Automation Software
          INFO 2016-01-19 09:09:32,038 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'maintenanceEvents', v1.5.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:32,057 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'reports', v2.2.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:32,084 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'serial', v1.2.1 by Infinite Automation
          INFO 2016-01-19 09:09:32,098 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'excelReports', v1.0.3 by Infinite Automation Software
          INFO 2016-01-19 09:09:32,151 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'dataFile', v1.1.1 by Infinite Automation
          INFO 2016-01-19 09:09:32,181 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'snmp', v1.5.2 by Infinite Automation Software
          INFO 2016-01-19 09:09:32,194 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'http', v1.5.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:32,213 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'sqlConsole', v1.5.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:32,240 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'openv4j', v1.1.2 by Infinite Automation Systems Inc.
          INFO 2016-01-19 09:09:32,250 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'mbus', v1.1.2 by Infinite Automation Systems Inc.
          INFO 2016-01-19 09:09:32,265 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'log4JReset', v1.1.1 by Infinite Automation Software
          INFO 2016-01-19 09:09:32,276 (com.serotonin.m2m2.Main.loadModules:417) - Loading module 'persistent', v1.6.2 by Infinite Automation Software
          INFO 2016-01-19 09:09:34,834 (com.infiniteautomation.mangoApi.MangoApiReloadingProperties.checkForReload:146) - (mangoApiHeaders) Found updated file at /opt/mango/web/modules/mangoApi/classes/mangoApiHeaders.properties. Reloading properties
          INFO 2016-01-19 09:09:35,038 (com.serotonin.m2m2.Lifecycle.loadLic:450) - Checking license...
          INFO 2016-01-19 09:09:35,371 (com.serotonin.m2m2.db.H2Proxy.initializeImpl:42) - Initializing H2 connection manager
          WARN 2016-01-19 09:09:37,023 (com.serotonin.m2m2.db.upgrade.DBUpgrade.checkUpgrade:96) - Upgrading 'core' from 9 to 10
          INFO 2016-01-19 09:09:37,024 (com.serotonin.m2m2.db.upgrade.DBUpgrade.createUpdateLogOutputStream:152) - Writing upgrade log to /opt/mango/logs/com.serotonin.m2m2.db.upgrade.Upgrade9.log
          ERROR 2016-01-19 09:09:37,827 (com.serotonin.m2m2.Main.main:120) - Error during initialization
          com.serotonin.ShouldNeverHappenException: org.springframework.jdbc.BadSqlGrammarException: StatementCallback; bad SQL grammar [ALTER TABLE users ADD COLUMN permissions VARCHAR(255); ]; nested exception is org.h2.jdbc.JdbcSQLException: Duplicate column name "PERMISSIONS"; SQL statement:
          ALTER TABLE users ADD COLUMN permissions VARCHAR(255); [42121-181]
          at com.serotonin.m2m2.db.upgrade.DBUpgrade.checkUpgrade(DBUpgrade.java:102)
          at com.serotonin.m2m2.db.upgrade.DBUpgrade.checkUpgrade(DBUpgrade.java:34)
          at com.serotonin.m2m2.db.DatabaseProxy.initialize(DatabaseProxy.java:180)
          at com.serotonin.m2m2.Lifecycle.databaseInitialize(Lifecycle.java:588)
          at com.serotonin.m2m2.Lifecycle.initialize(Lifecycle.java:266)
          at com.serotonin.m2m2.Main.main(Main.java:116)
          Caused by: org.springframework.jdbc.BadSqlGrammarException: StatementCallback; bad SQL grammar [ALTER TABLE users ADD COLUMN permissions VARCHAR(255); ]; nested exception is org.h2.jdbc.JdbcSQLException: Duplicate column name "PERMISSIONS"; SQL statement:
          at org.springframework.jdbc.support.SQLErrorCodeSQLExceptionTranslator.doTranslate(SQLErrorCodeSQLExceptionTranslator.java:231)
          at org.springframework.jdbc.support.AbstractFallbackSQLExceptionTranslator.translate(AbstractFallbackSQLExceptionTranslator.java:73)
          at org.springframework.jdbc.core.JdbcTemplate.execute(JdbcTemplate.java:415)
          at org.springframework.jdbc.core.JdbcTemplate.execute(JdbcTemplate.java:439)
          at com.serotonin.m2m2.db.H2Proxy.runScript(H2Proxy.java:146)
          at com.serotonin.m2m2.db.upgrade.DBUpgrade.runScript(DBUpgrade.java:129)
          at com.serotonin.m2m2.db.upgrade.DBUpgrade.runScript(DBUpgrade.java:143)
          at com.serotonin.m2m2.db.upgrade.DBUpgrade.runScript(DBUpgrade.java:134)
          at com.serotonin.m2m2.db.upgrade.Upgrade9.upgrade(Upgrade9.java:27)
          at com.serotonin.m2m2.db.upgrade.DBUpgrade.checkUpgrade(DBUpgrade.java:98)
          ... 5 more
          Caused by: org.h2.jdbc.JdbcSQLException: Duplicate column name "PERMISSIONS"; SQL statement:
          at org.h2.message.DbException.getJdbcSQLException(DbException.java:345)
          at org.h2.message.DbException.get(DbException.java:179)
          at org.h2.message.DbException.get(DbException.java:155)
          at org.h2.table.Table.setColumns(Table.java:398)
          at org.h2.table.TableBase.<init>(TableBase.java:44)
          at org.h2.table.RegularTable.<init>(RegularTable.java:74)
          at org.h2.schema.Schema.createTable(Schema.java:584)
          at org.h2.command.ddl.AlterTableAlterColumn.cloneTableStructure(AlterTableAlterColumn.java:321)
          at org.h2.command.ddl.AlterTableAlterColumn.copyData(AlterTableAlterColumn.java:229)
          at org.h2.command.ddl.AlterTableAlterColumn.update(AlterTableAlterColumn.java:161)
          at org.h2.command.CommandContainer.update(CommandContainer.java:78)
          at org.h2.command.Command.executeUpdate(Command.java:254)
          at org.h2.jdbc.JdbcStatement.executeInternal(JdbcStatement.java:185)
          at org.h2.jdbc.JdbcStatement.execute(JdbcStatement.java:159)
          at org.springframework.jdbc.core.JdbcTemplate$1ExecuteStatementCallback.doInStatement(JdbcTemplate.java:431)
          at org.springframework.jdbc.core.JdbcTemplate.execute(JdbcTemplate.java:404)
          ... 12 more
          INFO 2016-01-19 09:09:37,833 (com.serotonin.m2m2.Lifecycle.terminate:330) - Mango Lifecycle terminating...
          Exception in thread "high-pool-1-thread-2" java.lang.NullPointerException
          at com.serotonin.m2m2.CoreLicenseDefinition$2.run(CoreLicenseDefinition.java:149)
          at com.serotonin.timer.sync.Synchronizer$TaskWrapper.run(Synchronizer.java:155)
          at java.util.concurrent.ThreadPoolExecutor.runWorker(ThreadPoolExecutor.java:1142)
          at java.util.concurrent.ThreadPoolExecutor$Worker.run(ThreadPoolExecutor.java:617)
          INFO 2016-01-19 09:09:37,993 (com.serotonin.m2m2.Lifecycle.terminate:432) - Mango Lifecycle terminated.
          INFO 2016-01-19 09:09:37,995 (com.serotonin.m2m2.Lifecycle.terminate:330) - Mango Lifecycle terminating...
          ma-start: MA done
          • D Offline
            dmsmith
            Oh, forgot to mention that having it go through the process in the last message there before dying is not at all uncommon.
              Is this a new installation or is there data in the database? If this is a new database, go ahead and delete your Mango/databases directory and start it up again. This looks like it tried to upgrade the database at some point but couldn't finish the upgrade script. If there is data there, this will possibly take 1) deleting the column so that the upgrade can succeed or 2) increment the database version number if everything was properly formed. If you had a previous Mango, I bet that it was on a different database, and you're attempting to convert to H2 and upgrade the schema in the same launch. We discourage this. A database should be converted, then upgraded or upgraded and then converted, but they should be done in separate launches of the program.
              You may still have the easiest time stashing the database (in case you want it at some point), launching on a clean one, and restoring the database and using the backup utilities on the systems settings page to restore from your Mango/backups folder if there was data or configuration that needs to be kept.
                You will note that you logged in to get those path results. To see the global su PATH, log in as your other user and sudo echo $PATH
                • D Offline
                  dmsmith
                  Thanks Phil. There was nothing in the database that couldn't be recreated relatively easily so went ahead and moved the old databases directory aside and did an 'ma.sh start' - has worked nicely. Have only had Mango installed for around 2 or 3 weeks and haven't initiated a db upgrade so I'm not sure where that would have gone wrong.
                  Thanks for the help.
                  • D Offline
                    dmsmith
                    Hi Phil,
                    OK, so using sudo from the regular user rather than su-ing :
                    ml350g5@HPS350G5:/opt/mango/bin$ sudo echo $JAVA_HOME
                    ml350g5@HPS350G5:/opt/mango/bin$ sudo ./ma.sh start
                    ma-start: MA started with Process ID: 21182
                    ma-start: MA done
                    Immediately prior to this Mango was running correctly when started by root. As root I issued "ma.sh stop" which completed successfully, exited from the root shell, and then did what you see above. Any thoughts?
                    Thanks!
                      It looks like your JAVA_HOME variable is pointing to a JVM rather than the JDK. It needs to point to the JDK to work. Let us know if that solves it.
                        After you have that resolved I would recommend setting up the service to start and stop Mango: http://infiniteautomation.com/wiki/doku.php?id=installation:services
                        • D Offline
                          dmsmith
                          Thanks Joel.
                          It's definitely the JDK.
                          /usr/lib/jvm/oracle_jdk8# javac -version
                          javac 1.8.0_66
                          I have indeed created that service, I just have a habit of going directly to ma.sh instead :)
                            Can you check the /opt/mango/lib folder I wonder if it is empty? If so there could have been a upgrade issue in which case you would want to download the core zip file again and copy all the contents of the lib folder. This is just another guess. If that doesn't resolve it contact us at support and we'll hop on a screen share with you to poke around directly.
                            • D Offline
                              dmsmith
                              Definitely not empty - 156 jar files in there.
                                Well, more information could be gained by modifying the bin/ma-init.sh script to echo relevant stuff during the bin/ma.sh launch
                                Perhaps...
                                echo $EXECJAVA
                                ls -l $(echo $EXECJAVA | sed -e 's/java$//') | grep java
                                ... around line 27 of bin/ma-init.sh
                                • D Offline
                                  dmsmith
                                  OK, that did the trick thanks Phil. Even though sudo echo $PATH didn't suggest that the path was being reset, adding those lines into the init script showed that it actually was being reset. Launching with sudo -E ./ma.sh start worked correctly! :)
                                    mihairosu
                                    We've been having a similar problem (not auto starting at boot) for months now. However, I'm not so Linux savvy as smith. Could one of you poke around and try to resolve this issue?
                                    PS, We're Sheridan Point Condominiums.
                                    D 1 Reply Last reply Reply Quote 0
                                    • D Offline
                                      dmsmith @mihairosu
                                      @mihairosu
                                      Hi. What happens when you try to manually start Mango after boot? What process do you use to do that?
                                      Cheers,
                                      David
                                        Hi Mihairosu,
                                        Can you email us the log from your Mango? You can find these on the computer at /opt/mango/logs/ma.log or more easily by logging in to Mango as the admin, navigating to the logging console page (tree log icon), and clicking the 'email logs to Infinite Automation' button (I believe this is Core 2.7+)
                                        Icon:
                                          Hi Mihairosu, I may already be able to look into it. I will conduct the rest by email.
                                            mihairosu
                                            Thanks for fixing it for us Phil, this is much nicer!