    Why did wind sensor canot received the data via modbus serial port.
    26 Posts 4 Posters 24.2k Views 1 Watching
    • E Offline
      edmond
      Now I have wind sensor and want to received data from mango in modbus serial port. and I have set modbus mode in wind sensor .
      and can received data use modscan32 software.
      But when I choose mango to received the data and display "modbus Main equipment malfunction".
      I donot know the what is wrong with it ?
      please give suggestion.
      Thanks.
      • E Offline
        edmond
        And I use other wind sensor for experiments .
        and the result is "No response from slave 1"
        What is wrong with it ?
        Any idea?
        The sensor is 1723-PS-0015 MetPak Pro
        • E Offline
          edmond
          I post the new picture for reference.
          • jeremyhJ Offline
            jeremyh
            Modscan doesn't receive any data..
            Your equipment is not set up correctly
            • E Offline
              edmond
              jeremyhs.
              You are not right.
              I can received data via modbus ip as show attachment ,and it display same as like this.This prove modbus scan software can received data and display in this type.
              you can see I can received data in mango.
              BR
              • jeremyhJ Offline
                jeremyh
                It PROVES nothing.
                In all of your pictures there is no indication that you are receiving ANY data over serial.
                So if Modbus over IP works just use that?
                You should use stop bits = 1 too
                • E Offline
                  edmond
                  yes.
                  but I change slave id =1
                  Still as same as before.
                  • E Offline
                    edmond
                    still status .
                    Any idea?
                    • E Offline
                      edmond
                      below is some log for reference. (ma.log file)
                      INFO 2014-08-14 14:56:49,100 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module abeip
                      INFO 2014-08-14 14:56:50,386 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module abpccc
                      INFO 2014-08-14 14:56:50,668 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module asciiFile
                      INFO 2014-08-14 14:56:51,515 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module BACnet
                      INFO 2014-08-14 14:56:52,367 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module controlcore
                      INFO 2014-08-14 14:56:52,632 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module dataFile
                      INFO 2014-08-14 14:57:15,367 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module dataImport
                      INFO 2014-08-14 14:57:15,841 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module dglux
                      INFO 2014-08-14 14:58:11,121 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module dnp3
                      INFO 2014-08-14 14:58:11,873 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module galil
                      INFO 2014-08-14 14:58:12,022 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module graphicalViews
                      INFO 2014-08-14 14:58:13,876 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module http
                      INFO 2014-08-14 14:58:16,768 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module internal
                      INFO 2014-08-14 14:58:17,299 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module jmxds
                      INFO 2014-08-14 14:58:18,323 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module jspViews
                      INFO 2014-08-14 14:58:21,590 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module log4JReset
                      INFO 2014-08-14 14:58:22,370 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module loggingConsole
                      INFO 2014-08-14 14:58:23,666 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module maintenanceEvents
                      INFO 2014-08-14 14:58:25,282 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module mbus
                      INFO 2014-08-14 14:58:25,685 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module meta
                      INFO 2014-08-14 14:58:26,233 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module modbus
                      INFO 2014-08-14 14:58:26,679 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module onewire
                      INFO 2014-08-14 14:58:27,110 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module opcda
                      INFO 2014-08-14 14:58:28,060 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module openv4j
                      INFO 2014-08-14 14:58:28,410 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module pachube
                      INFO 2014-08-14 14:58:29,590 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module persistent
                      INFO 2014-08-14 14:58:30,402 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module pid
                      INFO 2014-08-14 14:58:33,381 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module pointLinks
                      INFO 2014-08-14 14:58:35,767 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module pop3
                      INFO 2014-08-14 14:58:37,098 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module reports
                      INFO 2014-08-14 14:58:37,841 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module scheduledEvents
                      INFO 2014-08-14 14:58:38,322 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module scripting
                      INFO 2014-08-14 14:58:38,592 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module serial
                      INFO 2014-08-14 14:58:39,143 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module snmp
                      INFO 2014-08-14 14:58:39,411 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module sqlConsole
                      INFO 2014-08-14 14:58:39,765 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module sqlds
                      INFO 2014-08-14 14:58:40,028 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module sstGlobalScripts
                      INFO 2014-08-14 14:58:40,301 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module sstGraphics
                      INFO 2014-08-14 14:58:40,893 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module sstTheme
                      INFO 2014-08-14 14:58:41,068 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module templateConfig
                      INFO 2014-08-14 14:58:41,432 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module twilio
                      INFO 2014-08-14 14:58:41,773 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module virtualDS
                      INFO 2014-08-14 14:58:42,103 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module vmstat
                      INFO 2014-08-14 14:58:42,795 (com.serotonin.m2m2.Main.openZipFiles:164) - Installing module watchlists
                      INFO 2014-08-14 14:58:45,595 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'abeip', v1.0.6 by Deltamation Software
                      INFO 2014-08-14 14:58:45,754 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'abpccc', v1.0.4 by Deltamation Software
                      INFO 2014-08-14 14:58:45,783 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'asciiFile', v1.1.3 by Infinite Automation
                      INFO 2014-08-14 14:58:45,787 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'BACnet', v2.1.0 by Infinite Automation Software
                      INFO 2014-08-14 14:58:45,857 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'controlcore', v1.0.4 by Infinite Automation
                      INFO 2014-08-14 14:58:45,873 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dataFile', v1.0.4 by Infinite Automation
                      INFO 2014-08-14 14:58:45,932 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dataImport', v1.3.4 by Infinite Automation Software
                      INFO 2014-08-14 14:58:45,938 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dglux', v1.0.11 by Infinite Automation Software
                      INFO 2014-08-14 14:58:45,939 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dnp3', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 14:58:45,946 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'galil', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 14:58:45,950 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'graphicalViews', v1.4.8 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,018 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'http', v1.4.6 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,026 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'internal', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,029 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'jmxds', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,032 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'jspViews', v2.0.3 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,269 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'log4JReset', v1.0.5 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,271 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'loggingConsole', v1.0.1 by Infinite Automation
                      INFO 2014-08-14 14:58:46,272 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'maintenanceEvents', v1.4.7 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,278 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'mbus', v1.0.4 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,280 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'meta', v2.0.7 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,285 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'modbus', v1.4.8 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,291 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'onewire', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,295 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'opcda', v1.5.5 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,306 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'openv4j', v1.0.4 by aploese
                      INFO 2014-08-14 14:58:46,308 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pachube', v1.4.7 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,312 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'persistent', v1.4.6 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,317 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pid', v1.0.2 by Infinite Automation
                      INFO 2014-08-14 14:58:46,322 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pointLinks', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,325 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pop3', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,329 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'reports', v2.0.6 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,349 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'scheduledEvents', v1.4.6 by (unknown vendor)
                      INFO 2014-08-14 14:58:46,352 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'scripting', v1.0.7 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,355 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'serial', v1.1.2 by Infinite Automation
                      INFO 2014-08-14 14:58:46,359 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'snmp', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,374 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sqlConsole', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,380 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sqlds', v1.5.5 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,390 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sstGlobalScripts', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,396 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sstGraphics', v1.0.5 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,397 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sstTheme', v1.0.5 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,398 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'templateConfig', v1.0.4 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,402 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'twilio', v1.0.3 by (unknown vendor)
                      INFO 2014-08-14 14:58:46,406 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'virtualDS', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,410 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'vmstat', v1.4.6 by Infinite Automation Software
                      INFO 2014-08-14 14:58:46,413 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'watchlists', v1.5.7 by Infinite Automation Software
                      INFO 2014-08-14 14:59:05,785 (com.serotonin.m2m2.web.M2M2ContextListener.contextInitialized:31) - Mango Automation context starting
                      INFO 2014-08-14 14:59:05,786 (com.serotonin.m2m2.web.M2M2ContextListener.contextInitialized:39) - Mango Automation context started
                      INFO 2014-08-14 14:59:10,341 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/users.shtm] onto handler 'usersController'
                      INFO 2014-08-14 14:59:10,430 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source.shtm] onto handler 'dataSourceController'
                      INFO 2014-08-14 14:59:10,494 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/publisher_edit.shtm] onto handler 'publisherEditController'
                      INFO 2014-08-14 14:59:10,855 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/login.htm] onto handler 'loginController'
                      INFO 2014-08-14 14:59:10,856 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/shutdown.htm] onto handler 'shutdownController'
                      INFO 2014-08-14 14:59:10,979 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source_properties.shtm] onto handler 'dataSourcePropertiesController'
                      INFO 2014-08-14 14:59:10,984 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/startup.htm] onto handler 'startupController'
                      INFO 2014-08-14 14:59:11,040 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/webcam_live_feed.htm] onto handler 'webcamLiveFeedController'
                      INFO 2014-08-14 14:59:11,041 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/unauthorized.htm] onto handler 'unauthorizedController'
                      INFO 2014-08-14 14:59:11,043 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_point_edit.shtm] onto handler 'dataPointEditController'
                      INFO 2014-08-14 14:59:11,080 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source_properties_error.shtm] onto handler 'dataSourceErrorController'
                      INFO 2014-08-14 14:59:11,082 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source_edit.shtm] onto handler 'dataSourceEditController'
                      INFO 2014-08-14 14:59:11,084 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/users.shtm] onto handler 'usersController'
                      INFO 2014-08-14 14:59:11,125 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile.shtm] onto handler 'mobileController'
                      INFO 2014-08-14 14:59:11,126 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/help.shtm] onto handler 'helpController'
                      INFO 2014-08-14 14:59:11,127 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/logout.htm] onto handler 'logoutController'
                      INFO 2014-08-14 14:59:52,935 (com.serotonin.m2m2.Lifecycle.lic:404) - Checking license...
                      INFO 2014-08-14 14:59:52,936 (com.serotonin.m2m2.Lifecycle.loadLic:519) - License file not found
                      INFO 2014-08-14 15:00:04,488 (com.serotonin.m2m2.db.H2Proxy.initializeImpl:37) - Initializing H2 connection manager
                      INFO 2014-08-14 15:00:36,633 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                      INFO 2014-08-14 15:00:36,638 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.modbus.dwr.ModbusEditDwr
                      INFO 2014-08-14 15:00:36,702 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                      INFO 2014-08-14 15:00:36,707 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                      INFO 2014-08-14 15:00:36,715 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: br.org.scadabr.dnp3.dwr.DnpEditDwr
                      INFO 2014-08-14 15:00:37,156 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_point_details.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,160 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/events.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,162 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/pending_alarms.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,163 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/event_handlers.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,164 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_sources.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,165 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/point_hierarchy.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,166 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mailing_lists.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,167 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/publishers.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,170 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/system_settings.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,171 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/modules.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,172 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/emport.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,173 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/upload.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,173 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/download.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,174 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile_data_point_details.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,175 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/logging_console.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,175 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/templateConfig.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,178 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/dataImport.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,180 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/dglux.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,182 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/dglux/login.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,184 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/views.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,186 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/public_view.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,189 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/view_edit.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,190 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/maintenance_events.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,191 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/point_links.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,193 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/reportChart.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,194 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/reports.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,194 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/scheduled_events.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,199 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/sqlConsole.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,201 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/globalScripts.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,205 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/watch_list.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,208 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/login.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,217 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/watch_list.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:00:37,223 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/logout.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:02:37,023 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'abeip', v1.0.6 by Deltamation Software
                      INFO 2014-08-14 15:02:37,322 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'abpccc', v1.0.4 by Deltamation Software
                      INFO 2014-08-14 15:02:37,327 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'asciiFile', v1.1.3 by Infinite Automation
                      INFO 2014-08-14 15:02:37,333 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'BACnet', v2.1.0 by Infinite Automation Software
                      INFO 2014-08-14 15:02:37,787 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'controlcore', v1.0.4 by Infinite Automation
                      INFO 2014-08-14 15:02:37,791 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dataFile', v1.0.4 by Infinite Automation
                      INFO 2014-08-14 15:02:38,258 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dataImport', v1.3.4 by Infinite Automation Software
                      INFO 2014-08-14 15:02:38,262 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dglux', v1.0.11 by Infinite Automation Software
                      INFO 2014-08-14 15:02:38,264 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dnp3', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:02:38,270 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'galil', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:02:38,274 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'graphicalViews', v1.4.8 by Infinite Automation Software
                      INFO 2014-08-14 15:02:40,138 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'http', v1.4.6 by Infinite Automation Software
                      INFO 2014-08-14 15:02:41,299 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'internal', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:02:41,305 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'jmxds', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:02:41,311 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'jspViews', v2.0.3 by Infinite Automation Software
                      INFO 2014-08-14 15:02:41,742 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'log4JReset', v1.0.5 by Infinite Automation Software
                      INFO 2014-08-14 15:02:41,744 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'loggingConsole', v1.0.1 by Infinite Automation
                      INFO 2014-08-14 15:02:41,745 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'maintenanceEvents', v1.4.7 by Infinite Automation Software
                      INFO 2014-08-14 15:02:41,862 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'mbus', v1.0.4 by Infinite Automation Software
                      INFO 2014-08-14 15:02:41,864 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'meta', v2.0.7 by Infinite Automation Software
                      INFO 2014-08-14 15:02:42,072 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'modbus', v1.4.8 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,137 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'onewire', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,144 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'opcda', v1.5.5 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,166 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'openv4j', v1.0.4 by aploese
                      INFO 2014-08-14 15:02:43,168 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pachube', v1.4.7 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,358 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'persistent', v1.4.6 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,481 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pid', v1.0.2 by Infinite Automation
                      INFO 2014-08-14 15:02:43,596 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pointLinks', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,599 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pop3', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,602 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'reports', v2.0.6 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,673 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'scheduledEvents', v1.4.6 by (unknown vendor)
                      INFO 2014-08-14 15:02:43,676 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'scripting', v1.0.7 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,681 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'serial', v1.1.2 by Infinite Automation
                      INFO 2014-08-14 15:02:43,685 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'snmp', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,688 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sqlConsole', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,692 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sqlds', v1.5.5 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,695 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sstGlobalScripts', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,699 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sstGraphics', v1.0.5 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,700 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sstTheme', v1.0.5 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,700 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'templateConfig', v1.0.4 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,704 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'twilio', v1.0.3 by (unknown vendor)
                      INFO 2014-08-14 15:02:43,709 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'virtualDS', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,713 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'vmstat', v1.4.6 by Infinite Automation Software
                      INFO 2014-08-14 15:02:43,716 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'watchlists', v1.5.7 by Infinite Automation Software
                      INFO 2014-08-14 15:02:47,978 (com.serotonin.m2m2.web.M2M2ContextListener.contextInitialized:31) - Mango Automation context starting
                      INFO 2014-08-14 15:02:47,979 (com.serotonin.m2m2.web.M2M2ContextListener.contextInitialized:39) - Mango Automation context started
                      INFO 2014-08-14 15:02:48,954 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/users.shtm] onto handler 'usersController'
                      INFO 2014-08-14 15:02:49,009 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source.shtm] onto handler 'dataSourceController'
                      INFO 2014-08-14 15:02:49,059 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/publisher_edit.shtm] onto handler 'publisherEditController'
                      INFO 2014-08-14 15:02:49,173 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/login.htm] onto handler 'loginController'
                      INFO 2014-08-14 15:02:49,206 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/shutdown.htm] onto handler 'shutdownController'
                      INFO 2014-08-14 15:02:49,327 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source_properties.shtm] onto handler 'dataSourcePropertiesController'
                      INFO 2014-08-14 15:02:49,328 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/startup.htm] onto handler 'startupController'
                      INFO 2014-08-14 15:02:49,373 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/webcam_live_feed.htm] onto handler 'webcamLiveFeedController'
                      INFO 2014-08-14 15:02:49,373 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/unauthorized.htm] onto handler 'unauthorizedController'
                      INFO 2014-08-14 15:02:49,374 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_point_edit.shtm] onto handler 'dataPointEditController'
                      INFO 2014-08-14 15:02:49,418 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source_properties_error.shtm] onto handler 'dataSourceErrorController'
                      INFO 2014-08-14 15:02:49,418 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source_edit.shtm] onto handler 'dataSourceEditController'
                      INFO 2014-08-14 15:02:49,419 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/users.shtm] onto handler 'usersController'
                      INFO 2014-08-14 15:02:49,473 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile.shtm] onto handler 'mobileController'
                      INFO 2014-08-14 15:02:49,474 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/help.shtm] onto handler 'helpController'
                      INFO 2014-08-14 15:02:49,474 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/logout.htm] onto handler 'logoutController'
                      INFO 2014-08-14 15:02:59,968 (com.serotonin.m2m2.Lifecycle.lic:404) - Checking license...
                      INFO 2014-08-14 15:02:59,968 (com.serotonin.m2m2.Lifecycle.loadLic:519) - License file not found
                      INFO 2014-08-14 15:03:00,379 (com.serotonin.m2m2.db.H2Proxy.initializeImpl:37) - Initializing H2 connection manager
                      INFO 2014-08-14 15:03:05,339 (com.serotonin.m2m2.db.upgrade.DBUpgrade.checkUpgrade:36) - Starting instance with core version 2.4.0, db 9
                      INFO 2014-08-14 15:03:07,271 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                      INFO 2014-08-14 15:03:07,277 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.modbus.dwr.ModbusEditDwr
                      INFO 2014-08-14 15:03:07,365 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                      INFO 2014-08-14 15:03:07,388 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                      INFO 2014-08-14 15:03:07,399 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: br.org.scadabr.dnp3.dwr.DnpEditDwr
                      INFO 2014-08-14 15:03:07,452 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_point_details.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,452 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/events.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,452 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/pending_alarms.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,452 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/event_handlers.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,453 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_sources.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,453 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/point_hierarchy.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,453 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mailing_lists.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,453 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/publishers.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,453 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/system_settings.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,454 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/modules.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,454 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/emport.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,454 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/upload.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,454 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/download.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,454 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile_data_point_details.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,455 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/logging_console.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,455 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/templateConfig.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,458 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/dataImport.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,459 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/dglux.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,460 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/dglux/login.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,462 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/views.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,463 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/public_view.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,465 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/view_edit.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,466 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/maintenance_events.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,467 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/point_links.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,469 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/reportChart.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,470 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/reports.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,470 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/scheduled_events.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,472 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/sqlConsole.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,472 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/globalScripts.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,475 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/watch_list.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,477 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/login.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,480 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/watch_list.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:03:07,482 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/logout.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:13,545 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'abeip', v1.0.6 by Deltamation Software
                      INFO 2014-08-14 15:20:13,793 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'abpccc', v1.0.4 by Deltamation Software
                      INFO 2014-08-14 15:20:14,082 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'asciiFile', v1.1.3 by Infinite Automation
                      INFO 2014-08-14 15:20:14,147 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'BACnet', v2.1.0 by Infinite Automation Software
                      INFO 2014-08-14 15:20:14,605 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'controlcore', v1.0.4 by Infinite Automation
                      INFO 2014-08-14 15:20:14,757 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dataFile', v1.0.4 by Infinite Automation
                      INFO 2014-08-14 15:20:14,871 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dataImport', v1.3.4 by Infinite Automation Software
                      INFO 2014-08-14 15:20:14,886 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dglux', v1.0.11 by Infinite Automation Software
                      INFO 2014-08-14 15:20:14,907 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dnp3', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:20:14,974 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'galil', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:20:14,985 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'graphicalViews', v1.4.8 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,186 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'http', v1.4.6 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,227 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'internal', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,232 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'jmxds', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,237 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'jspViews', v2.0.3 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,415 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'log4JReset', v1.0.5 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,421 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'loggingConsole', v1.0.1 by Infinite Automation
                      INFO 2014-08-14 15:20:15,422 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'maintenanceEvents', v1.4.7 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,448 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'mbus', v1.0.4 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,450 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'meta', v2.0.7 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,491 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'modbus', v1.4.8 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,524 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'onewire', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,529 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'opcda', v1.5.5 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,540 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'openv4j', v1.0.4 by aploese
                      INFO 2014-08-14 15:20:15,543 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pachube', v1.4.7 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,565 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'persistent', v1.4.6 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,588 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pid', v1.0.2 by Infinite Automation
                      INFO 2014-08-14 15:20:15,593 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pointLinks', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,596 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pop3', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,600 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'reports', v2.0.6 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,606 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'scheduledEvents', v1.4.6 by (unknown vendor)
                      INFO 2014-08-14 15:20:15,612 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'scripting', v1.0.7 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,629 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'serial', v1.1.2 by Infinite Automation
                      INFO 2014-08-14 15:20:15,635 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'snmp', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,640 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sqlConsole', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,650 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sqlds', v1.5.5 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,657 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sstGlobalScripts', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,662 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sstGraphics', v1.0.5 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,663 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sstTheme', v1.0.5 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,664 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'templateConfig', v1.0.4 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,692 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'twilio', v1.0.3 by (unknown vendor)
                      INFO 2014-08-14 15:20:15,697 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'virtualDS', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,703 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'vmstat', v1.4.6 by Infinite Automation Software
                      INFO 2014-08-14 15:20:15,710 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'watchlists', v1.5.7 by Infinite Automation Software
                      INFO 2014-08-14 15:20:19,515 (com.serotonin.m2m2.web.M2M2ContextListener.contextInitialized:31) - Mango Automation context starting
                      INFO 2014-08-14 15:20:19,526 (com.serotonin.m2m2.web.M2M2ContextListener.contextInitialized:39) - Mango Automation context started
                      INFO 2014-08-14 15:20:20,594 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/users.shtm] onto handler 'usersController'
                      INFO 2014-08-14 15:20:20,656 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source.shtm] onto handler 'dataSourceController'
                      INFO 2014-08-14 15:20:20,761 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/publisher_edit.shtm] onto handler 'publisherEditController'
                      INFO 2014-08-14 15:20:20,887 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/login.htm] onto handler 'loginController'
                      INFO 2014-08-14 15:20:20,891 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/shutdown.htm] onto handler 'shutdownController'
                      INFO 2014-08-14 15:20:21,029 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source_properties.shtm] onto handler 'dataSourcePropertiesController'
                      INFO 2014-08-14 15:20:21,031 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/startup.htm] onto handler 'startupController'
                      INFO 2014-08-14 15:20:21,090 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/webcam_live_feed.htm] onto handler 'webcamLiveFeedController'
                      INFO 2014-08-14 15:20:21,091 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/unauthorized.htm] onto handler 'unauthorizedController'
                      INFO 2014-08-14 15:20:21,092 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_point_edit.shtm] onto handler 'dataPointEditController'
                      INFO 2014-08-14 15:20:21,143 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source_properties_error.shtm] onto handler 'dataSourceErrorController'
                      INFO 2014-08-14 15:20:21,144 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_source_edit.shtm] onto handler 'dataSourceEditController'
                      INFO 2014-08-14 15:20:21,144 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/users.shtm] onto handler 'usersController'
                      INFO 2014-08-14 15:20:21,201 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile.shtm] onto handler 'mobileController'
                      INFO 2014-08-14 15:20:21,202 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/help.shtm] onto handler 'helpController'
                      INFO 2014-08-14 15:20:21,205 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/logout.htm] onto handler 'logoutController'
                      INFO 2014-08-14 15:20:25,315 (com.serotonin.m2m2.Lifecycle.lic:404) - Checking license...
                      INFO 2014-08-14 15:20:25,317 (com.serotonin.m2m2.Lifecycle.loadLic:519) - License file not found
                      INFO 2014-08-14 15:20:25,808 (com.serotonin.m2m2.db.H2Proxy.initializeImpl:37) - Initializing H2 connection manager
                      INFO 2014-08-14 15:20:34,743 (com.serotonin.m2m2.db.upgrade.DBUpgrade.checkUpgrade:36) - Starting instance with core version 2.4.0, db 9
                      INFO 2014-08-14 15:20:41,805 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                      INFO 2014-08-14 15:20:41,947 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.modbus.dwr.ModbusEditDwr
                      INFO 2014-08-14 15:20:41,961 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                      INFO 2014-08-14 15:20:41,972 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                      INFO 2014-08-14 15:20:41,983 (com.serotonin.m2m2.Lifecycle.configureDwr:822) - Duplicate definition of DWR class ignored: br.org.scadabr.dnp3.dwr.DnpEditDwr
                      INFO 2014-08-14 15:20:42,101 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_point_details.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,103 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/events.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,104 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/pending_alarms.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,105 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/event_handlers.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,106 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/data_sources.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,107 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/point_hierarchy.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,110 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mailing_lists.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,111 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/publishers.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,113 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/system_settings.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,115 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/modules.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,116 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/emport.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,118 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/upload.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,119 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/download.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,120 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile_data_point_details.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,121 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/logging_console.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,121 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/templateConfig.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,129 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/dataImport.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,132 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/dglux.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,135 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/dglux/login.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,139 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/views.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,142 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/public_view.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,144 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/view_edit.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,144 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/maintenance_events.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,145 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/point_links.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,149 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/reportChart.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,149 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/reports.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,150 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/scheduled_events.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,165 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/sqlConsole.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,167 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/globalScripts.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,173 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/watch_list.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,191 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/login.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,249 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/watch_list.shtm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:20:42,281 (org.springframework.web.servlet.handler.AbstractUrlHandlerMapping.registerHandler:411) - Mapped URL path [/mobile/logout.htm] onto handler of type [class com.serotonin.m2m2.web.mvc.UrlHandlerController]
                      INFO 2014-08-14 15:22:17,683 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'abeip', v1.0.6 by Deltamation Software
                      INFO 2014-08-14 15:22:17,701 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'abpccc', v1.0.4 by Deltamation Software
                      INFO 2014-08-14 15:22:17,706 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'asciiFile', v1.1.3 by Infinite Automation
                      INFO 2014-08-14 15:22:17,737 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'BACnet', v2.1.0 by Infinite Automation Software
                      INFO 2014-08-14 15:22:17,743 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'controlcore', v1.0.4 by Infinite Automation
                      INFO 2014-08-14 15:22:17,748 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dataFile', v1.0.4 by Infinite Automation
                      INFO 2014-08-14 15:22:17,765 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dataImport', v1.3.4 by Infinite Automation Software
                      INFO 2014-08-14 15:22:17,773 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dglux', v1.0.11 by Infinite Automation Software
                      INFO 2014-08-14 15:22:17,776 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'dnp3', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:22:17,825 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'galil', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:22:17,872 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'graphicalViews', v1.4.8 by Infinite Automation Software
                      INFO 2014-08-14 15:22:17,981 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'http', v1.4.6 by Infinite Automation Software
                      INFO 2014-08-14 15:22:17,986 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'internal', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:22:17,991 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'jmxds', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:22:17,997 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'jspViews', v2.0.3 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,101 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'log4JReset', v1.0.5 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,105 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'loggingConsole', v1.0.1 by Infinite Automation
                      INFO 2014-08-14 15:22:18,108 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'maintenanceEvents', v1.4.7 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,115 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'mbus', v1.0.4 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,116 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'meta', v2.0.7 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,121 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'modbus', v1.4.8 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,126 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'onewire', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,132 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'opcda', v1.5.5 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,134 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'openv4j', v1.0.4 by aploese
                      INFO 2014-08-14 15:22:18,146 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pachube', v1.4.7 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,156 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'persistent', v1.4.6 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,165 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pid', v1.0.2 by Infinite Automation
                      INFO 2014-08-14 15:22:18,172 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pointLinks', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,176 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'pop3', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,182 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'reports', v2.0.6 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,192 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'scheduledEvents', v1.4.6 by (unknown vendor)
                      INFO 2014-08-14 15:22:18,263 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'scripting', v1.0.7 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,315 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'serial', v1.1.2 by Infinite Automation
                      INFO 2014-08-14 15:22:18,321 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'snmp', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,325 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sqlConsole', v1.4.4 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,329 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sqlds', v1.5.5 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,332 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sstGlobalScripts', v1.4.5 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,335 (com.serotonin.m2m2.Main.loadModules:399) - Loading module 'sstGraphics', v1.0.5 by Infinite Automation Software
                      INFO 2014-08-14 15:22:18,336
                        All I see is Modbus messages going out and no responses coming back.
                        I would put another serial port on the end of the Modbus network and use a Modbus or serial sniffer program to watch the actual traffic on the network. Also you should ideally be using an serial adapter with RX / TX lights, can you confirm that the TX light flashes when the read command is given.
                        • E Offline
                          edmond
                          yes,When I click" read data "button and the usb(virual com port) adapter will flashes.but no data return and display"No response from slave 1".
                          • jeremyhJ Offline
                            jeremyh
                            In one of your other threads (good luck finding it) I pointed out that you need to actually change the weather station to Modbus mode before you can read data using Modbus. Have you definitely done that?
                            • E Offline
                              edmond
                              yes.I am sure now the wind sensor mode is modbus mode. and I can received the data from modbus scan software. But mango is not ok.
                              • jeremyhJ Offline
                                jeremyh
                                Show me where you are receiving the modbus data over serial using Modscan?
                                @jeremyh said:
                                @edmond said:
                                and can received data use modscan32 software.
                                Modscan doesn't receive any data..
                                Your equipment is not set up correctly
                                • E Offline
                                  edmond
                                  as show in the attachment . I use other device via modbus ip to received data .
                                  and display mango and modbus scan software as below.
                                  • E Offline
                                    edmond
                                    now I modify the connection to rs 485 .
                                    and I test again
                                    display "argument type mismatch"
                                    many data 32 bit float.and mango have no this option.
                                    • jeremyhJ Offline
                                      jeremyh
                                      32 bit = 4 byte
                                      and I test again
                                      What did you expect? That your RS232 adapter would turn into a RS485 adapter? :shock:
                                      • E Offline
                                        edmond
                                        in wind sensor side ,have two type:rs422 or rs485,
                                        before the connection always is rs 422, and I change a adapter to rs485 to test to see have any changing.
                                        • E Offline
                                          edmond
                                          and I test serval times.
                                          and display"Exception from modbus master:CRC mismatch:given=1536,calc=8432"
                                          • hussamH Offline
                                            hussam
                                            as your attachment, the modscan32 don't receive any value?don't you know what's mean valid slave responses:0?