    44 Posts 4 Posters 63.3k Views 4 Watching
    • danD Offline
      dan
      Then this one
        does 0x02 not work? it's asking for a string as well... is the datatype not an integer?
        • danD Offline
          dan
          I think it's wanting '2' then '35702' written into 4104 and 4105 respectively, both at once using function 16 multiple write.
          Here's an excerpt from the manual for what they're getting at..
          1. One of the system control keys from the table below must be written into register 8 and its ones-compliment written into register 9
            with a single function 16 (write multiple registers) to perform the specified system control function.
          2. Writing any other value or using a function that is not available will return extended exception code 7 (Illegal value written to
            register) and have no affect.
          The table looks like this..
            @dan said in A Bit Stuck on Writing Multiple MODBUS Registers:
            35702
            I've entered it in like this since the values are a different length:
            • danD Offline
              dan
              Oh, that makes more sense :)
              I'll try that, thanks heaps.
              • danD Offline
                dan
                  That doesn't give you much to work with does it??
                  I got this working!
                  • danD Offline
                    dan
                    oh yeh, that's interesting, I'll try the coils.
                    Cheers for that hey.
                    • danD Offline
                      dan
                      FML...
                      It does say Control Registers at the top of the info page..
                        So it's a nope? - note your 0x2 should be 0x02
                        • danD Offline
                          dan
                          Na I don't think I can write to coils on this device.
                            write
                            4104
                            0
                            2
                            ASCII
                            0x8B76,0x8B76
                            That sets that control key and calls function 2
                              Hi Dan
                              Ive run into similar situations before with modbus device.
                              Make sure your data source has Use multiple write commands only checked.
                              Modbus function 16 writes to holding registers
                              Use a 4 byte unsigned int.
                              I believe the decimal number would be 166774:
                              Turn on the log I/O of the data source so you can inspect the modbus commands.
                              There may be a chance you might need to use a 4 byte unsigned int swapped
                              If you dont come right paste your I/O commands here.
                              • danD Offline
                                dan
                                Hi Craig, I've definitely got multiple writes selected in the data source.
                                I might have to re-visit the calculator / converter looking at that number. I was just sending it the raw hex value.
                                I'll give it a go. Thanks :)
                                  Hey Dan
                                  Did a quick tet for you. I believe it is correct checkout the snapshot I took from Wireshark:
                                  Something to note about modbus is that sometime in manuals they will prefix the register number with the register type. Holding register is decimal 4. So when you see that on a manual you will just put offset 104 in mango. You will also see that some manual are 0 based and some are 1 based. So you might need to try 103 instead of 104.
                                  Below is the settings I used for my point. I used decimal 166774
                                    Ok, so I can understand using 166774 gives you 0x00028b76, basically just bit shifts the entire thing in. And that by using a holding register implicitly puts a 4 in the front so only 104 is needed... But if the manual states you need a control key into 8 and its 1's complement into register 9, shouldn't it be 0x8B768B76 = 2339801974 DEC?
                                    • danD Offline
                                      dan
                                      OK, now my brain is really hurting, I'll turn on the i/o log and see what mine is outputting.
                                      Just to clarify a little further, the MODBUS register I need to write to is on 'Page 16', the manual says to multiply 256 x Page then add the Offset, so in this case I'm on (256 x 16) + 8 = 4104
                                      When reading off battery voltages and other engine diagnostics off this the formula seems to work.
                                      I'll try again with the decimal.
                                      • danD Offline
                                        dan
                                        • danD Offline
                                          dan
                                          Interestingly, when I write the hex values I get this pop up error..
                                          Nothing written in the log during this time however :/
                                          • cwangvC Offline
                                            cwangv @dan
                                            @dan
                                            just curious why the 'Number of registers' is '0'? shouldn't be at least '1'?