    44 Posts 4 Posters 63.3k Views 4 Watching
    • danD Offline
      dan
      FML...
      It does say Control Registers at the top of the info page..
        So it's a nope? - note your 0x2 should be 0x02
        • danD Offline
          dan
          Na I don't think I can write to coils on this device.
            write
            4104
            0
            2
            ASCII
            0x8B76,0x8B76
            That sets that control key and calls function 2
              Hi Dan
              Ive run into similar situations before with modbus device.
              Make sure your data source has Use multiple write commands only checked.
              Modbus function 16 writes to holding registers
              Use a 4 byte unsigned int.
              I believe the decimal number would be 166774:
              Turn on the log I/O of the data source so you can inspect the modbus commands.
              There may be a chance you might need to use a 4 byte unsigned int swapped
              If you dont come right paste your I/O commands here.
              • danD Offline
                dan
                Hi Craig, I've definitely got multiple writes selected in the data source.
                I might have to re-visit the calculator / converter looking at that number. I was just sending it the raw hex value.
                I'll give it a go. Thanks :)
                  Hey Dan
                  Did a quick tet for you. I believe it is correct checkout the snapshot I took from Wireshark:
                  Something to note about modbus is that sometime in manuals they will prefix the register number with the register type. Holding register is decimal 4. So when you see that on a manual you will just put offset 104 in mango. You will also see that some manual are 0 based and some are 1 based. So you might need to try 103 instead of 104.
                  Below is the settings I used for my point. I used decimal 166774
                    Ok, so I can understand using 166774 gives you 0x00028b76, basically just bit shifts the entire thing in. And that by using a holding register implicitly puts a 4 in the front so only 104 is needed... But if the manual states you need a control key into 8 and its 1's complement into register 9, shouldn't it be 0x8B768B76 = 2339801974 DEC?
                    • danD Offline
                      dan
                      OK, now my brain is really hurting, I'll turn on the i/o log and see what mine is outputting.
                      Just to clarify a little further, the MODBUS register I need to write to is on 'Page 16', the manual says to multiply 256 x Page then add the Offset, so in this case I'm on (256 x 16) + 8 = 4104
                      When reading off battery voltages and other engine diagnostics off this the formula seems to work.
                      I'll try again with the decimal.
                      • danD Offline
                        dan
                        • danD Offline
                          dan
                          Interestingly, when I write the hex values I get this pop up error..
                          Nothing written in the log during this time however :/
                          • cwangvC Offline
                            cwangv @dan
                            @dan
                            just curious why the 'Number of registers' is '0'? shouldn't be at least '1'?
                              It's greyed out and disabled.
                                Hi Dan
                                Regarding the address, I think you are correct. Well since other address work you are correct. If 4104 is not working I would try 4103.
                                I think @MattFox is correct regarding the ones's compliment that needs to be written to address 9. I get a different number tho.
                                  I think your answer is right here craig, something is amiss with how I did it, but looking at it now, I think we're all starting to break the back of it.
                                  • danD Offline
                                    dan
                                    Hey Guys, thanks again for helping out. That's a big number. I'll give that one a go, I'll try it into 4104 and 4103.
                                    Dan
                                    • danD Offline
                                      dan
                                      Interestingly I get a timeout message if I try writing the whole decimal number to either data point register.
                                      If I change back to a hex value it just comes up with the top blue error again.
                                      • danD Offline
                                        dan
                                        although might actually currently be a timeout in the network, as it's on the top of a mountain in NZ. at the end of a Mimomax link :/
                                        I do believe it's snowing up there currently..
                                        • danD Offline
                                          dan
                                          Bugga, still same timeout message when network is responding better.
                                          com.serotonin.modbus4j.exception.ModbusTransportException: java.net.SocketTimeoutException: connect timed out
                                          If I interrogate a standard read point it works fine.
                                            MattFox @dan
                                            @dan Sounds like I need to make a roadtrip! Haha