    Help getting ma-watch-list-get points into a controller/service
    19 Posts 3 Posters 8.1k Views 3 Watching
    • B Offline
      BobDay
      Thanks, @CraigWeb. To answer your question, yes - I'm not an angular programmer by trade or avocation - while I am reasonably accomplished in javascript, and understand angularjs at a high level, I am not particularly practiced in its nuanced use, and have not previously used components.
      As well, there is further complication :) here, which I've excluded for 'brevity', which seem to require link function, including further CSS decoration on certain attribute values, and click event which toggles a different point.
      • B Offline
        BobDay
        @CraigWeb - if it's helpful, happy to provide a higher level use case for the component, as it were.
        • B Offline
          BobDay
          @CraigWeb @Jared-Wiltshire: Whether or not I should be using components, my problem is, clearly, in not understanding how to access watchlist points. I have read dozens of posts here, but I'm not getting it. Just asking for a little further explanation from IAS.
          The ONLY way I've been successful in accessing <ma-watch-list-get> points is, per last code above, wrapping it in a $rootScope object, and accessing it through injection - even at that, I'm getting flakey async problems unless I timeout more than one seconds.
          What am I doing wrong here?
            • Do not use the ng-controller attribute
            • Do not use module.controller()
            • Don't set properties on the $rootScope
            • Prefer .controller({opts}) instead of .directive(function() { return {opts}; })
            • Instead of controller: 'PushCtrl' use controller: ['$scope', function($scope) { // do something }] or (my preference):
            class PushCtrl {
              static get $$ngIsClass() { return true; }
              static get $inject() { return ['$scope']; }
              constructor($scope) {
                this.$scope = $scope;
            // then
            .controller: PushCtrl // no single quotes
            Basically the way you are using the PushCtrl controller in ng-controller then also as the controller for the <push-lamp> directive makes no sense. And <push-lamp points="point" is never going to work as it is the wrong variable name.
              Also use the $onChanges() hook of the controller rather than setting a timeout.
                Basically I think it boils down to this -
                <div ng-init="page = {}"></div>
                <ma-watch-list-get ng-model="indicatorWl.watchlist" parameters="indicatorWl.parameters" on-points-change="page.points = $points" id="wl-indicator-id" watch-list-xid="WL_Indicator"></ma-watch-list-get>
                <ma-get-point-value points="page.points"></ma-get-point-value>
                <div>
                    <push-lamp point="page.points | filter:{xid:'DP_ind_H2OT1'}:true | maFirst"></push-lamp>
                    <push-lamp point="page.points | filter:{xid:'DP_ind_H2OT2'}:true | maFirst"></push-lamp>
                    <push-lamp point="page.points | filter:{xid:'DP_ind_H2OT3'}:true | maFirst"></push-lamp>
                    <push-lamp point="page.points | filter:{xid:'DP_ind_H2OMX'}:true | maFirst"></push-lamp>
                User module:
                module.component('pushLamp', {
                      template: `<div class="indicator" ng-class="$ctrl.point.renderedValue"
                        <br/>{{$ctrl.point.xid}}; {{$ctrl.point.name}}<br/>{{$ctrl.point.tags.indText}}</div>`,
                      bindings: {
                        point: '<'
                • B Offline
                  BobDay
                  Thank you @Jared-Wiltshire. interesting. Ok I'll give it a try. Could you clarify the use of $onChanges() with the controller? would it be in this case
                  $onChanges($ctrl.point) {...}
                    Jared Wiltshire @BobDay
                    @bobday
                    $onChanges(changes) {
                      if (changes.point) {
                        // point changed
                    Have a read of https://docs.angularjs.org/guide/component for more details.
                    • B Offline
                      BobDay
                      aha. thanks. I also have to toggle a different binary point when this element is clicked. Do I need to use the api to do that, or is there a different way to set a point's value (which point's xid can be passed in as an attr of the <push-lamp> or calculated? and, would I just include that function in the component's controller? Thank you - I'm drinking 1.5 from a firehose (and Tom Motto!)
                      • B Offline
                        BobDay
                        Thanks very much - that all worked.
                        <div class="ma-designer-root" id="30987a71-8c32-4308-a9ae-3fdff231c44b" style="width: 1366px; height: 768px; position: relative;">
                        <div>
                        user module:
                          'use strict';
                          var userModule = angular.module('userModule', ['maUiApp'])
                              template: `<div class="indicator" ng-click="$ctrl.pushed(this.$ctrl.point.xid)" ng-class="$ctrl.point.renderedValue"<br/>{{$ctrl.point.xid}}; {{$ctrl.point.name}}<br/>{{$ctrl.point.tags.indText}}</div>`,
                              bindings: {
                                point: '<'
                              controller: function() {
                                var self = this;
                                self.$onChanges = function (changes) {
                                    console.log(self.point.value);
                                self.pushed = function(pid) {
                                  var swXid = 'DP_sw_' + pid.substr(7);
                                  // toggle point.xid=swXid
                                  console.log(swXid, ' was clicked');
                          return userModule;
                        }); // define
                        If I could just get your opinion on preferred way to toggle point... also would appreciate any comments on view syntax/order.
                        Best.
                          @bobday said in Help getting ma-watch-list-get points into a controller/service:
                          You should use the maPoint class' toggleValue() method. So in your controller's pushed() method you could just call self.point.toggleValue() or self.point.setValue(true) etc.
                          However I note that you want to toggle a different point, so I would suggest this-
                          • Change your point attribute/binding to points and pass the whole points array though
                          • Locate the two points you wish to use in the $onChanges() method when the points array changes
                          So bringing it together -
                            'use strict';
                                template: `<div class="indicator" ng-click="$ctrl.pushed()" ng-class="$ctrl.point.renderedValue">
                                  {{$ctrl.point.xid}}<br>{{$ctrl.point.name}}<br>{{$ctrl.point.tags.indText}}
                                </div>`,
                                bindings: {
                                  points: '<',
                                  target: '@'
                                  this.$onChanges = function (changes) {
                                    if (changes.points && Array.isArray(this.points)) {
                                      this.point = this.points.find(p => p.xid === 'DP_ind_' + this.target);
                                      this.switchPoint = this.points.find(p => p.xid === 'DP_sw_' + this.target);
                                  this.pushed = function() {
                                      if (this.switchPoint) {
                                          this.switchPoint.toggleValue();
                            return userModule;
                          }); // define
                          PS the template was not properly formed and you had an extra this. at the front of this expression -
                          Suggestions -
                          • Find the points via tags rather than by XIDs (In the past we relied on encoding information into the XID, however with the advent of tags we can do this more easily)
                          • Use an ES6 class for the controller as per my previous post
                          • B Offline
                            BobDay
                            @Jared-Wiltshire - thanks for all that. That works if I put the switchpoints on the watchlist of course - I hadn't thought of that - I was looking for the correct method to get/set a point directly.
                            I'm still not getting the point.value or any of the other properties added via <ma-point-value> in the bound points variable via $ctrl. Odd, though, if I log this.point, everything shows up in the object - just shows undefined if I try to access this.point.value. Shows up via template though.
                            I'm stumped...
                            <div>
                                <push-lamp points="page.points" target="H2OT1"></push-lamp>
                                <push-lamp points="page.points" target="H2OT2"></push-lamp>
                            console.log(this.point.xid, this.point.value);
                            //console:
                            DP_ind_H2OT1 undefined
                            DP_ind_H2OT2 undefined
                            console.log(this.point);
                            //console:
                            {id: 164, xid: "DP_ind_H2OT1", name: "T1-Water", enabled: true, deviceName: "buttonTest", …}
                            chartColour: ""
                            chartRenderer: {timePeriod: {…}, type: "chartRendererImage"}
                            convertedValue: 13
                            dataSourceEditRoles: []
                            dataSourceId: 33
                            dataSourceName: "buttonTest"
                            dataSourceTypeName: "VIRTUAL"
                            dataSourceXid: "DS_buttonTest"
                            enabled: true
                            lastPayload: {xid: "DP_ind_H2OT1", event: "UPDATE", value: {…}, renderedValue: "green", convertedValue: 13, …}
                            loggingProperties: {loggingType: "INTERVAL", intervalLoggingType: "AVERAGE", intervalLoggingPeriod: {…}, tolerance: 0, discardExtremeValues: false, …}
                            originalId: "DP_ind_H2OT1"
                            plotType: "SPLINE"
                            pointFolderId: 0
                            pointLocator: {offset: 0, min: 12, max: 53, period: 0, values: Array(0), …}
                            preventSetExtremeValues: false
                            purgeOverride: false
                            readPermission: ""
                            renderedColor: "#32cd32"
                            rollup: "NONE"
                            running: true
                            setPermission: ""
                            simplifyTarget: 5000
                            simplifyTolerance: 10
                            simplifyType: "NONE"
                            tags: {indText: "H2O", loc: "tank1", xid: "vm.pid", type: "indicator"}
                            templateXid: null
                            textRenderer: {useUnitAsSuffix: false, format: "0", rangeValues: Array(6), type: "textRendererRange"}
                            time: 1574382356912
                            unit: ""
                            unreliable: false
                            useIntegralUnit: false
                            useRenderedUnit: false
                            value: 13
                            xid: "DP_ind_H2OT1"
                            _textRenderer: {rangeValues: Array(6)}
                            dataType: (...)
                            isEnabled: (...)
                            tagsString: (...)
                            valueGetterSetter: (...)
                            __proto__: Object
                            EDIT Indeed, when looping through this.point (from within the controller),
                            angular.forEach(this.point, function(value, key){
                                          console.log(key + ':', value);
                            none of the point-value properties exist in the point object:
                            //console
                            xid: DP_ind_H2OT1
                            enabled: true
                            deviceName: buttonTest
                            readPermission:
                            setPermission:
                            pointFolderId: 0
                            unit:
                            chartColour:
                            plotType: SPLINE
                            rollup: NONE
                            simplifyType: NONE
                            templateXid: null
                            dataSourceId: 33
                            dataSourceXid: DS_buttonTest
                            dataSourceName: buttonTest
                            dataSourceTypeName: VIRTUAL
                            tags: {indText: "H2O", loc: "tank1", type: "indicator"}
                            originalId: DP_ind_H2OT1
                            Assume I have a scoping or async issue, but can't seem to solve it.
                            I'll follow your suggestions when I have this licked - thank you!
                              You can definitely still just fetch the datapoint by XID using the maPoint service. But you would also then have to get its current value before setting the new value...
                              OK, I'm not following exactly where you are putting the console.log() statements so it is pretty hard for me to say what is happening. The first block of output you posted does have a value property, and it looks like it is from inside the component controller as you used console.log(this.point); if this was in the template it would be $ctrl.point.
                              Do this -
                              • Put <pre ng-bind="page.points[0].value"></pre> in your page and verify it has a value
                              • Put a console.log(this.point.value) inside your component controller's pushed() method and verify it has a value, you probably cant do this in the $onChanges() method as it may not have a value at that time
                              • Put <pre ng-bind="$ctrl.point.value"></pre> in your component template and verify it has a value
                              • B Offline
                                BobDay
                                @Jared-Wiltshire Ok - sorry for the confusion.
                                <pre ng-bind="page.points[0].value"></pre> renders the value on the page;
                                console.log(this.point.value) in pushed() renders the value when element is clicked;
                                <pre ng-bind="$ctrl.point.value"></pre> in template renders the value, (as well as does {{$ctrl.point.value}});
                                @Jared-Wiltshire said: ...The first block of output you posted does have a value property, and it looks like it is from inside the component controller as you used console.log(this.point);
                                Yes, however, this from SO:
                                The output of console.log(anObject) is misleading; the state of the object displayed is only resolved when you expand the > in the console. It is not the state of the object when you console.log'd the object.
                                ...which I learned 3 years ago, but completely forgot!
                                using console.log(JSON.stringify(this.point) (inside the controller) returns:
                                {"id":169,"xid":"DP_ind_H2OMX","name":"MX-Water","enabled":true,"deviceName":"buttonTest","readPermission":"","setPermission":"","pointFolderId":0,"purgeOverride":false,"unit":"","useIntegralUnit":false,"useRenderedUnit":false,"pointLocator":{"offset":0,"min":12,"max":53,"period":0,"values":[],"change":10,"startValue":"12","maxChange":0,"volatility":0,"roll":false,"amplitude":0,"phaseShift":0,"attractionPointXid":"DP_ch_current","modelType":"PL.VIRTUAL","changeType":"INCREMENT_ANALOG","dataType":"NUMERIC","settable":false,"relinquishable":false},"chartColour":"","plotType":"SPLINE","loggingProperties":{"loggingType":"INTERVAL","intervalLoggingType":"AVERAGE","intervalLoggingPeriod":{"periods":1,"type":"MINUTES"},"tolerance":0,"discardExtremeValues":false,"overrideIntervalLoggingSamples":false,"cacheSize":1},"textRenderer":{"useUnitAsSuffix":false,"format":"0","rangeValues":[{"from":0,"to":9,"text":"off","colour":null},{"from":10,"to":19,"text":"green","colour":"green"},{"from":20,"to":29,"text":"yellow","colour":"yellow"},{"from":30,"to":39,"text":"red","colour":"red"},{"from":40,"to":49,"text":"blue","colour":"blue"},{"from":50,"to":59,"text":"white","colour":"#cdcdcd"}],"type":"textRendererRange"},"chartRenderer":{"timePeriod":{"periods":1,"type":"DAYS"},"type":"chartRendererImage"},"rollup":"NONE","simplifyType":"NONE","simplifyTolerance":10,"simplifyTarget":5000,"preventSetExtremeValues":false,"templateXid":null,"dataSourceId":33,"dataSourceXid":"DS_buttonTest","dataSourceName":"buttonTest","dataSourceTypeName":"VIRTUAL","dataSourceEditRoles":[],"tags":{"indText":"H2O","loc":"mixer","type":"indicator"},"originalId":"DP_ind_H2OMX"}
                                clearly without the value, etc. properties.
                                EDIT Solved - I think ;-). The reason the .value shows up in pushed() is that it is on the object by the time the element is clicked, while not so, immediately after the controller. console.log places a static prototype on the console, but does not evaluate its properties until the triangle is clicked, per the comment above. Putting the log in a $timeout solved the problem. The console.log is a bit of red herring here, as it all works in the template so far...
                                Apologies for the lack of diligence on my part.
                                Incidentally, what is the reason for the array check in:
                                if (changes.points && Array.isArray($ctrl.points))?
                                  Glad you got it sorted. The array check is simply to ensure that you passed the correct object to the attribute, also a check against undefined values which might happen if you set the attribute to a variable name which might not be set initially.
                                  • B Offline
                                    BobDay
                                    Thanks for all the help.