    How to configure email?
    emailsmtpreportsstarttls
    13 Posts 4 Posters 3.9k Views 4 Watching
      jflores13
      I am trying to set up the email so I can start making excel reports testing, but when I try to send the test email, I get the following event:
      "Failed to send email titled "Mango test email" to "xxxx@xxxxx.com". Message: "Failed messages: com.sun.mail.smtp.SMTPSendFailedException: 530 5.7.0 Must issue a STARTTLS command first. r1sm31895728oti.44 - gsmtp " "
      My settings are as follows:
      SMTP host: smpt.gmail.com, port 25. (Port 465 is closed)
      No TLS. Use Authorization.
      Do I need to do something else, power cycle the MangoES or something random?
      Thanks!
        @jflores13 said in How to configure email?:
        This indicates that you need to enable TLS.
          jflores13 @Jared Wiltshire
          Hey thanks @jared-wiltshire, I did try that before posting here, and I just tried again checking the TLS box, saving the conf, and clicking the "send test email button". Half-success. For some reason now it does try to log in but the error has to do with Google not allowing access to the application because it "doesn't meet the security requirements".
          I know now this doesn't have to do specifically with Mango, but do you happen to know how to overcome this easily?
            Jared Wiltshire @jflores13
            Can you post the full error output please.
            Mango does work fine with Google, personally I use port 587 and TLS. It depends on your account though - https://support.google.com/a/answer/176600?hl=en
              @jared-wiltshire
              I just managed to solve the rest of the issue. Being logged in, I clicked the profile pic, then Google Account/Security, then on the section of "Less secure app access" and turned that from "Don't allow" (recommended) to "Allow" (not recommended), and now it worked.
              Thanks for your replies, Jared.
                Interesting, I can't even see that setting. I am using a G-Suite account with 2FA turned on so I have a "device password" configured for Mango.
                edit. It does seem like it is dependent on your G-Suite admin allowing you to see the "less secure access" setting and with 2FA enabled its different again - https://devanswers.co/allow-less-secure-apps-access-gmail-account/
                  @jared-wiltshire I see.
                  Why would Google say that Mango doesn't use modern security standards and, as a result, is "easier to break into"?
                  And so, if I used 2 Step Verification I'd need to create an app password for mango and then use that one as the email account's password?
                    I have no idea. They don't give any technical details on their help page - https://support.google.com/accounts/answer/6010255?hl=en
                    All I know is I can use TLS to port 587 on smtp.gmail.com and it works fine without me changing any "Less secure app access" settings. I use 2FA and a device password.
                    Correct.
                      @jared-wiltshire Alright, I will try to enable the 2FA and use that port instead. Thanks again!
                        JAST
                        We are encountering a similar issue with emailing reports on Mango3.6.3
                        It is a gmail account, all settings appear to be correct (TLS, SMTP 587,, less secure apps allowed, IMAP enabled) When sending a test email) We keep getting an error but are not seeing anything on the log to further debug this.
                        INFO  2020-02-17T12:28:48,166 (com.serotonin.m2m2.Main.main:105) - Starting Mango 3.6.3 with Schema Version: 28
                        INFO  2020-02-17T12:28:48,756 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'asciiFile', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,766 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'BACnet', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,770 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'controlcore', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,773 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'dashboardDesigner', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,774 (com.serotonin.m2m2.util.DocumentationManifest.parseManifestFile:60) - Documentation manifest file not found: C:\Mango\web\modules\dashboardDesigner\web\dox\manifest.xml
                        INFO  2020-02-17T12:28:48,776 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'dataFile', v3.6.1 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,784 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'dataImport', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,786 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'deviceConfig', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,788 (com.serotonin.m2m2.util.DocumentationManifest.parseManifestFile:60) - Documentation manifest file not found: C:\Mango\web\modules\deviceConfig\web\dox\manifest.xml
                        INFO  2020-02-17T12:28:48,789 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'dnp3', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,793 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'egauge', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,796 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'envcands', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,798 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'excelReports', v3.6.1 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,808 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'graphicalViews', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,831 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'Haystack', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,834 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'http', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,838 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'jsonFileImport', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,840 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'log4jDS', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,843 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'log4JReset', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,844 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'loggingConsole', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,846 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'maintenanceEvents', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,849 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'mangoApi', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,853 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'mangoUI', v3.6.2 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,854 (com.serotonin.m2m2.util.DocumentationManifest.parseManifestFile:60) - Documentation manifest file not found: C:\Mango\web\modules\mangoUI\web\dox\manifest.xml
                        INFO  2020-02-17T12:28:48,874 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'mbus', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,877 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'meta', v3.6.1 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,880 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'modbus', v3.6.2 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,883 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'onewire', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,886 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'opcda', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,887 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'pakbus', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,891 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'pointLinks', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,895 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'pop3', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,898 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'reports', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,902 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'scheduledEvents', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,905 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'scripting', v3.6.2 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,907 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'serial', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,910 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'snmp', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,913 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'sqlConsole', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,915 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'sqlds', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,918 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'ssh', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,920 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'sstGlobalScripts', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,923 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'sstGraphics', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,933 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'TCPIP', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,936 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'templateConfig', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,939 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'twilio', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,942 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'virtualDS', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,944 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'vmstat', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,948 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'watchlists', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:48,954 (com.serotonin.m2m2.Main.loadModules:586) - Loading module 'internal', v3.6.0 by Infinite Automation Systems Inc.
                        INFO  2020-02-17T12:28:50,584 (com.serotonin.m2m2.Lifecycle.loadLic:611) - Checking license...
                        INFO  2020-02-17T12:28:50,658 (com.serotonin.m2m2.db.H2Proxy.initializeImpl:61) - Initializing H2 connection manager
                        INFO  2020-02-17T12:28:53,493 (com.serotonin.m2m2.db.upgrade.DBUpgrade.checkUpgrade:38) - Starting instance with core version 3.6.3, schema v28
                        INFO  2020-02-17T12:28:55,306 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:125) - Spring context 'runtimeContext' refreshed: org.springframework.context.annotation.AnnotationConfigApplicationContext@6e3ecf5c
                        INFO  2020-02-17T12:28:55,309 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextStarted:139) - Spring context 'runtimeContext' started: org.springframework.context.annotation.AnnotationConfigApplicationContext@6e3ecf5c
                        INFO  2020-02-17T12:28:55,437 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initialize:176) - Starting 0 Publishers...
                        INFO  2020-02-17T12:28:55,438 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initialize:188) - 0 Publisher's started in 2ms
                        WARN  2020-02-17T12:28:55,885 (org.eclipse.jetty.webapp.StandardDescriptorProcessor.addServletMapping:1220) - Duplicate mapping from *.jsp to jsp
                        INFO  2020-02-17T12:28:56,134 (com.serotonin.m2m2.web.M2M2ContextListener.contextInitialized:32) - Mango Automation context starting
                        INFO  2020-02-17T12:28:56,134 (com.serotonin.m2m2.web.M2M2ContextListener.contextInitialized:40) - Mango Automation context started
                        INFO  2020-02-17T12:28:57,123 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:125) - Spring context 'rootWebContext' refreshed: Root WebApplicationContext
                        INFO  2020-02-17T12:28:57,643 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:125) - Spring context 'jspDispatcherContext' refreshed: WebApplicationContext for namespace 'JSP_DISPATCHER-servlet'
                        INFO  2020-02-17T12:28:57,794 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:125) - Spring context 'rootRestDispatcherContext' refreshed: WebApplicationContext for namespace 'ROOT_REST_DISPATCHER-servlet'
                        INFO  2020-02-17T12:28:58,731 (com.serotonin.m2m2.web.mvc.rest.v1.BacnetDiscoveryRestController.<init>:54) - Creating Discovery Rest Controller
                        INFO  2020-02-17T12:28:59,254 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:125) - Spring context 'restV1DispatcherContext' refreshed: WebApplicationContext for namespace 'restV1DispatcherServlet-servlet'
                        INFO  2020-02-17T12:29:01,348 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:125) - Spring context 'restV2DispatcherContext' refreshed: WebApplicationContext for namespace 'restV2DispatcherServlet-servlet'
                        INFO  2020-02-17T12:29:01,349 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: EnvCanEditDwr
                        INFO  2020-02-17T12:29:01,350 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: HttpDataSourceDwr
                        INFO  2020-02-17T12:29:01,351 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: TcpIpDataSourceEditDwr
                        INFO  2020-02-17T12:29:01,352 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: Pop3EditDwr
                        INFO  2020-02-17T12:29:01,353 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: HaystackDataSourceDwr
                        INFO  2020-02-17T12:29:01,353 (com.serotonin.m2m2.Lifecycle.configureDwr:1267) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                        INFO  2020-02-17T12:29:01,354 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: DataFileDataSourceEditDwr
                        INFO  2020-02-17T12:29:01,356 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: OPCDAEditDwr
                        INFO  2020-02-17T12:29:01,358 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: BACnetMSTPEditDwr
                        INFO  2020-02-17T12:29:01,360 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: PakBusEditDwr
                        INFO  2020-02-17T12:29:01,361 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: MBusEditDwr
                        INFO  2020-02-17T12:29:01,361 (com.serotonin.m2m2.Lifecycle.configureDwr:1267) - Duplicate definition of DWR class ignored: com.infiniteautomation.mango.pakbus.dwr.PakBusEditDwr
                        INFO  2020-02-17T12:29:01,362 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: SNMPEditDwr
                        INFO  2020-02-17T12:29:01,363 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: InternalEditDwr
                        INFO  2020-02-17T12:29:01,364 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: SerialEditDwr
                        INFO  2020-02-17T12:29:01,365 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: MetaEditDwr
                        INFO  2020-02-17T12:29:01,367 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: DnpEditDwr
                        INFO  2020-02-17T12:29:01,368 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: ModbusEditDwr
                        INFO  2020-02-17T12:29:01,369 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: Log4jEditDwr
                        INFO  2020-02-17T12:29:01,370 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: ScriptingEditDwr
                        INFO  2020-02-17T12:29:01,372 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: SshDataSourceEditDwr
                        INFO  2020-02-17T12:29:01,373 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: AsciiFileEditDwr
                        INFO  2020-02-17T12:29:01,373 (com.serotonin.m2m2.Lifecycle.configureDwr:1267) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                        INFO  2020-02-17T12:29:01,375 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: OneWireEditDwr
                        INFO  2020-02-17T12:29:01,376 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: SqlEditDwr
                        INFO  2020-02-17T12:29:01,377 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: VMStatEditDwr
                        INFO  2020-02-17T12:29:01,378 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: EgaugeDataSourceDwr
                        INFO  2020-02-17T12:29:01,378 (com.serotonin.m2m2.Lifecycle.configureDwr:1267) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                        INFO  2020-02-17T12:29:01,380 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: BACnetIPEditDwr
                        INFO  2020-02-17T12:29:01,380 (com.serotonin.m2m2.Lifecycle.configureDwr:1267) - Duplicate definition of DWR class ignored: br.org.scadabr.dnp3.dwr.DnpEditDwr
                        INFO  2020-02-17T12:29:01,381 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: ControlCoreEditDwr
                        INFO  2020-02-17T12:29:01,381 (com.serotonin.m2m2.Lifecycle.configureDwr:1267) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.modbus.dwr.ModbusEditDwr
                        INFO  2020-02-17T12:29:01,381 (com.serotonin.m2m2.Lifecycle.configureDwr:1267) - Duplicate definition of DWR class ignored: com.serotonin.m2m2.http.dwr.HttpDataSourceDwr
                        INFO  2020-02-17T12:29:01,382 (com.serotonin.m2m2.Lifecycle.configureDwr:1274) - Added DWR definition for: VirtualEditDwr
                        INFO  2020-02-17T12:47:09,662 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initializeDataSourceStartup:403) - Data source 'Field Server' initialized
                        INFO  2020-02-17T12:47:09,746 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initializeDataSourceStartup:403) - Data source 'Mango Internal' initialized
                        WARN  2020-02-17T13:10:21,579 (com.serotonin.m2m2.web.dwr.MiscDwr.jsError:167) - Javascript error
                           Description: SyntaxError: unterminated parenthetical
                           Page: http://localhost:8080/resources/view/dataPoint/allDataPoints.js
                           Line: 329
                           Browser name: Firefox
                           Browser version: 72
                           osName: Windows
                           location: http://localhost:8080/data_source_edit.shtm?dsid=
                        WARN  2020-02-17T13:10:22,091 (com.serotonin.m2m2.web.dwr.MiscDwr.jsError:167) - Javascript error
                           Line: 329
                           Browser version: 72
                           osName: Windows
                        WARN  2020-02-17T13:10:26,106 (com.serotonin.m2m2.web.dwr.MiscDwr.jsError:167) - Javascript error
                           Line: 329
                           Browser version: 72
                           osName: Windows
                        WARN  2020-02-17T13:10:26,494 (com.serotonin.m2m2.web.dwr.MiscDwr.jsError:167) - Javascript error
                           Line: 329
                           Browser version: 72
                           osName: Windows
                          You have setup an application only password haven't you?
                            JAST
                            Hi MattFox, not sure what you mean by application only password
                            Are you referring to the mango instance?
                              You need to setup an application only password in gmail for mango to use. Otherwise you are unable to send mail.
