    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
    Radix IoT Website Mango 4 Documentation Website Mango 5 Documentation Website Radix IoT LinkedIn
    BACnetDataSourceRT rejected
    Scheduled Pinned Locked Moved User help
    6 Posts 3 Posters 3.1k Views 2 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • T Offline
      ThienTran
      Dear,
      How can i fix error: 'FCU18-7(5025)': Task com.serotonin.ma.bacnet.BACnetDataSourceRT$1@1d3e309 rejected from java.util.concurrent.ThreadPoolExecutor@2bc823[Running, pool size = 100, active threads = 100, queued tasks = 0, completed tasks = 4381].
      I have config thread High priority core pool size: 1000 and High priority maximum pool size: 1000
      Thanks,
      Tran
      1 Reply Last reply Reply Quote 0
      • JoelHaggarJ Offline
        JoelHaggar
        Increase your high priority thread pool. This can be done in Mango 2.6 and higher on the system settings page. The max setting will depend on your server size and number of BACnet data points but try raising it from 100 to 1000 to start with.
          JoelHaggar
          See this wiki article for more information on the thread pools:
          http://infiniteautomation.com/wiki/doku.php?id=system_admin:threadpools
          • C Offline
            craig
            I have a mangoES and the modules page reports the core is 2.6.0 build 373. I don't see anything to adjust the number of theads or work items on the system settings page? What sub topic is it under.
            I have 4 modbus TCP data sources with a total of less than a hundred points, which may be quite non-contiguous in the PLC memory, and I am finding the polls overlap at 1s read and log frequency, so I have backed it off to 3s but still am getting overlapping polls sometimes.
            the error is:
            Work Item Rejected: Task com.infiniteautomation.nosql.MangoNoSqlBatchWriteBehind rejected from java.util.concurrent.ThreadPoolExecutor@48cec7[Running, pool size = 100, active threads = 100, queued tasks = 0, completed tasks = 6681827] This may indicate a need to increase thread pool maximum size
            I think it is choking any time it goes to a page with a plot on it. A report with 8 points takes 30s to generate and reports. I also got this error which rendered the mangoES unreachable for a couple of hours:
            ERROR 2016-02-16 11:53:10,540 (org.apache.taglibs.log.LoggerTag.doStartTag:97) -
            java.lang.OutOfMemoryError: Java heap space at java.util.Arrays.copyOf(Arrays.java:3356) at
            java.awt.geom.Path2D$Float.needRoom(Path2D.java:302) at
            java.awt.geom.Path2D$Float.lineTo(Path2D.java:373) at org.jfree.chart.renderer
            .xy.XYSplineRenderer.drawPrimaryLineAsPath(XYSplineRenderer.java:265) at org.j
            free.chart.renderer.xy.XYLineAndShapeRenderer.drawItem(XYLineAndShapeRenderer. java:909) at
            org.jfree.chart.plot.XYPlot.render(XYPlot.java:3828) at
            org.jfree.chart.plot.XYPlot.draw(XYPlot.java:3389) at
            org.jfree.chart.JFreeChart.draw(JFreeChart.java:1237) at
            org.jfree.chart.JFreeChart.createBufferedImage(JFreeChart.java:1411) at
            org.jfree.chart.JFreeChart.createBufferedImage(JFreeChart.java:1391) at
            org.jfree.chart.ChartUtilities.writeChartAsPNG(ChartUtilities.java:183) at
            org.jfree.chart.ChartUtilities.writeChartAsPNG(ChartUtilities.java:136) at com
            .serotonin.m2m2.util.chart.ImageChartUtils.writeChart(ImageChartUtils.java:209 ) at
            com.serotonin.m2m2.util.chart.ImageChartUtils.getChartData(ImageChartUtil s.java:64) at
            com.serotonin.m2m2.util.chart.ImageChartUtils.getChartData(Image ChartUtils.java:56) at
            com.serotonin.m2m2.web.servlet.ImageChartServlet.getIma geData(ImageChartServlet.java:219) at
            com.serotonin.m2m2.web.servlet.ImageChar tServlet.doGet(ImageChartServlet.java:69) at
            javax.servlet.http.HttpServlet.service(HttpServlet.java:687) at
            javax.servlet.http.HttpServlet.service(HttpServlet.java:790) at
            org.eclipse.jetty.servlet.ServletHolder.handle(ServletHolder.java:808) at org.
            eclipse.jetty.servlet.ServletHandler$CachedChain.doFilter(ServletHandler.java: 1669) at
            com.serotonin.m2m2.web.filter.UrlRewriteFilter.doFilter(UrlRewriteFil ter.java:63) at
            org.eclipse.jetty.servlet.ServletHandler$CachedChain.doFilter( ServletHandler.java:1652) at
            org.eclipse.jetty.servlets.UserAgentFilter.doFilter(UserAgentFilter.java:83) at
            org.eclipse.jetty.servlets.GzipFilter.doFilter(GzipFilter.java:364) at org.
            eclipse.jetty.servlet.ServletHandler$CachedChain.doFilter(ServletHandler.java: 1652) at
            org.eclipse.jetty.servlet.ServletHandler.doHandle(ServletHandler.java:585) at
            org.eclipse.jetty.server.handler.ScopedHandler.handle(ScopedHandler.java:143) at
            org.eclipse.jetty.security.SecurityHandler.handle(SecurityHandler.java:577) at
            org.eclipse.jetty.server.session.SessionHandler.doHandle(SessionHandler.jav a:223) at
            org.eclipse.jetty.server.handler.ContextHandler.doHandle(ContextHand ler.java:1127) at
            org.eclipse.jetty.servlet.ServletHandler.doScope(ServletHandler.java:515) REQUEST URL
            http://redacted/exception/error.jsp REQUEST PARAMETERS REQUEST HEADERS
            Cookie=MANGO80=1fxiokosn6271cbheycgh136l Accept=image/webp,image/*,*/*;q=0.8 Connection=keep-alive
            User- Agent=Mozilla/5.0 (Windows NT 6.1; WOW64) AppleWebKit/537.36 (KHTML, like Gecko)
            Chrome/48.0.2564.109 Safari/537.36 Referer=http://162.251.73.92:5003/views.shtm?viewId=2
            Host=162.251.73.92:5003 Accept-Encoding=gzip, deflate, sdch Accept-Language=en-US,en;q=0.8 REQUEST
            ATTRIBUTES javax.servlet.forward.context_path= javax.servlet.error.status_code=500
            javax.servlet.forward.servlet_path=/chart
            javax.servlet.jsp.jstl.fmt.localizationContext.request=org.springframework.web
            .servlet.support.JstlUtils$SpringLocalizationContext@13aecc5 javax.servlet.for
            ward.request_uri=/chart/1455646343379_86400000_58_75_67_68_w500_h300.png javax
            .servlet.forward.path_info=/1455646343379_86400000_58_75_67_68_w500_h300.png sessionUser=User [id=1,
            username=admin, password=//vpBU=, email=foo@bar.com, phone=,
            disabled=false, homeUrl=/watch_list.shtm, lastLogin=1455560042957, receiveAlarmEmails=0,
            receiveOwnAuditEvents=false, timezone=, permissions=admin,user,superadmin]
            org.eclipse.jetty.server.error_page=/exception/error.jsp javax.servlet.error.servlet_name=imageChart
            javax.servlet.error.message=java.lang.OutOfMemoryError: Java heap space
            javax.servlet.error.exception_type=class java.lang.OutOfMemoryError javax.serv
            let.error.request_uri=/chart/1455646343379_86400000_58_75_67_68_w500_h300.png
            javax.servlet.jsp.jstl.fmt.locale.request=en_US
            javax.servlet.error.exception=java.lang.OutOfMemoryError: Java heap space SESSION ATTRIBUTES
            sessionUser=User [id=1, username=admin, password=/8LKdlEX076NFvI8QAPKAl/vpBU=,
            email=foo@bar.com, phone=, disabled=false, homeUrl=/watch_list.shtm,
            lastLogin=1455560042957, receiveAlarmEmails=0, receiveOwnAuditEvents=false, timezone=,
            permissions=admin,user,superadmin] LONG_POLL_DATA_TIMEOUT=1455647923501
            LONG_POLL_DATA=[com.serotonin.m2m2.web.dwr.longPoll.LongPollData@2faf9f,
            com.serotonin.m2m2.web.dwr.longPoll.LongPollData@d3788d] CONTEXT ATTRIBUTES
            SystemManagerDwr=com.infiniteautomation.system.SystemManagerDwr@eb5210
            org.eclipse.jetty.server.webapp.ContainerIncludeJarPattern=.*\.jar$
            DataSourceEditDwr=com.serotonin.m2m2.web.dwr.DataSourceEditDwr@1f8b244
            DwrContainer=org.directwebremoting.impl.DefaultContainer@8eb833
            MailingListsDwr=com.serotonin.m2m2.web.dwr.MailingListsDwr@190b5bf
            LocalDeviceDwr=com.serotonin.ma.bacnet.device.LocalDeviceDwr@129174f
            constants.EventType.EventTypeNames.AUDIT=AUDIT constants.SystemEventType.TYPE_USER_LOGIN=USER_LOGIN
            constants.Permissions.DataPointAccessTypes.READ=1 org.directwebremoting.Contai
            nerList=[org.directwebremoting.impl.DefaultContainer@8eb833]
            ModbusEditDwr=com.serotonin.m2m2.modbus.dwr.ModbusEditDwr@1f3fcfc constants.DataTypes.BINARY=1
            constants.UserComment.TYPE_EVENT=1 constants.SystemEventType.TYPE_SYSTEM_STARTUP=SYSTEM_STARTUP
            constants.SystemEventType.TYPE_REJECTED_WORK_ITEM=REJECTED_WORK_ITEM javax.ser
            vlet.ServletConfig=org.eclipse.jetty.servlet.ServletHolder$Config@999691
            javax.servlet.http.HttpServlet=org.directwebremoting.servlet.DwrServlet@78e7b0
            org.eclipse.jetty.tmpdirConfigured=true constants.EventType.EventTypeNames.DATA_POINT=DATA_POINT
            clientSideMessages={c ommon.alarmLevel.lifeSafety=com.serotonin.m2m2.i18n.TranslatableMessage@1c7162
            6, common.disabled=com.serotonin.m2m2.i18n.TranslatableMessage@be9bfeff,
            header.mute=com.serotonin.m2m2.i18n.TranslatableMessage@43df3cba,
            header.unmute=com.serotonin.m2m2.i18n.TranslatableMessage@d635aa93, common.ala
            rmLevel.critical=com.serotonin.m2m2.i18n.TranslatableMessage@2b076d7,
            js.help.related=com.serotonin.m2m2.i18n.TranslatableMessage@3dce6ae3,
            js.help.lastUpdated=com.serotonin.m2m2.i18n.TranslatableMessage@729293fd,
            js.email.addAddress=com.serotonin.m2m2.i18n.TranslatableMessage@cbb9a38a,
            js.help.error=com.serotonin.m2m2.i18n.TranslatableMessage@f876c0,
            js.email.addUser=com.serotonin.m2m2.i18n.TranslatableMessage@49cc77b5,
            js.email.addMailingList=com.serotonin.m2m2.i18n.TranslatableMessage@6fa4a69f,
            js.email.noRecipForEmail=com.serotonin.m2m2.i18n.TranslatableMessage@4b694592,
            common.access.set=com.serotonin.m2m2.i18n.TranslatableMessage@a3e5309b,
            common.access.read=com.serotonin.m2m2.i18n.TranslatableMessage@d8bff83d,
            common.loading=com.serotonin.m2m2.i18n.TranslatableMessage@cf5f0419,
            common.sendTestEmail=com.serotonin.m2m2.i18n.TranslatableMessage@8fd89c9f,
            common.disabledToggle=com.serotonin.m2m2.i18n.TranslatableMessage@d7f89333,
            common.alarmLevel.none=com.serotonin.m2m2.i18n.TranslatableMessage@223c1a70,
            common.administrator=com.serotonin.m2m2.i18n.TranslatableMessage@a467f3ea,
            common.enabledToggle=com.serotonin.m2m2.i18n.TranslatableMessage@ea5c2f12,
            common.alarmLevel.urgent=com.serotonin.m2m2.i18n.TranslatableMessage@8fa9c879,
            common.minimize=com.serotonin.m2m2.i18n.TranslatableMessage@5d740b21,
            js.email.noRecipients=com.serotonin.m2m2.i18n.TranslatableMessage@d78563d2,
            common.user=com.serotonin.m2m2.i18n.TranslatableMessage@8a9479ce,
            events.silence=com.serotonin.m2m2.i18n.TranslatableMessage@8376c0ac,
            js.email.testSent=com.serotonin.m2m2.i18n.TranslatableMessage@f59d9881,
            common.maximize=com.serotonin.m2m2.i18n.TranslatableMessage@c752a74f,
            events.unsilence=com.serotonin.m2m2.i18n.TranslatableMessage@29ad6533,
            common.alarmLevel.info=com.serotonin.m2m2.i18n.TranslatableMessage@2239cfe6} c
            onstants.SystemEventType.TYPE_SET_POINT_HANDLER_FAILURE=SET_POINT_HANDLER_FAIL URE
            MangoApiSystemSettingsDwr=com.infiniteautomation.mangoApi.web.MangoApiSyst emSettingsDwr@13801df
            constants.DataTypes.ALPHANUMERIC=4 org.apache.jasper.com
            piler.ELInterpreter=org.apache.jasper.compiler.ELInterpreterFactory$DefaultELI nterpreter@1980918
            constants.Permissions.DataPointAccessTypes.ADMIN=4 constants.Permissions.DataPointAccessTypes.SET=2
            DataSourceDwr=com.serotonin.m2m2.web.dwr.DataSourceDwr@1772c24
            constants.AuditEventType.TYPE_DATA_SOURCE=DATA_SOURCE
            constants.SystemEventType.TYPE_EMAIL_SEND_FAILURE=EMAIL_SEND_FAILURE
            constants.SystemEventType.TYPE_UPGRADE_CHECK=UPGRADE_CHECK
            constants.Permissions.DataPointAccessTypes.NONE=0 org.directwebremoting.impl.S
            erverContext=org.directwebremoting.impl.DefaultServerContext@27001d
            constants.EventType.EventTypeNames.PUBLISHER=PUBLISHER
            WatchListDwr=com.serotonin.m2m2.watchlist.WatchListDwr@1d0c37f org.eclipse.jet
            ty.containerInitializers=[ContainerInitializer{org.eclipse.jetty.apache.jsp.Je
            ttyJasperInitializer,interested=[],applicable=[],annotated=[]}]
            MangoNoSqlDwr=com.infiniteautomation.nosql.web.MangoNoSqlDwr@75ced4
            org.eclipse.jetty.server.Executor=qtp19415576{STARTED,8<=10<=200,i=1,q=0}
            constants.EventType.EventTypeNames.DATA_SOURCE=DATA_SOURCE
            constants.SystemEventType.TYPE_LICENSE_CHECK=LICENSE_CHECK
            EventInstanceDwr=com.serotonin.m2m2.web.dwr.EventInstanceDwr@adce32
            org.springframework.web.context.WebApplicationContext.ROOT=Root WebApplicationContext: startup date
            [Mon Feb 15 10:13:40 PST 2016]; root of context hierarchy
            org.springframework.web.context.support.ServletContextScope=
            org.springframework.web.context.support.ServletContextScope@d002d2
            constants.SystemEventType.TYPE_SYSTEM_SHUTDOWN=SYSTEM_SHUTDOWN
            SystemSettingsDwr=com.serotonin.m2m2.web.dwr.SystemSettingsDwr@13efacc
            DataPointDwr=com.serotonin.m2m2.web.dwr.DataPointDwr@1459b91
            constants.AuditEventType.TYPE_POINT_EVENT_DETECTOR=POINT_EVENT_DETECTOR
            mangoMessageKeys=[Ljava.lang.String;@88457e
            ReportsDwr=com.serotonin.m2m2.reports.web.ReportsDwr@1eb4368 org.directwebremo
            ting.WebContextFactory$WebContextBuilder=org.directwebremoting.impl.DefaultWeb
            ContextBuilder@1932443 org.apache.jasper.runtime.JspApplicationContextImpl=org
            .apache.jasper.runtime.JspApplicationContextImpl@39a9b3
            javax.servlet.context.tempdir=/opt/mango/work constants.DataTypes.MULTISTATE=2
            LoggingConsoleDwr=com.infiniteautomation.loggingconsole.web.LoggingConsoleDwr@ 1172513
            org.apache.tomcat.InstanceManager=org.apache.tomcat.SimpleInstanceMana ger@16d55a
            org.apache.catalina.jsp_classpath=/opt/mango/web/modules/mangoESCon
            figuration/classes:/opt/mango/web/modules/mangoESConfiguration/lib/m2m2-mangoE
            SConfiguration-1.1.0.jar:/opt/mango/web/modules/mangoESConfiguration/lib/jmdns
            -3.4.2-SNAPSHOT.jar:/opt/mango/web/modules/modbus/classes:/opt/mango/web/modul
            es/modbus/lib/httpclient-4.3.2.jar:/opt/mango/web/modules/modbus/lib/commons-
            logging-1.1.1.jar:/opt/mango/web/modules/modbus/lib/ant-launcher-1.8.1.jar:/op
            t/mango/web/modules/modbus/lib/aopalliance-1.0.jar:/opt/mango/web/modules/modb
            us/lib/modbus4j-2.1.1.jar:/opt/mango/web/modules/modbus/lib/joda-
            time-2.3.jar:/opt/mango/web/modules/modbus/lib/serotonin-
            utils-2.1.8.jar:/opt/mango/web/modules/modbus/lib/spring-
            beans-4.0.5.RELEASE.jar:/opt/mango/web/modules/modbus/lib/spring-
            expression-4.0.5.RELEASE.jar:/opt/mango/web/modules/modbus/lib/commons-lang3-3
            .0.jar:/opt/mango/web/modules/modbus/lib/freemarker-2.3.11.jar:/opt/mango/web/
            modules/modbus/lib/mail-1.5.0-b01.jar:/opt/mango/web/modules/modbus/lib /commons-
            pool-1.6.jar:/opt/mango/web/modules/modbus/lib/spring-context-support
            -4.0.5.RELEASE.jar:/opt/mango/web/modules/modbus/lib/m2m2-modbus-1.6.0.jar:/op
            t/mango/web/modules/modbus/lib/commons-io-2.1.jar:/opt/mango/web/modules/modbu
            s/lib/httpcore-4.3.2.jar:/opt/mango/web/modules/modbus/lib/log4j-1.2.17.jar:/o
            pt/mango/web/modules/modbus/lib/spring- jdbc-4.0.5.RELEASE.jar:/opt/mango/web/modules/modbus/lib
            /spring-webmvc-4.0.5.R
            ELEASE.jar:/opt/mango/web/modules/modbus/lib/jssc-2.8.0.jar:/opt/mango/web/mod
            ules/modbus/lib/activation-1.1.jar:/opt/mango/web/modules/modbus/lib/spring-
            web-4.0.5.RELEASE.jar:/opt/mango/web/modules/modbus/lib/serotonin-
            timer-2.0.7.jar:/opt/mango/web/modules/modbus/lib/spring-core-4.0.5.RELEASE.ja
            r:/opt/mango/web/modules/modbus/lib/ant-1.8.1.jar:/opt/mango/web/modules/modbu s/lib/spring-
            aop-4.0.5.RELEASE.jar:/opt/mango/web/modules/modbus/lib/commons-
            httpclient-3.1.jar:/opt/mango/web/modules/modbus/lib/spring-
            context-4.0.5.RELEASE.jar:/opt/mango/web/modules/modbus/lib/spring-
            tx-4.0.5.RELEASE.jar:/opt/mango/web/modules/modbus/lib/commons-
            codec-1.6.jar:/opt/mango/web/modules/modbus/lib/commons-dbcp-1.4.jar:/opt/mang
            o/web/modules/templateConfig/classes:/opt/mango/web/modules/templateConfig/lib
            /m2m2-templateConfig-1.0.7.jar:/opt/mango/web/modules/sstGraphics/classes:/opt
            /mango/web/modules/sstGraphics/lib/m2m2-sstGraphics-1.1.0.jar:/opt/mango/web/m
            odules/sstTheme/classes:/opt/mango/web/modules/sstTheme/lib/m2m2-sstTheme-1.1.
            0.jar:/opt/mango/web/modules/pachube/classes:/opt/mango/web/modules/pachube/li
            b/m2m2-pachube-1.5.0.jar:/opt/mango/web/modules/dashboards/classes:/opt/mango/
            web/modules/dashboards/lib/m2m2-dashboards-1.1.0.jar:/opt/mango/web/modules/pe
            rsistent/classes:/opt/mango/web/modules/persistent/lib/m2m2-persistent-1.6.0.j
            ar:/opt/mango/web/modules/scheduledEvents/classes:/opt/mango/web/modules/sched
            uledEvents/lib/m2m2-scheduledEvents-1.5.0.jar:/opt/mango/web/modules/mangoNoSq
            lDatabase/classes:/opt/mango/web/modules/mangoNoSqlDatabase/lib/mangoNoSQL-1.0
            .10.jar:/opt/mango/web/modules/mangoNoSqlDatabase/lib/m2m2-mangoNoSqlDatabase-
            1.2.0.jar:/opt/mango/web/modules/scripting/classes:/opt/mango/web/modules/scri
            pting/lib/m2m2-scripting-1.1.0.jar:/opt/mango/web/modules/opcda/classes:/opt/m
            ango/web/modules/opcda/lib/j-interopdeps-2.01.jar:/opt/mango/web/modules/opcda
            /lib/org.openscada.opc.dcom_0.7.0.201203290910.jar:/opt/mango/web/modules/opcd
            a/lib/j-interop-2.0.10.jar:/opt/mango/web/modules/opcda/lib/slf4j-log4j12-1.0.
            jar:/opt/mango/web/modules/opcda/lib/jcifs-1.2.19.jar:/opt/mango/web/modules/o
            pcda/lib/org.openscada.utils_0.17.0.201203290908.jar:/opt/mango/web/modules/op
            cda/lib/m2m2-opcda-1.6.0.jar:/opt/mango/web/modules/opcda/lib/org.openscada.op
            c.lib_0.9.0.201203290910.jar:/opt/mango/web/modules/mangoApi/classes:/opt/mang
            o/web/modules/mangoApi/lib/m2m2-mangoApi-1.1.0.jar:/opt/mango/web/modules/mang oApi/lib/apache-
            log4j-extras-1.2.17.jar:/opt/mango/web/modules/mangoApi/lib/lo
            g4j-1.2.17.jar:/opt/mango/web/modules/virtualDS/classes:/opt/mango/web/modules
            /virtualDS/lib/m2m2-virtualDS-1.5.0.jar:/opt/mango/web/modules/log4JReset/clas
            ses:/opt/mango/web/modules/log4JReset/lib/m2m2-log4JReset-1.1.0.jar:/opt/mango
            /web/modules/dglux/classes:/opt/mango/web/modules/dglux/lib/JoSQL-2.2.jar:/opt
            /mango/web/modules/dglux/lib/m2m2-dglux-1.3.0.jar:/opt/mango/web/modules/dglux /lib/gentlyWEB-
            utils-1.1.jar:/opt/mango/web/modules/dataFile/classes:/opt/mang o/web/modules/dataFile/lib/jaxb-
            api.jar:/opt/mango/web/modules/dataFile/lib/op
            encsv-2.3.jar:/opt/mango/web/modules/dataFile/lib/jaxb-
            core.jar:/opt/mango/web/modules/dataFile/lib/jaxb- jxc.jar:/opt/mango/web/modules/dataFile/lib/jaxb-
            xjc.jar:/opt/mango/web/modules/dataFile/lib/jaxb-impl.jar:/opt/mango/web/modul
            es/dataFile/lib/m2m2-dataFile-1.1.0.jar:/opt/mango/web/modules/jmxds/classes:/
            opt/mango/web/modules/jmxds/lib/m2m2-jmxds-1.5.0.jar:/opt/mango/web/modules/wa
            tchlists/classes:/opt/mango/web/modules/watchlists/lib/m2m2-watchlists-1.7.0.j
            ar:/opt/mango/web/modules/http/classes:/opt/mango/web/modules/http/lib/m2m2-ht
            tp-1.5.0.jar:/opt/mango/web/modules/maintenanceEvents/classes:/opt/mango/web/m
            odules/maintenanceEvents/lib/m2m2-maintenanceEvents-1.5.0.jar:/opt/mango/web/m
            odules/sstGlobalScripts/classes:/opt/mango/web/modules/sstGlobalScripts/lib/m2
            m2-sstGlobalScripts-1.5.0.jar:/opt/mango/web/modules/dataPointDetailsView/clas
            ses:/opt/mango/web/modules/dataPointDetailsView/lib/m2m2-dataPointDetailsView-
            1.0.0.jar:/opt/mango/web/modules/mbus/classes:/opt/mango/web/modules/mbus/lib /commons-
            logging-1.1.1.jar:/opt/mango/web/modules/mbus/lib/mbus4j-
            master-0.1.5.jar:/opt/mango/web/modules/mbus/lib/mbus4j-
            core-0.1.5.jar:/opt/mango/web/modules/mbus/lib/commons-
            beanutils-1.8.3.jar:/opt/mango/web/modules/mbus/lib/commons-lang-2.4.jar:/opt/
            mango/web/modules/mbus/lib/m2m2-mbus-1.1.0.jar:/opt/mango/web/modules/mbus/lib /json-
            lib-2.4-jdk15.jar:/opt/mango/web/modules/mbus/lib/ezmorph-1.0.6.jar:/opt
            /mango/web/modules/mbus/lib/commons- collections-3.2.1.jar:/opt/mango/web/modules/mbus/lib/spsw-
            java-0.0.4.jar:/opt /mango/web/modules/BACnet/classes:/opt/mango/web/modules/BACnet/lib/BACnet4J-3
            .1.1.jar:/opt/mango/web/modules/BACnet/lib/m2m2-BACnet-2.2.0.jar:/opt/mango/we
            b/modules/galil/classes:/opt/mango/web/modules/galil/lib/m2m2-galil-1.5.0.jar:
            /opt/mango/web/modules/TCPIP/classes:/opt/mango/web/modules/TCPIP/lib/m2m2-TCP
            IP-1.1.0.jar:/opt/mango/web/modules/dnp3/classes:/opt/mango/web/modules/dnp3/l
            ib/dnp34j.jar:/opt/mango/web/modules/dnp3/lib/m2m2-dnp3-1.6.0.jar:/opt/mango/w
            eb/modules/onewire/classes:/opt/mango/web/modules/onewire/lib/m2m2-onewire-1.5
            .0.jar:/opt/mango/web/modules/onewire/lib/RXTXcomm.jar:/opt/mango/web/modules/
            onewire/lib/OneWireAPI.jar:/opt/mango/web/modules/loggingConsole/classes:/opt/
            mango/web/modules/loggingConsole/lib/m2m2-loggingConsole-1.1.0.jar:/opt/mango/
            web/modules/internal/classes:/opt/mango/web/modules/internal/lib/m2m2-internal
            -1.5.0.jar:/opt/mango/web/modules/graphicalViews/classes:/opt/mango/web/module
            s/graphicalViews/lib/m2m2-graphicalViews-1.6.0.jar:/opt/mango/web/modules/repo
            rts/classes:/opt/mango/web/modules/reports/lib/m2m2-reports-2.2.0.jar:/opt/man
            go/web/modules/vmstat/classes:/opt/mango/web/modules/vmstat/lib/m2m2-vmstat-1.
            5.0.jar:/opt/mango/web/modules/pop3/classes:/opt/mango/web/modules/pop3/lib/m2
            m2-pop3-1.5.0.jar:/opt/mango/web/modules/serial/classes:/opt/mango/web/modules
            /serial/lib/m2m2-serial-1.2.0.jar:/opt/mango/web/modules/sqlConsole/classes:/o
            pt/mango/web/modules/sqlConsole/lib/m2m2-sqlConsole-1.5.0.jar:/opt/mango/web/m
            odules/twilio/classes:/opt/mango/web/modules/twilio/lib/twilio-java-sdk-3.4.1 -jar-with-
            dependencies.jar:/opt/mango/web/modules/twilio/lib/m2m2-twilio-1.1.0
            .jar:/opt/mango/web/modules/openv4j/classes:/opt/mango/web/modules/openv4j/lib
            /m2m2-openv4j-1.1.0.jar:/opt/mango/web/modules/openv4j/lib/openv4j-
            core-0.1.3.jar:/opt/mango/web/modules/openv4j/lib/mbus4j-master-0.1.3.jar:/opt
            /mango/web/modules/openv4j/lib/RXTXcomm.jar:/opt/mango/web/modules/openv4j/lib /mbus4j-
            core-0.1.3.jar:/opt/mango/web/modules/pointLinks/classes:/opt/mango/we
            b/modules/pointLinks/lib/m2m2-pointLinks-1.5.0.jar:/opt/mango/web/modules/jspV
            iews/classes:/opt/mango/web/modules/jspViews/lib/m2m2-jspViews-2.1.0.jar:/opt/
            mango/web/modules/egauge/classes:/opt/mango/web/modules/egauge/lib/m2m2-egauge
            -1.1.0.jar:/opt/mango/web/modules/asciiFile/classes:/opt/mango/web/modules/asc
            iiFile/lib/m2m2-asciiFile-1.2.0.jar:/opt/mango/web/modules/zwave/classes:/opt/
            mango/web/modules/zwave/lib/zwave4j-0.3.jar:/opt/mango/web/modules/zwave/lib/m
            2m2-zwave-1.1.0.jar:/opt/mango/web/modules/dataImport/classes:/opt/mango/web/m
            odules/dataImport/lib/opencsv-2.2.jar:/opt/mango/web/modules/dataImport/lib/m2
            m2-dataImport-1.4.0.jar:/opt/mango/web/modules/log4jDS/classes:/opt/mango/web/
            modules/log4jDS/lib/m2m2-log4jDS-1.1.0.jar:/opt/mango/web/modules/sqlds/classe
            s:/opt/mango/web/modules/sqlds/lib/opencsv-2.3.jar:/opt/mango/web/modules/sqld
            s/lib/m2m2-sqlds-1.6.0.jar:/opt/mango/web/modules/ssh/classes:/opt/mango/web/m
            odules/ssh/lib/m2m2-ssh-1.1.0.jar:/opt/mango/web/modules/ssh/lib/jsch-0.1.51.j
            ar:/opt/mango/web/modules/controlcore/classes:/opt/mango/web/modules/controlco
            re/lib/m2m2-controlcore-1.1.0.jar:/opt/mango/web/modules/snmp/classes:/opt/man
            go/web/modules/snmp/lib/SNMP4J.jar:/opt/mango/web/modules/snmp/lib/m2m2-snmp-1
            .5.0.jar:/opt/mango/web/modules/meta/classes:/opt/mango/web/modules/meta/lib/m
            vel2-2.1.3.Final.jar:/opt/mango/web/modules/meta/lib/m2m2-meta-2.2.0.jar
            constants.UserComment.TYPE_POINT=2 org.directwebremoting.Container=org.directw
            ebremoting.impl.DefaultContainer@8eb833 messageKeys=[Ljava.lang.String;@54527
            constants.DataTypes.IMAGE=5 org.apache.jasper.compiler.TldCache=org.apache.jas
            per.compiler.TldCache@1b409e5 org.springframework.web.servlet.FrameworkServlet
            .CONTEXT.springDispatcher=WebApplicationContext for namespace 'springDispatcher-servlet': startup
            date [Mon Feb 15 10:13:45 PST 2016]; parent: Root WebApplicationContext
            constants.Permissions.DataPointAccessTypes.DATA_SOURCE=3
            constants.EventType.EventTypeNames.SYSTEM=SYSTEM
            constants.SystemEventType.TYPE_PROCESS_FAILURE=PROCESS_FAILURE
            constants.AuditEventType.TYPE_DATA_POINT=DATA_POINT
            constants.SystemEventType.TYPE_MAX_ALARM_LEVEL_CHANGED=MAX_ALARM_LEVEL_CHANGED
            constants.DataTypes.NUMERIC=3 constants.Common.NEW_ID=-1
            MiscDwr=com.serotonin.m2m2.web.dwr.MiscDwr@12b9abd
            constants.AuditEventType.TYPE_EVENT_HANDLER=EVENT_HANDLER
            Any ideas appreciated
              JoelHaggar
              I don't remember if we had those setting in 2.6 but there is a good chance the setting has issues which is one of the reasons we went to 2.7. I would recommend upgrading to 2.7.
              We have a new release coming out end of the week or next week with some bug fixes that may also greatly increase your performance. What is the polling rate of the data sources?
              Thanks,
              C 1 Reply Last reply Reply Quote 0
              • C Offline
                craig @JoelHaggar
                Hi Joel,
                The polling rate is 3s. I'll keep an eye out for the update
                Craig
                Hello! It looks like you're interested in this conversation, but you don't have an account yet.
                Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.