    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website
    D
    • Profile
    • Following 0
    • Followers 0
    • Topics 3
    • Posts 10
    • Best 0
    • Controversial 0
    • Groups 0

    Topics created by dkudos

    • D

      Error with Bacnet Function is not unicast, broadcast, or forward (0xa, 0xb, or 0x4)

      User help
      • • • dkudos
      2
      0
      Votes
      2
      Posts
      1.9k
      Views

      D

      This is the Error I am receiving. 'Mitsubishi City Line': Function is not unicast, broadcast, or forward (0xa, 0xb, or 0x4). 'Mitsubishi City Line': is the Bacnet datapoint. I never had this error before just wondering what this means? Any idea let me know. I am running mango 1.13.0.

      Dominic

    • D

      Building/HVAC Automation

      Stories
      • • • dkudos
      2
      0
      Votes
      2
      Posts
      4.9k
      Views

      D

      Hey All,

      I needed a solution for large 2 pipe steam boiler system zoned by room. It is controlled by a Wago 750-841 modbus ip unit. Firing RIB relays to turn on the boiler and put the T-Stats into day or night mode. My Scheduling is done with google calendars. I wrote a java app the connect via google's API. Need to integrate with mango let me know if it is possible. Also control a Mitsubishi City Line system via BACnet at the same time. Awesome! Would have not been possible without this app. I will post pics and other cool stuff once I am done.

      Dominic

    • D

      Wago 750-841 Modbus Fieldbus Coupler

      Hardware
      • • • dkudos
      8
      0
      Votes
      8
      Posts
      7.5k
      Views

      D

      @zumiani said:

      You should look at the PLC program.
      Maybe a task turn it off after a while..
      Surely it isn't due to Mango or Modbus!

      Ok finally found the issue! I had created a binary 0 reset on the program I had wrote and was talking to mango at the same time. So everytime I had set a point in mango my program was reseting that point after 2 seconds.

      So now that I finally have it all working I am running a BAC-HD150 bacnet controller for the Mitsubishi City Line system with Bacnet IP of course. And running custom valve and boiler control for large steam system. I am controlling that with Wago 750-841 Modbus Field Coupler. I will update you with my setup once all is done.

      Thanks and hope this helps others.

      dk