Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
Illegal Data Address
-
Hi all,
My Mango is connected to the Main Switch via Modbus TCP.
I'm trying to read 2 registers (Circuit Breaker Open & Close) from main switch but it's showing illegal data address.
I tried to read these 2 registers with the Modbus Poll software. It's showing the same issue (illegal data address) in the Modbus Poll.
But in the software, I can set the read quantity to 2 and it fixed the issue. I can now read the 2 registers properly in Modbus Poll.
How do I configure in Mango to read only 2 registers? Or how to fix this illegal address issue?
Thanks,
Ryan -
@ryanlo assuming you're using tcp/ip, check that you can actually ping the unit from your mango box.
Second, confirm of the unit has a zero or one offset for the registers.
Mango is zero by default, you may need to increment your register addresses by one.Fox
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.