Setting point values in Graphic View
-
I have settable points (either from MODBUS IP source or Virtual source) which are settable through the Watch List or the Point Details but are not settable through a Graphic view. If I hover over the graphic point I do not get the wrench icon, only the info icon. It does this whether I'm in edit mode or viewing mode. I am logged in as administrator and created the Graphic view myself so I should have permission to set the point. I've tried with and without the Settable Override check box marked. I assume it should be unmarked to work the way I want it to. Is there another setting somewhere I need to enable to make settable points settable within graphic views?
-
No, there are no other settings. The "Settable override" box should be checked, as well as "Display controls". Otherwise, the point only needs to be settable itself. If you are still having problems, can you provide an export of the view?