Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
Temperature/Humidity device configuration
-
Hello!
I need help with configuration of DataPoint:The device I'm using has 2 registers:
- Temperature
- Humidity
I finnally found a configuration to retrieve humidity values:
--> Modbus Serial --> New Data Point:
Register Range: Holding Register
Modbus Data Type: 8 Byte Unsigned Integer
Offset: 0
Bit: (disabled)
Settable: Uncheked
Multiplier: 0.1
Additive: 0But I can't found a configuration to retrieve temperature. I tried too many combinations without success.
Well, how do I configure the datapoint to retrieve different Holding Registers values?
The device manual you can found here:
http://www.laudolab.com.br/tmp/n322.pdf
Thank you!
Marcelo Amorim Ferreira
-
Hi Marcelo,
On the point setting there is a value called: Offset (0-based) this is where you put in the holding register for the value you want to read.
I don't read Portuguese so I'm not sure of the registers you want to read but it looks like it is all on the list. I would also check to make sure it really is a 8 byte register. In the temperature and humidity devices I use it's always just 2 bytes.
Hope this helps,
Joel. -
Joel,
you're right!2 bytes works for me. Offset was'nt working because I was selecting 4 or 8 bytes.
Now I got things working here.Thank you and best regards!