    Temperature/Humidity device configuration
    4 Posts 2 Posters 3.4k Views 1 Watching
      marceloudi
      Hello!
      I need help with configuration of DataPoint:
      The device I'm using has 2 registers:
      • Temperature
      • Humidity
      I finnally found a configuration to retrieve humidity values:
      --> Modbus Serial --> New Data Point:
      Register Range: Holding Register
      Modbus Data Type: 8 Byte Unsigned Integer
      Offset: 0
      Bit: (disabled)
      Settable: Uncheked
      Multiplier: 0.1
      Additive: 0
      But I can't found a configuration to retrieve temperature. I tried too many combinations without success.
      Well, how do I configure the datapoint to retrieve different Holding Registers values?
      The device manual you can found here:
      http://www.laudolab.com.br/tmp/n322.pdf
      Thank you!
      Marcelo Amorim Ferreira
        Hi Marcelo,
        On the point setting there is a value called: Offset (0-based) this is where you put in the holding register for the value you want to read.
        I don't read Portuguese so I'm not sure of the registers you want to read but it looks like it is all on the list. I would also check to make sure it really is a 8 byte register. In the temperature and humidity devices I use it's always just 2 bytes.
        Hope this helps,
        Joel.
          marceloudi
          Joel,
          you're right!
          2 bytes works for me. Offset was'nt working because I was selecting 4 or 8 bytes.
          Now I got things working here.
          Thank you and best regards!
          [<O>] Brazil