Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
Question on Modbus Comms
-
Hello,
We have a client that will be using quite a few modbus devices. One thing he asked about, which I wasn't sure of an answer, is how does Mango handle modbus CRC and any partial data transmissions / failures?
- Is this something that one of the Exception alarms would capture?
- If we're using a slave monitor point, what value would that data point have? I'm guessing 0 since it's not a successful transmission, but not sure.
Any information is appreciated.
Thanks,
Chad -
Hi @cmusselm
These would generate a data source exception event if a poll for a specific Modbus slave fails for any reason the monitor will be set to 0.
-
Thanks for the confirmation, I appreciate it.
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.
With your input, this post could be even better 💗
Register Login