Trouble Connecting To Modbus IP
-
Hello,
I am using Mango v 2.8.8
I am trying to use the Modbus IP Module on Mango. With another a modbus scanning tool, I can confirm I have the correct IP, Port #, Slave ID and Register #.
However on Mango, when I try to scan for nodes I am getting no results, it seems to be stuck scanning. I also get the error Illegal data address when trying to read the modbus directly.
-
Try starting at 1280 and try reading less than 100 registers. Illegal data address is an error returned from the Modbus Slave saying you are trying to read a register that you are not allowed to read.
-
Hey Joel! Yup, that was it. I was trying to read the wrong register. Thank you!