    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    Modbus data source setup

    User help
    4
    14
    6.5k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • Woody BeverleyW
      Woody Beverley @patd2020
      last edited by

      @patd2020 said in Modbus data source setup:

      (however when I test in a Modbus test programme I am having no issue and am able to send commands and receive responses with no delay etc)

      Hello Pat,

      The program you referenced, is this software that shipped with the device?
      When you run this program, are you using the same computer and Comm ports on which you are running Mango?
      If yes, then we know the comm ports and wiring are working.

      I find that scan node often doesn't work with devices. The better tool for troubleshooting in Mango I think is the Modbus read data tool.
      0_1466436927196_upload-1e3d4623-2a26-43b5-b521-915a24e4e967

      Double check all your comm port settings, Baud rate, etc then verify you Register range. It seems like a lot of newer devices typically use Holding register. I would set the Number of registers from 100 to 1 or 2. Be sure to disable the data source while you are using the Read Data Tool.

      Hope this helps!

      -WoodyB

      1 Reply Last reply Reply Quote 0
      • P
        patd2020
        last edited by

        Hi Woody, thank you for taking the time to reply. the modbus test software is generic not supplied with the device. i checked the comm port settings and they match. So I wonder if my serial to ethernet converters servers for some reason are not playing nice with Mango. Because they work with the test software.
        Basically each modbus device is connector to a serial to ethernet converter see drawing (thetop part is description bottom part just icons of the same) and a virtual comm port is created for each device.

        They also support IP so I tried MODBUS IP and get the same no response error. but if I change the ip port from the real one to a random ip port I get a timeout error. Which makes me think the connection settings are right and the request to the slave is getting through but just not getting a response from the devi0_1466476518946_ConnectionDrawingt.pdf ce.

        Any thoughts?

        1 Reply Last reply Reply Quote 0
        • JoelHaggarJ
          JoelHaggar
          last edited by

          Try checking the Override timing box and leaving the settings as 0. This leaves the timing up to the adapter and can work much better. We are changing the way this works in the next release.

          1 Reply Last reply Reply Quote 0
          • JoelHaggarJ
            JoelHaggar
            last edited by

            You probably need a longer timeout setting if this is going over the internet. I would try up to 5000 ms.

            1 Reply Last reply Reply Quote 0
            • P
              patd2020
              last edited by

              Thanks for your suggestion Joel but still getting the no response error

              1 Reply Last reply Reply Quote 0
              • JoelHaggarJ
                JoelHaggar
                last edited by

                I think you'll need to run a Modbus packet capture software on the end of the virtual com port to verify what communication is or isn't coming out.

                The error you are seeing in Mango just means Mango sent out a message and didn't get any response back from the device.

                1 Reply Last reply Reply Quote 0
                • P
                  patd2020
                  last edited by

                  any recommendations
                  for this type of software?

                  1 Reply Last reply Reply Quote 0
                  • JoelHaggarJ
                    JoelHaggar
                    last edited by

                    Here is a good free one: http://www.isquared.ca/English/downloads_CC.htm RS-485 spy

                    1 Reply Last reply Reply Quote 0
                    • phildunlapP
                      phildunlap
                      last edited by phildunlap

                      Hi Patd,

                      Some other thoughts as I'm also reading...

                      Is it possible the slave IDs are flipped / mistaken? I see COM1 trying to talk to slave 2, and COM2 trying to talk to slave 1. Sometimes operating systems can switch their identifier on you at a reboot and such.

                      You can try to make equivalent requests from your test software and Mango through Modbus IP to netcat, then compare (or if you're feeling serial you can cat -v /dev/ttyUSBN)...

                      [sudo] nc -l 900 > testSoftware
                      *run query from test software pointed to this machines ip, port 900*
                      [sudo] nc -l 900 > testMango
                      *run query from Mango*
                      hexdump -C testSoftware
                      hexdump -C testMango
                      

                      But alas you are probably using Windows with names like "COM1" :P You can do it if you have a Linux system on hand.

                      1 Reply Last reply Reply Quote 0
                      • P
                        patd2020
                        last edited by

                        Thanks Joel & Phil. yes I see your point about the non matching slave/com port. I should have matched it to avoid confusion but that is actually how they are setup/ Slave 1 on Com2 and slave2 on COM1. Yes I am on Windows. I will attempt to run your suggested tests and report back

                        1 Reply Last reply Reply Quote 0
                        • P
                          patd2020
                          last edited by

                          here is the RS485 Modbus guide for the Flow m0_1466480777062_FlowRS485.doc

                          1 Reply Last reply Reply Quote 0
                          • P
                            patd2020
                            last edited by

                            Here is an update. I now can read the registers of both devices. the second device which had Modbsus ASCII as default I had to change to RTU. Now I need to figure out how to set up the data points

                            1 Reply Last reply Reply Quote 0
                            • P
                              patd2020
                              last edited by

                              Sorry I meant to say I change the data source to MODBUS IP because I could not get the COM to to work

                              1 Reply Last reply Reply Quote 0