Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
Modbus Reg Write
-
Hi Modbus experts. I have a energy meter and would like to set a certain register. Mango allows me to write to the register from the write tool see here write ok

When i add the point and try to set it i get this error in the logging console error.txt
Any Ideas?? -
There are a couple setting that might help. Are you able to read this register as well? If not you might need to set the data point to be a write only rather than read and write.
The other thing is on the data source setting try setting the Max Write Register count to 1. With modbus you can do a single write command or multiple write command. Mango will try and be as efficient as possible and some devices don't support the full modbus specification.
Let me know if either of these help.
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.