• Recent
    • Tags
    • Popular
    • Register
    • Login

    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    Errors of BACnet Data Source

    User help
    3
    5
    2.1k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • mebiusM
      mebius
      last edited by

      we are running a MA 2.4 with around 4500 data points and more than 50 data source.

      These recent days we found a problem of the BACnet data source which has near 400 data points.

      when active data points are less than 200, the data source is updating smoothly. But when more than 200 active data points, it updates slowly and goes to stop when active points turn more.

      It seems that socket connection can't be created, but the DDC device can be pinged successfully from the Mango machine.

      I attached screenshots of errors and configuration of the data source for your suggestion. thanks.

      Attachment: download link

      1 Reply Last reply Reply Quote 0
      • JoelHaggarJ
        JoelHaggar
        last edited by

        Hi Mebius,

        I think we will also want to have a look at your logs and then can get back to you shortly.

        Joel.

        1 Reply Last reply Reply Quote 0
        • mebiusM
          mebius
          last edited by

          Hi Joel, since the log including some customized information. I will mail it to you rather than posting here.

          Thanks.

          1 Reply Last reply Reply Quote 0
          • M
            mlohbihler
            last edited by

            Mebius,

            Do you have a single data source that is getting points from the BACnet device, or do you have multiple? If the latter, you might have multiple simultaneous requests going to the device, which it may not be able to handle, causing timeouts and the appearance of a slowdown.

            I know at least that even the BACnet MS/TP is capable of polling for thousands of points without problems, subject to the speed of the connection. (I know you are using I/P, which should be much faster than MS/TP.)

            Best regards,
            Matthew

            1 Reply Last reply Reply Quote 0
            • First post
              Last post