    Invalid slave id
    11 Posts 6 Posters 12.4k Views 4 Watching
    • H Offline
      HenryDUT
      Hi, I want to specify the value of slave id , but when I execute the following code, I get an exception "com.serotonin.modbus4j.exception.ModbusTransportException: Invalid slave id".
      If slave id is less than 248?it will be OK.
      Is there a problem with the code? or slave id can not be greater than 247 ?
      int slave_id=255;
      ModbusRequest req = new ReadInputRegistersRequest(slave_id, 0, 5);
      ReadInputRegistersResponse rep = (ReadInputRegistersResponse) mp.send(req);
      • F Offline
        fmunhoz
        As I recall Modbus only has an 8-bit address, so one master can only talk to 255 slaves via 1 port, so valid addresses are in the range 0..247 where 0 is used as a broadcast address.
        However you can use another port, though.
        If have any doubts about it I recommend you google for modbus documentation.
          Actually, max slave id is 240.
          • H Offline
            HenryDUT
            Thanks for fmunhoz's recommendation.
            In MODBUS Messaging on TCP/IP Implementation Guide, it says that
            On TCP/IP, the MODBUS server is addressed using its IP address; therefore, the MODBUS Unit Identifier is useless. The value 0xFF has to be used.
            When addressing a MODBUS server connected directly to a TCP/IP network, it’s recommended not using a significant MODBUS slave address in the “Unit Identifier” field. 0xFF is recommended for the “Unit Identifier" as non-significant value.
            But 0xFF is greater than 247 (decimal), how can I assign 0xFF to the slave device address?
            • H Offline
              HenryDUT
              really?
              Is it not assigned from 1 to 247 (decimal) ?
              • H Offline
                HenryDUT
                Who can help me?
                  Is the slave id actually causing problems for you?
                  • V Offline
                    villadaniel_750
                    Amazing. Here i have PLC General Electric F650, with slave Modbus TCP and the slave id is 254 (HEX FE). Great job Modbus4J assuming a slave id between 0 to 247. JAR to TRASH
                      I will refer you to the protocol specification.
                      http://modbus.org/docs/PI_MBUS_300.pdf
                      Page 19 (#10) is probably the page you'd be interested in, first paragraph. Some people suggest there are extra functions mapped onto units addressed 248-255, but I can't find a spec for that.
                      http://www.modbus.org/docs/Modbus_over_serial_line_V1.pdf
                      page 8
                      http://www.modbus.org/docs/Modbus_Messaging_Implementation_Guide_V1_0b.pdf
                      page 23
                        craig
                        villadaniel_, since it is a PLC why don't you change its slave id to something in the range that will work?