Invalid slave id
 Hi, I want to specify the value of slave id , but when I execute the following code, I get an exception "com.serotonin.modbus4j.exception.ModbusTransportException: Invalid slave id". If slave id is less than 248?it will be OK. Is there a problem with the code? or slave id can not be greater than 247 ? int slave_id=255;
 ModbusRequest req = new ReadInputRegistersRequest(slave_id, 0, 5);
 ReadInputRegistersResponse rep = (ReadInputRegistersResponse) mp.send(req);Thanks
 As I recall Modbus only has an 8-bit address, so one master can only talk to 255 slaves via 1 port, so valid addresses are in the range 0..247 where 0 is used as a broadcast address. However you can use another port, though. If have any doubts about it I recommend you google for modbus documentation.
 Actually, max slave id is 240.
 Thanks for fmunhoz's recommendation. In MODBUS Messaging on TCP/IP Implementation Guide, it says that On TCP/IP, the MODBUS server is addressed using its IP address; therefore, the MODBUS Unit Identifier is useless. The value 0xFF has to be used. When addressing a MODBUS server connected directly to a TCP/IP network, it’s recommended not using a significant MODBUS slave address in the “Unit Identifier” field. 0xFF is recommended for the “Unit Identifier" as non-significant value. But 0xFF is greater than 247 (decimal), how can I assign 0xFF to the slave device address?
 @mlohbihler said: Actually, max slave id is 240. really? Is it not assigned from 1 to 247 (decimal) ?
 @HenryDUT said: Thanks for fmunhoz's recommendation. In MODBUS Messaging on TCP/IP Implementation Guide, it says that On TCP/IP, the MODBUS server is addressed using its IP address; therefore, the MODBUS Unit Identifier is useless. The value 0xFF has to be used. When addressing a MODBUS server connected directly to a TCP/IP network, it’s recommended not using a significant MODBUS slave address in the “Unit Identifier” field. 0xFF is recommended for the “Unit Identifier" as non-significant value. But 0xFF is greater than 247 (decimal), how can I assign 0xFF to the slave device address? Who can help me?
 Is the slave id actually causing problems for you?
 Amazing. Here i have PLC General Electric F650, with slave Modbus TCP and the slave id is 254 (HEX FE). Great job Modbus4J assuming a slave id between 0 to 247. JAR to TRASH
 I will refer you to the protocol specification.
 http://modbus.org/docs/PI_MBUS_300.pdfPage 19 (#10) is probably the page you'd be interested in, first paragraph. Some people suggest there are extra functions mapped onto units addressed 248-255, but I can't find a spec for that. http://www.modbus.org/docs/Modbus_over_serial_line_V1.pdf
 page 8http://www.modbus.org/docs/Modbus_Messaging_Implementation_Guide_V1_0b.pdf
 page 23
 villadaniel_, since it is a PLC why don't you change its slave id to something in the range that will work?