    Simple Examples
    28 Posts 4 Posters 50.1k Views 1 Watching
      This is excellent Arne. Thanks very much for sharing your work.
        apl
        trying to read all property values by using this changed code in :
            private void addPropertyReferences(PropertyReferences refs, ObjectIdentifier oid) {
                for (int i = 0; i < 12; i++) {
                    refs.add(oid, new PropertyIdentifier(75 + i));
        and choose values greater of 12 >> the app will fail.
        Any hints?
        Arne
          apl
          Hi Matthew,
          the offending PropertyId are: 8, 87, 105, which throw a java.lang.reflect.InvocationTargetException.
          Should I file a bug against it in the SF bug parade?
          Arne
            Hi Arne,
            I can't reproduce the problem. This code worked fine for me:
                public static void main(String[] args) throws Exception {
                    ObjectIdentifier oid = new ObjectIdentifier(ObjectType.accumulator, 0);
                    PropertyReferences refs = new PropertyReferences();
                    for (int i=0; i&lt200; i++)
                        refs.add(oid, new PropertyIdentifier(i));
            A stack trace goes a long way to explaining things. Maybe you can include that if you still have this problem.
            Also, can you please start a new topic when you are changing subject. This thread is getting too expansive.
              apl
              Sorry,
              I thought this belongs also to create a bunch of example that runs out of the box.
              OK, here is my stack trace:
              com.serotonin.bacnet4j.exception.BACnetException: java.lang.reflect.InvocationTargetException
                      at com.serotonin.bacnet4j.type.Encodable.read(Encodable.java:168)
                      at com.serotonin.bacnet4j.type.constructed.SequenceOf.<init>(SequenceOf.java:54)
                      at com.serotonin.bacnet4j.type.Encodable.readSequenceOf(Encodable.java:213)
                      at com.serotonin.bacnet4j.service.acknowledgement.ReadPropertyMultipleAck.<init>(ReadPropertyMultipleAck.java:50)
                      at com.serotonin.bacnet4j.service.acknowledgement.AcknowledgementService.createAcknowledgementService(AcknowledgementService.java:48)
                      at com.serotonin.bacnet4j.apdu.ComplexACK.parseServiceData(ComplexACK.java:196)
                      at com.serotonin.bacnet4j.npdu.ip.IpMessageControl.waitForAck(IpMessageControl.java:658)
                      at com.serotonin.bacnet4j.npdu.ip.IpMessageControl.send(IpMessageControl.java:288)
                      at com.serotonin.bacnet4j.npdu.ip.IpMessageControl.send(IpMessageControl.java:268)
                      at com.serotonin.bacnet4j.npdu.ip.IpMessageControl.send(IpMessageControl.java:224)
                      at com.serotonin.bacnet4j.LocalDevice.send(LocalDevice.java:411)
                      at com.serotonin.bacnet4j.LocalDevice.send(LocalDevice.java:399)
                      at com.serotonin.bacnet4j.LocalDevice.send(LocalDevice.java:392)
                      at com.serotonin.bacnet4j.LocalDevice.readProperties(LocalDevice.java:760)
                      at com.serotonin.bacnet4j.test.DiscoveryTest.doDiscover(DiscoveryTest.java:155)
                      at com.serotonin.bacnet4j.test.DiscoveryTest.main(DiscoveryTest.java:187)
              Caused by: java.lang.reflect.InvocationTargetException
                      at sun.reflect.NativeConstructorAccessorImpl.newInstance(NativeConstructorAccessorImpl.java:57)
                      at sun.reflect.DelegatingConstructorAccessorImpl.newInstance(DelegatingConstructorAccessorImpl.java:45)
                      at java.lang.reflect.Constructor.newInstance(Constructor.java:532)
                      at com.serotonin.bacnet4j.type.Encodable.read(Encodable.java:165)
                      ... 15 more
              Caused by: com.serotonin.bacnet4j.exception.BACnetException: java.lang.reflect.InvocationTargetException
                      at com.serotonin.bacnet4j.type.constructed.SequenceOf.<init>(SequenceOf.java:66)
                      at com.serotonin.bacnet4j.type.Encodable.readSequenceOf(Encodable.java:224)
                      at com.serotonin.bacnet4j.type.Encodable.readOptionalSequenceOf(Encodable.java:233)
                      at com.serotonin.bacnet4j.type.constructed.ReadAccessResult.<init>(ReadAccessResult.java:64)
                      ... 20 more
                      at sun.reflect.GeneratedConstructorAccessor3.newInstance(Unknown Source)
                      ... 24 more
                      at com.serotonin.bacnet4j.type.Encodable.readWrapped(Encodable.java:318)
                      at com.serotonin.bacnet4j.type.Encodable.readEncodable(Encodable.java:263)
                      at com.serotonin.bacnet4j.type.constructed.ReadAccessResult$Result.<init>(ReadAccessResult.java:124)
                      ... 28 more
                      ... 31 more
                      at com.serotonin.bacnet4j.type.constructed.PriorityArray.<init>(PriorityArray.java:41)
                      ... 36 more
                      ... 38 more
              Caused by: com.serotonin.bacnet4j.exception.BACnetErrorException
                      at com.serotonin.bacnet4j.type.Encodable.popStart(Encodable.java:109)
                      at com.serotonin.bacnet4j.type.AmbiguousValue.<init>(AmbiguousValue.java:11)
                      at com.serotonin.bacnet4j.type.constructed.PriorityValue.<init>(PriorityValue.java:83)
                      ... 43 more
              Any Idea?
              Arne
                apl
                Hi Matthew,
                this happends by ObjectType == multiStateOutput and analogOutput
                Arne
                  If the goal is to provide a set of simple examples, i would think the reporting of possible errors would just clutter things up.
                  But in any case, i still cannot reproduce this error. It appears to be an incorrectly formatted response. I expanded my test code to the following. It won't work for you because i added some convenience methods in the PropertyValues object, but i think you'll see what i'm getting at.
                          LocalDevice localDevice = new LocalDevice(1234, &quot;192.168.0.255&quot;);
                          localDevice.initialize();
                          localDevice.sendBroadcast(2068, new WhoIsRequest(null, null));
                          Thread.sleep(1000);
                          RemoteDevice d = localDevice.getRemoteDevices().get(0);
                          ObjectIdentifier oid = new ObjectIdentifier(ObjectType.analogInput, 0);
                          PropertyValues pvs = localDevice.readProperties(d, refs);
                          for (ObjectPropertyReference opr : pvs)
                              System.out.println(pvs.getNoErrorCheck(opr));
                          Thread.sleep(2000);
                          localDevice.terminate();
                  The listener that returned the response is the SlaveDeviceTest example.
                    Hi Arne,
                    I have a fix for the PriorityArray (87). The class was not decoding properly. I have checked the updates into the CVS repo, but did not release a new version of the library. Here are the changes:
                    In PriorityArray, added an int to the constructor:
                        public PriorityArray(ByteQueue queue, int contextId) throws BACnetException {
                            super(queue, PriorityValue.class, contextId);
                    In Encodable, added this method:
                        protected static &lt;T extends Encodable&gt; T readSequenceType(ByteQueue queue, Class&lt;T&gt; clazz, int contextId)
                            popStart(queue, contextId);
                            T result;
                            try {
                                result = clazz.getConstructor(new Class[] {ByteQueue.class, Integer.TYPE}).newInstance(
                                        new Object[] {queue, contextId});
                            catch (Exception e) {
                                throw new BACnetException(e);
                            popEnd(queue, contextId);
                            return result;
                    ... and added a call to that method in this method as shown:
                        protected static Encodable readEncodable(ByteQueue queue, ObjectType objectType,
                                PropertyIdentifier propertyIdentifier, UnsignedInteger propertyArrayIndex, int contextId)
                            // A property array index of 0 indicates a request for the length of an array.
                            if (propertyArrayIndex != null && propertyArrayIndex.intValue() == 0)
                                return readWrapped(queue, UnsignedInteger.class, contextId);
                            if (!matchNonEndTag(queue, contextId))
                                throw new BACnetErrorException(ErrorClass.property, ErrorCode.missingRequiredParameter);
                            PropertyTypeDefinition def = ObjectProperties.getPropertyTypeDefinition(objectType, propertyIdentifier);
                            if (def == null)
                                return new AmbiguousValue(queue, contextId);
                            if (propertyArrayIndex != null && !def.isSequence())
                                throw new BACnetErrorException(ErrorClass.property, ErrorCode.propertyIsNotAList);
                            if (propertyArrayIndex == null && def.isSequence())
                                return readSequenceOf(queue, def.getClazz(), contextId);
                            if (propertyArrayIndex == null && SequenceOf.class.isAssignableFrom(def.getClazz()))
                                return readSequenceType(queue, def.getClazz(), contextId);
                            return readWrapped(queue, def.getClazz(), contextId);
                    Can you let me know if this has any effect on the other types you mentioned (8 and 105).
                      apl
                      Thank you, iI got it from CVS.
                      so here is my next "streamlined" ex DiscoveryTest example
                      It sends a WhoIs Request, waits for the first device to answer (in doDiscover()).
                      And then it requests all available Properties with PropertyIdentifier.all.
                      Then it prints the properties sorted by ObjectId.
                       * GNU Lesser General Public License
                       * Copyright (C) 2006-2009 Serotonin Software Technologies Inc. http://serotoninsoftware.com
                       * @author Matthew Lohbihler
                       * This library is free software; you can redistribute it and/or
                       * modify it under the terms of the GNU Lesser General Public
                       * License as published by the Free Software Foundation; either
                       * version 2.1 of the License, or (at your option) any later version.
                       * This library is distributed in the hope that it will be useful,
                       * but WITHOUT ANY WARRANTY; without even the implied warranty of
                       * MERCHANTABILITY or FITNESS FOR A PARTICULAR PURPOSE.  See the GNU
                       * Lesser General Public License for more details.
                       * You should have received a copy of the GNU Lesser General Public
                       * License along with this library; if not, write to the Free Software
                       * Foundation, Inc., 59 Temple Place, Suite 330, Boston, MA  02111-1307, USA.
                      package com.serotonin.bacnet4j.test;
                      import com.serotonin.bacnet4j.RemoteObject;
                      import com.serotonin.bacnet4j.exception.BACnetException;
                      import com.serotonin.bacnet4j.obj.BACnetObject;
                      import com.serotonin.bacnet4j.type.Encodable;
                      import com.serotonin.bacnet4j.type.constructed.Choice;
                      import com.serotonin.bacnet4j.type.constructed.PropertyValue;
                      import com.serotonin.bacnet4j.type.constructed.TimeStamp;
                      import com.serotonin.bacnet4j.type.enumerated.EventState;
                      import com.serotonin.bacnet4j.type.enumerated.EventType;
                      import com.serotonin.bacnet4j.type.enumerated.MessagePriority;
                      import com.serotonin.bacnet4j.type.enumerated.NotifyType;
                      import com.serotonin.bacnet4j.type.notificationParameters.NotificationParameters;
                      import com.serotonin.bacnet4j.type.primitive.Boolean;
                      import com.serotonin.bacnet4j.type.primitive.CharacterString;
                      import java.io.IOException;
                      import java.util.List;
                      import com.serotonin.bacnet4j.LocalDevice;
                      import com.serotonin.bacnet4j.RemoteDevice;
                      import com.serotonin.bacnet4j.event.DeviceEventListener;
                      import com.serotonin.bacnet4j.service.unconfirmed.WhoIsRequest;
                      import com.serotonin.bacnet4j.type.constructed.ObjectPropertyReference;
                      import com.serotonin.bacnet4j.type.constructed.SequenceOf;
                      import com.serotonin.bacnet4j.type.enumerated.PropertyIdentifier;
                      import com.serotonin.bacnet4j.type.primitive.ObjectIdentifier;
                      import com.serotonin.bacnet4j.type.primitive.UnsignedInteger;
                      import com.serotonin.bacnet4j.util.PropertyReferences;
                      import com.serotonin.bacnet4j.util.PropertyValues;
                      import java.util.ArrayList;
                       * Discovers and devices and print all properties of all objects found.
                       * this is done by using PropertyIdentifier.all so the Device will send all propertys that are set.
                       * if you want poll all PropertyId {@link ReadPropertyRangeTest}.
                       * @author Arne Plöse
                      public class ReadAllAvailabeProperties {
                          public static String BROADCAST_ADDRESS = "127.0.0.255";
                          private LoopDevice loopDevice;
                          private LocalDevice localDevice;
                          // remote devices found
                          private List<RemoteDevice> remoteDevices = new ArrayList<RemoteDevice>();
                          public ReadAllAvailabeProperties(String broadcastAddress, int port) throws IOException {
                              localDevice = new LocalDevice(1234, broadcastAddress);
                              localDevice.setPort(port);
                              localDevice.getEventHandler().addListener(new DeviceEventListener() {
                                  public void listenerException(Throwable e) {
                                      System.out.println("DiscoveryTest listenerException");
                                  public void iAmReceived(RemoteDevice d) {
                                      System.out.println("DiscoveryTest iAmReceived");
                                      remoteDevices.add(d);
                                      synchronized (ReadAllAvailabeProperties.this) {
                                          ReadAllAvailabeProperties.this.notifyAll();
                                  public boolean allowPropertyWrite(BACnetObject obj, PropertyValue pv) {
                                      System.out.println("DiscoveryTest allowPropertyWrite");
                                      return true;
                                  public void propertyWritten(BACnetObject obj, PropertyValue pv) {
                                      System.out.println("DiscoveryTest propertyWritten");
                                  public void iHaveReceived(RemoteDevice d, RemoteObject o) {
                                      System.out.println("DiscoveryTest iHaveReceived");
                                  public void covNotificationReceived(UnsignedInteger subscriberProcessIdentifier, RemoteDevice initiatingDevice, ObjectIdentifier monitoredObjectIdentifier, UnsignedInteger timeRemaining, SequenceOf<PropertyValue> listOfValues) {
                                      System.out.println("DiscoveryTest covNotificationReceived");
                                  public void eventNotificationReceived(UnsignedInteger processIdentifier, RemoteDevice initiatingDevice, ObjectIdentifier eventObjectIdentifier, TimeStamp timeStamp, UnsignedInteger notificationClass, UnsignedInteger priority, EventType eventType, CharacterString messageText, NotifyType notifyType, Boolean ackRequired, EventState fromState, EventState toState, NotificationParameters eventValues) {
                                      System.out.println("DiscoveryTest eventNotificationReceived");
                                  public void textMessageReceived(RemoteDevice textMessageSourceDevice, Choice messageClass, MessagePriority messagePriority, CharacterString message) {
                                      System.out.println("DiscoveryTest textMessageReceived");
                                  public void privateTransferReceived(UnsignedInteger vendorId, UnsignedInteger serviceNumber, Encodable serviceParameters) {
                                      System.out.println("DiscoveryTest privateTransferReceived");
                           * Send a WhoIs request and wait for the first to answer
                           * @throws java.lang.Exception
                          public void doDiscover() throws Exception {
                              // Who is
                              System.out.println("Send Broadcast WhoIsRequest() ");
                              // Send the broadcast to the correct port of the LoopDevice !!!
                              localDevice.sendBroadcast(loopDevice.getPort(), new WhoIsRequest(null, null));
                              // wait for notification in iAmReceived() Timeout 2 sec
                              synchronized (this) {
                                  final long start = System.currentTimeMillis();
                                  this.wait(2000);
                                  System.out.println(" waited for iAmReceived: " + (System.currentTimeMillis() - start) + " ms");
                              // An other way to get to the list of devices
                              // return localDevice.getRemoteDevices();
                          private void printDevices() throws BACnetException {
                              for (RemoteDevice d : remoteDevices) {
                                  localDevice.getExtendedDeviceInformation(d);
                                  List<ObjectIdentifier> oids = ((SequenceOf<ObjectIdentifier>) localDevice.sendReadPropertyAllowNull(
                                          d, d.getObjectIdentifier(), PropertyIdentifier.objectList)).getValues();
                                  // add the property references of the "device object" to the list
                                  refs.add(d.getObjectIdentifier(), PropertyIdentifier.all);
                                  // and now from all objects under the device object >> ai0, ai1,bi0,bi1...
                                  for (ObjectIdentifier oid : oids) {
                                      refs.add(oid, PropertyIdentifier.all);
                                  System.out.println("Start read properties");
                                  System.out.println(String.format("Properties read done in %d ms", System.currentTimeMillis() - start));
                                  printObject(d.getObjectIdentifier(), pvs);
                                      printObject(oid, pvs);
                              System.out.println("Remote devices done...");
                          private void printObject(ObjectIdentifier oid, PropertyValues pvs) {
                              System.out.println(String.format("\t%s", oid));
                              for (ObjectPropertyReference opr : pvs) {
                                  if (oid.equals(opr.getObjectIdentifier())) {
                                      System.out.println(String.format("\t\t%s = %s", opr.getPropertyIdentifier().toString(), pvs.getNoErrorCheck(opr)));
                           * Note same Bropadcast address, but different ports!!!
                           * @param args
                          @SuppressWarnings("unchecked")
                              ReadAllAvailabeProperties dt = new ReadAllAvailabeProperties(BROADCAST_ADDRESS, LocalDevice.DEFAULT_PORT);
                              try {
                                  dt.setLoopDevice(new LoopDevice(BROADCAST_ADDRESS, LocalDevice.DEFAULT_PORT + 1));
                              } catch (RuntimeException e) {
                                  dt.localDevice.terminate();
                                  throw e;
                              try {
                                  dt.doDiscover();
                                  dt.printDevices();
                              } finally {
                                  System.out.println("Cleanup loopDevice");
                                  dt.getLoopDevice().doTerminate();
                           * @return the loopDevice
                          public LoopDevice getLoopDevice() {
                              return loopDevice;
                           * @param loopDevice the loopDevice to set
                          public void setLoopDevice(LoopDevice loopDevice) {
                              this.loopDevice = loopDevice;
                      If you find this useful, you may add this to CVS.
                      If you interested, I would write a read specific property the old DiscoveryTest and a writeProperty test.
                      Arne
                        Hi Arne,
                        This looks great. I will add it to the distribution, but a couple things:
                        • I changed the class name from ReadAllAvailabeProperties to ReadAllAvailableProperties
                        • You reference a class named LoopDevice for which i don't have the code. Can you provide it? (Is it just a RemoteObject?)
                          apl
                          Ok,
                          here we go:
                          import com.serotonin.bacnet4j.exception.BACnetServiceException;
                          import com.serotonin.bacnet4j.type.enumerated.BinaryPV;
                          import com.serotonin.bacnet4j.type.enumerated.EngineeringUnits;
                          import com.serotonin.bacnet4j.type.enumerated.ObjectType;
                          import com.serotonin.bacnet4j.type.enumerated.Reliability;
                          import com.serotonin.bacnet4j.type.primitive.Real;
                           * software only device default local loop ;-)
                           * @author mlohbihler
                           * @author aploese
                          public class LoopDevice implements Runnable {
                                  LoopDevice ld = new LoopDevice("127.0.0.255", LocalDevice.DEFAULT_PORT + 1);
                                  Thread.sleep(12000); // wait 2 min
                                  ld.doTerminate();
                              private boolean terminate;
                              private BACnetObject ai0;
                              private BACnetObject ai1;
                              private BACnetObject bi0;
                              private BACnetObject bi1;
                              private BACnetObject mso0;
                              private BACnetObject ao0;
                              public LoopDevice(String broadcastAddress, int port) throws BACnetServiceException, IOException {
                                  localDevice = new LocalDevice(1968, broadcastAddress);
                                  try {
                                              System.out.println("loopDevice listenerException");
                                              System.out.println("loopDevice iAmReceived");
                                              System.out.println("loopDevice allowPropertyWrite");
                                              return true;
                                              System.out.println("loopDevice propertyWritten");
                                              System.out.println("loopDevice iHaveReceived");
                                              System.out.println("loopDevice covNotificationReceived");
                                              System.out.println("loopDevice eventNotificationReceived");
                                              System.out.println("loopDevice textMessageReceived");
                                              System.out.println("loopDevice privateTransferReceived");
                                      // for valid property values with valid datatypes see com.serotonin.bacnet4j.obj.ObjectProperties and ther look for the big static block at the end;
                                      // properties of device object
                                      localDevice.getConfiguration().setProperty(PropertyIdentifier.modelName, new CharacterString("BACnet4J LoopDevice"));
                                      // Set up a few objects.
                                      ai0 = new BACnetObject(localDevice, localDevice.getNextInstanceObjectIdentifier(ObjectType.analogInput));
                                      //mandatory properties
                                      ai0.setProperty(PropertyIdentifier.objectName, new CharacterString("G1-RLT03-TM-01")); // this is a cryptic encoded name of a temp sensor from a drawing... (ahm. actually taken from a book ;-))
                                      ai0.setProperty(PropertyIdentifier.presentValue, new Real((float)11));
                                      ai0.setProperty(PropertyIdentifier.outOfService, new Boolean(false));
                                      ai0.setProperty(PropertyIdentifier.units, EngineeringUnits.degreesCelsius);
                                      //some optional properties
                                      ai0.setProperty(PropertyIdentifier.description, new CharacterString("temperature"));
                                      ai0.setProperty(PropertyIdentifier.deviceType, new CharacterString("random values"));
                                      ai0.setProperty(PropertyIdentifier.reliability, Reliability.noFaultDetected);
                                      ai0.setProperty(PropertyIdentifier.updateInterval, new UnsignedInteger(10));
                                      ai0.setProperty(PropertyIdentifier.minPresValue, new Real(-70));
                                      ai0.setProperty(PropertyIdentifier.maxPresValue, new Real(120));
                                      ai0.setProperty(PropertyIdentifier.resolution, new Real((float)0.1));
                                      ai0.setProperty(PropertyIdentifier.profileName, new CharacterString("funny reader"));
                                      localDevice.addObject(ai0);
                                      ai1 = new BACnetObject(
                                      ai1.setProperty(PropertyIdentifier.units, EngineeringUnits.percentObscurationPerFoot);
                                      localDevice.addObject(ai1);
                                      bi0 = new BACnetObject(
                                              localDevice, localDevice.getNextInstanceObjectIdentifier(ObjectType.binaryInput));
                                      localDevice.addObject(bi0);
                                      bi0.setProperty(PropertyIdentifier.objectName, new CharacterString("Off and on"));
                                      bi0.setProperty(PropertyIdentifier.inactiveText, new CharacterString("Off"));
                                      bi0.setProperty(PropertyIdentifier.activeText, new CharacterString("On"));
                                      bi1 = new BACnetObject(
                                      localDevice.addObject(bi1);
                                      bi1.setProperty(PropertyIdentifier.objectName, new CharacterString("Good and bad"));
                                      bi1.setProperty(PropertyIdentifier.inactiveText, new CharacterString("Bad"));
                                      bi1.setProperty(PropertyIdentifier.activeText, new CharacterString("Good"));
                                      mso0 = new BACnetObject(
                                              localDevice, localDevice.getNextInstanceObjectIdentifier(ObjectType.multiStateOutput));
                                      mso0.setProperty(PropertyIdentifier.objectName, new CharacterString("Vegetable"));
                                      mso0.setProperty(PropertyIdentifier.numberOfStates, new UnsignedInteger(4));
                                      mso0.setProperty(PropertyIdentifier.stateText, 1, new CharacterString("Tomato"));
                                      mso0.setProperty(PropertyIdentifier.stateText, 2, new CharacterString("Potato"));
                                      mso0.setProperty(PropertyIdentifier.stateText, 3, new CharacterString("Onion"));
                                      mso0.setProperty(PropertyIdentifier.stateText, 4, new CharacterString("Broccoli"));
                                      mso0.setProperty(PropertyIdentifier.presentValue, new UnsignedInteger(1));
                                      localDevice.addObject(mso0);
                                      ao0 = new BACnetObject(
                                              localDevice, localDevice.getNextInstanceObjectIdentifier(ObjectType.analogOutput));
                                      ao0.setProperty(PropertyIdentifier.objectName, new CharacterString("Settable analog"));
                                      localDevice.addObject(ao0);
                                      // Start the local device.
                                      new Thread(this).start();
                                      System.out.println("Ex in LoopDevice() ");
                                      e.printStackTrace();
                                      localDevice = null;
                                      throw e;
                              public void run() {
                                  try {
                                      System.out.println("LoopDevice start changing values" + this);
                                      // Let it go...
                                      float ai0value = 0;
                                      float ai1value = 0;
                                      boolean bi0value = false;
                                      boolean bi1value = false;
                                      getMso0().setProperty(PropertyIdentifier.presentValue, new UnsignedInteger(2));
                                      while (!isTerminate()) {
                                          System.out.print("Change values of LoopDevice " + this);
                                          // Update the values in the objects.
                                          ai0.setProperty(PropertyIdentifier.presentValue, new Real(ai0value));
                                          ai1.setProperty(PropertyIdentifier.presentValue, new Real(ai1value));
                                          bi0.setProperty(PropertyIdentifier.presentValue, bi0value ? BinaryPV.active : BinaryPV.inactive);
                                          bi1.setProperty(PropertyIdentifier.presentValue, bi1value ? BinaryPV.active : BinaryPV.inactive);
                                              wait(1000); // 1 second or notified (faster exit then stupid wait for 1 second)
                                      System.out.println("Close LoopDevive " + this);
                                  } catch (Exception ex) {
                                  localDevice = null;
                              @Override
                              protected void finalize() throws Throwable {
                                  if (localDevice != null) {
                                      localDevice = null;
                               * @return the terminate
                              public boolean isTerminate() {
                                  return terminate;
                               * @param terminate the terminate to set
                              public void doTerminate() {
                                  this.terminate = true;
                                      this.notifyAll(); // we may wait for this in run() ...
                               * @return the broadcastAddress
                              public String getBroadcastAddress() {
                                  return localDevice.getBroadcastAddress();
                               * @return the port
                              public int getPort() {
                                  return localDevice.getPort();
                               * @return the localDevice
                              public LocalDevice getLocalDevice() {
                                  return localDevice;
                               * @return the ai0
                              public BACnetObject getAi0() {
                                  return ai0;
                               * @return the ai1
                              public BACnetObject getAi1() {
                                  return ai1;
                               * @return the bi0
                              public BACnetObject getBi0() {
                                  return bi0;
                               * @return the bi1
                              public BACnetObject getBi1() {
                                  return bi1;
                               * @return the mso0
                              public BACnetObject getMso0() {
                                  return mso0;
                               * @return the ao0
                              public BACnetObject getAo0() {
                                  return ao0;
                          the classname was a typo, thank you.
                          You (or probably me) can improve it to pass a broadcastaddress and timeout via main().
                          Arne
                            Ok, this has been added with one other change. In ReadAllAvailableProperties at line 220:
                            ... changed to:
                              akc
                              I am also having problems running discovery test.
                              Here is my error message:
                              Exception in thread "main" java.lang.Error: Unresolved compilation problems:
                              The import com.serotonin.util cannot be resolved
                              ObjectUtils cannot be resolved
                              at com.serotonin.bacnet4j.LocalDevice.<init>(LocalDevice.java:96)
                              at DiscoveryTest.main(DiscoveryTest.java:22)
                              I am missing the com.serotonin.util directory. Where do I get this file? I only have com.serotonin.bacnet4j.
                              -Andrew
                                You should have downloaded the seroUtils.jar file as well. This needs to be included in your classpath.
                                  akc
                                  Thanks mlohbihler. sorry for my novice question.
                                  -andrew
                                  • D Offline
                                    drubin
                                    To prevent hair loss for anyone who stumbles upon this thread looking for somewhere to start with bacnet4j... I could not find this code anywhere in the bacnet4j Java package. I created ReadAllAvailabeProperties and LoopDevice classes in my own package. In order for this code to work with the newer versions of bacnet4j I had to replace all occurrences of DeviceEventListener with DefaultDeviceEventListener in both classes. This was just guess but it apparently worked.
                                    • D Offline
                                      drubin
                                      Nevermind on that last post... all the test classes which compile correctly can be found in the source archive: bacnet4J-src.zip which can be found here: http://sourceforge.net/projects/bacnet4j/files/bacnet4j/1.2/
                                      The are not in bacnet4j.jar or seroUtils.jar
                                      I would still love to know the basic design of this package or a good description of the LocalDevice and RemoteDevice classes...
                                      With your input, this post could be even better đź’—