    maJsonStore (JSON store)
    35 Posts 4 Posters 45.5k Views 4 Watching
    • richard.mortimerR Offline
      richard.mortimer @CraigWeb
      @craigweb said in maJsonStore (JSON store):
      Hi Richard
      The best way to cycle through the array that the watchlist gives you is to use the angular filter pipe. You can filter by any point attribute. such as deviceName, name or tag.
      Thanks - is it possible to see some sample/example code (or if you have a site which outlines it) to use the filter?
      Richard
        <div flex="100" flex-gt-md="33" layout="column" ng-if="designer.points | filter:{name:'Level'}:true | maFirst" ng-repeat="res in designer.points | filter:{name:'Level'}:false">
                        <md-card>
                                <md-toolbar class="md-whiteframe-1dp md-hue-3">
                                    <div class="md-toolbar-tools">
                                        <h2 flex="">
                                            <span>{{ res.deviceName }} </span>
                                        </h2>
                                </md-toolbar>
                                <md-card-content>
                                    <div flex="100" layout="row">
                                        <div layout="column" flex="50">
                                            <h2> Level:</h2>
                                            <ma-point-value style=" width: 25%; font-weight: bolder; font-size: 25px;" enable-popup="right" point="res"></ma-point-value>
                                        <div class="flex">
                                            <img ng-src="/rest/v2/file-stores/default/img/Reservoir.svg" style="z-index:-2 width: 200px; height: 150px;">
                            </md-card-content>
                            </md-card>
        My watchlist is a dynamic watchlist the queries all points where the "site" tag matches.
        I then filter down to only have the points with name = "Level" then use ng-repeat to display them all in a md-card.
        Your table might get a little complicated with nested ng-repeats. You might want to read up on the angular docs on how to use ng-repeat-end. https://docs.angularjs.org/api/ng/directive/ngRepeat
        richard.mortimerR 1 Reply Last reply Reply Quote 0
          richard.mortimer
          Thanks - these are working quite well, and I've been making some good progress - I was curious if tags can be set on the edge devices, or if they can only be set on the server?
          Richard
            The edge device and the server runs the same software The ES just has limited hardware capacity. So yes they can be set there and the publisher/data source can be set to update any point properties on the server if they are changed on the ES.
              Does the designer.points map to all points, that then need to be filtered? Or, after adding the tags, do I also need to create a dynamic watchlist (as is kinda eluded to here: https://forum.infiniteautomation.com/topic/4153/using-ma-state-params/15#) to address?
              Richard
                This post is deleted!
                  Designer.points has all the points that are in the watchlist that I created, the watchlist points get brought into the page with a <ma-watch-list-get>
                  So yes you will need to make a watchlist.
                  The other option is to use a
                  <ma-point-query query="{name:query.filter, deviceName:query.filter}" limit="query.limit"
                  start="(query.page-1)*query.limit" sort="query.order" points="points" promise="promise"></ma-point-query>
                  in your page, use {{points}} so show youthe object it returns.
                    richard.mortimer
                    So, just trying to tie together Craig's example and Jared's example above, I'm getting confused how to filter by the tags; so far I have:
                    <ma-point-query query="{deviceName:'SPS001'}" points="points" promise="promise"></ma-point-query>
                    <!-- show me everything -->
                    <!--div style="color: white;background-color:black; border: 1px solid red;" ng-if="points" ><pre>{{points}}</pre></div-->
                    <div md-progress="promise" style="border: 1px solid blue; background-color: white; color: black;" ng-repeat="point in points">
                        <span>{{point.xid}}</span>
                        <span style="background-color: yellow;">{{point.tags.Display}}</span>
                    Which successfully shows me everything that matches the device name in the commented out (first) div, or the secondary DIV, which shows me the same points, but just the XID for the point and the tag for "Display" - but how do I get a specific point from the array if I want the "Display" equal to, say, "Battery Capacity" for this one site? I don't know if I need to put this filter within the ma-point-query section, or if I load the whole array into points and then filter in the ng-repeat section ... nor the syntax, as the tags seem to be at a secondary level of the initial query (as per the two spans, where one is point.xid and the tags are point.tag.Display).
                    BTW: there is a typo on the page: /ui/docs/ng-mango/ma-point-query in the 'limit' description: "no limit by defualt"
                    Richard
                      I can help you with the point query.
                      You can either be specific at what you want at the beginning, or take a multitude of points then filter them accordingly with a filter or using ng-if="point.tags.Display=='displayType'"
                      For your point query, you can work from the watchlist builder to generate an RQL query.
                      You'll get something like:
                      <ma-point-query query="'eq(deviceName,SPS001)&in(tags.Display,Battery Capacity)'" points="points" promise="promise"></ma-point-query>
                      Hope that's of some help
                        Using the query builder as MattFox suggested is definitely a pro tip!
                        Your question seems to be around where best to do the filtering. IMO you will be better off doing one simple query to the backend and then doing all your filtering on the front end. That is if your page is going to have a lot of different components using those points. If the page is focused on only certain points then you could query for only those points. The choice is yours
                        The point query gives you an object with an array of points and all the points attributes, it is not live updating. So now you know that in your page you only have points from SPS001, you can now filter down to the specific point you want in sps001 as such. The syntax is like this because of the nested structure.
                        <ma-point-value point="points | filter:{tags:{Display: 'Battery Capacity'} }"></ma-point-value>
                        You can have multiple filters like such
                        <ma-point-value point="points | filter:{deviceName:'myDevice',tags:{Site: 'myTag'} }"></ma-point-value>
                        If you want to use an ng-repeat then you make your filter less precise that it gives multiple points that match the criteria. You have a couple of options for the order that the ng-repeat will use.
                          richard.mortimer
                          Unfortunately I'm still not getting the results I require; if I put the point query as:
                          <ma-point-query query="'eq(tags.SiteName,SPS001)&&(tags.Display,Customer Load)'" points="points" ></ma-point-query>
                          I'm getting nothing back, but if I put:
                          <ma-point-query query="'eq(tags.SiteName,SPS001)'" points="points" ></ma-point-query>
                          It only returns the tag SiteName and knocks out the tag Display, so I can't further filter on it...
                          Also, when I did get this working (in a different capacity, using the SIteName tag to filter a specific site), the data populated in my DIV, but was destroyed almost instantaneously:
                          <tr ng-repeat="site in sites.sites">
                              <td>
                                  <ma-point-query query="'&in(tags.SiteName,{{site.name}})'" points="points" ></ma-point-query>
                                  <div style="color: white;background-color:black; border: 1px solid red;" ng-if="points | filter:{tags:'Display'}" ><pre>{{points}}</pre></div>
                              </td>
                          Is this where the promise keyword becomes important?
                          Richard
                            Hi Richard
                            The promise variable will have 3 states fulfilled, rejected and pending. It gives you the status of the query. So no is the answer to your question about the promise.
                            There is no operatore for your second criteria. This should work
                            <ma-point-query query="'eq(tags.SiteName,SPS001)&eq(tags.Display,Customer Load)'" points="points" ></ma-point-query>
                            As Mattfox sugested useing the watchlist builder to make your RQL queries. Let me show you how. The nice thing about using this method is there is you can see the results immediately on the query preview tab.
                            As for what you are doing in the table. I think you might be running into scoping issues with using points. Hopefully, @Jared-Wiltshire can comment on that.
                            ng-if="points | filter:{tags:'Display'}" Will not work and I'm sure there are plenty of errors in your browser's console when you use this. tags is an object, what you are doing there is filtering the points array for any object that has a tag with a value of string 'Display'
                            As in my previous post if you want to filter with tags you need to supply a nested object the filter ie:
                            If you want to use it in a ng-if you need to use maFirst
                            point="points | filter:{tags:{Display: 'Battery Capacity'} | maFirst}"
                            Lastly, I think that your pages are getting quite complex and you would be better off creating a user module where you have a controller to do all your logic and mapping of arrays,
                              Hi Richard
                              Thanks - that was the syntax I was after; I couldn't see anything like i in the RQL syntax: https://cubicweb.readthedocs.io/en/3.26/book/annexes/rql/language/#rql
                              Is there somewhere that I can read about this??
                              Also I note that in my nested repeats, this will work, and display all the relevant info for a single point:
                              <ma-json-store xid="sitesDataXID" value="sites"></ma-json-store>
                              <div style="border:2px solid blue;" ng-repeat="site in sites.sites">
                                  <div style="color: white;background-color:black; border: 1px solid red;">--{{ site.name }}--<pre>{{ points }}</pre>--</div>
                              Yet if I change the tag.SiteName to {{site.name}} thus:
                                  <ma-point-query query="'eq(tags.SiteName,{{site.name}})&eq(tags.Display,Customer Load)'" points="points" ></ma-point-query>
                              I'm getting this:
                              Although the browsers (Firefox) code inspector displays the code as it should:
                              So - should that work as I have it, or does Angular not allow variable substitution in this manner? I al;so tried to do it with ' + {{site.name}} + ' and a few variations (but clearly not the right one!)
                              My apologies - I left this in with changing the page so much ...
                              Thanks for that - I'm looking into how that all works ...
                              Richard
                                @richard-mortimer said in maJsonStore (JSON store):
                                Yikes, you're repeating your queries multiple times and calling the same data. We may need to start moving you into angularJS component territory.
                                However, if you're after that site name, you need to do this:
                                    <ma-point-query query="'eq(tags.SiteName,'+site.name+')&eq(tags.Display,Customer Load)'" points="points[site.name]" ></ma-point-query>
                                    <!-- show me everything in this point! -->
                                    <div style="color: white;background-color:black; border: 1px solid red;">--{{ site.name }}--<pre>{{ points[site.name] }}</pre>--</div>
                                if you have points="points" being used every time for each of your ma-point-query items, they'll continue to be updated and overwrite one another as they all share the same scope.
                                Storing them in an object using the site name as the key makes it a bit easier.
                                or alternatively!
                                <div style="border:2px solid blue;" ng-repeat="(index,site) in sites.sites">
                                    <ma-point-query query="'eq(tags.SiteName,'+site.name+')&eq(tags.Display,Customer Load)'" points="points[index]" ></ma-point-query>
                                    <div style="color: white;background-color:black; border: 1px solid red;">--{{ site.name }}--<pre>{{ points[index] }}</pre>--</div>
                                This will map everything by the index in your JSON store.
                                Let me know how you go.
                                  I agree with Mattfox and I think Richard will be more familiar since you can code pure javascript functions in the component controller to manipulate your data. instead of pseudo angular/javascript
                                  I believe you are safe to use points="points" unless points is initiated somewhere else in the ng-repeats parent scope. As ng-repeat creates a scope for each iteration but will first look in the parent scope for points
                                    richard.mortimer
                                    Sorry to drag up an old subject, but I've got a curious thing happening within my repeats - and I'm not sure if it's an Angular issue, or I've done something to upset it ...
                                    My code used two ng-if statements to determine if the value is output value is in watts or kilowatts, thus:
                                    <span ng-repeat="point in points[site.name]"><!-- Load -->
                                        <ma-get-point-value point-xid="{{ point.xid }}" point="output"></ma-get-point-value>
                                        <div ng-if="output.value > 1000">{{ (output.value / 1000) | number:1 }}kW</div>
                                        <div ng-if="output.value <= 1000">{{ output.value | number:0 }}W</div>
                                    </span><!-- end Load -->
                                    The problem is - I'm sometimes getting two values returned, (for example 984W and 1kW) - if I directyly print the value on the screen via {{ output.value }} I'm seeing what I would expect to see (mostly integers, a couple of float types for some points).
                                    Am I doing something wrong here, or is there a better way to do this?
                                    [edit] Here's one I managed to catch as it happened:0_1559714978372_output_error.jpg
                                    Richard
                                      Evening Richard!
                                      Are your points numeric types or alphanumeric?
                                      I say keep it simple and just do
                                          <div ng-if="parseInt(output.value) > 1000">{{  parseFloat(output.value / 1000).toFixed(1) }}kW</div>
                                          <div ng-if="parseInt(output.value) <= 1000">{{ Number(output.value)}}W</div>
                                      You don't have to use what I put int the div inner HTML. But as far as the ng-if is concerned at least you'd have a consistent read with your values.
                                        richard.mortimer @MattFox
                                        @mattfox said in maJsonStore (JSON store):
                                        Evening Richard!
                                        I believed they were simply numeric - but whern I add the parseInt(output.value) everything disappears (as in - neither ng-if statement is true), similarly the same with the Number and parseFloat functions ...
                                        If I do: <script>console.log(typeof {{output.value}});</script> I get:
                                        Richard
                                          I'll just have a quick look in the mango dash to see fi I can run some tests.
                                          As for typeof you want: note javascript generally has a numeric. doesn't have ints or floats like compiled languages.
                                          {{ typeof output.value }} //although i'm not confident if it will work...
                                            Nope, that didn't work ... :(
