    maJsonStore (JSON store)
    35 Posts 4 Posters 44.5k Views 4 Watching
    • richard.mortimerR Offline
      richard.mortimer
      Unfortunately I'm still not getting the results I require; if I put the point query as:
      <ma-point-query query="'eq(tags.SiteName,SPS001)&&(tags.Display,Customer Load)'" points="points" ></ma-point-query>
      I'm getting nothing back, but if I put:
      <ma-point-query query="'eq(tags.SiteName,SPS001)'" points="points" ></ma-point-query>
      It only returns the tag SiteName and knocks out the tag Display, so I can't further filter on it...
      Also, when I did get this working (in a different capacity, using the SIteName tag to filter a specific site), the data populated in my DIV, but was destroyed almost instantaneously:
      <tr ng-repeat="site in sites.sites">
          <td>
              <ma-point-query query="'&in(tags.SiteName,{{site.name}})'" points="points" ></ma-point-query>
              <div style="color: white;background-color:black; border: 1px solid red;" ng-if="points | filter:{tags:'Display'}" ><pre>{{points}}</pre></div>
          </td>
      Is this where the promise keyword becomes important?
      Richard
        Hi Richard
        The promise variable will have 3 states fulfilled, rejected and pending. It gives you the status of the query. So no is the answer to your question about the promise.
        There is no operatore for your second criteria. This should work
        <ma-point-query query="'eq(tags.SiteName,SPS001)&eq(tags.Display,Customer Load)'" points="points" ></ma-point-query>
        As Mattfox sugested useing the watchlist builder to make your RQL queries. Let me show you how. The nice thing about using this method is there is you can see the results immediately on the query preview tab.
        As for what you are doing in the table. I think you might be running into scoping issues with using points. Hopefully, @Jared-Wiltshire can comment on that.
        ng-if="points | filter:{tags:'Display'}" Will not work and I'm sure there are plenty of errors in your browser's console when you use this. tags is an object, what you are doing there is filtering the points array for any object that has a tag with a value of string 'Display'
        As in my previous post if you want to filter with tags you need to supply a nested object the filter ie:
        point="points | filter:{tags:{Display: 'Battery Capacity'} }"
        If you want to use it in a ng-if you need to use maFirst
        point="points | filter:{tags:{Display: 'Battery Capacity'} | maFirst}"
        Lastly, I think that your pages are getting quite complex and you would be better off creating a user module where you have a controller to do all your logic and mapping of arrays,
        richard.mortimerR 1 Reply Last reply Reply Quote 0
          richard.mortimer @CraigWeb
          @craigweb said in maJsonStore (JSON store):
          Hi Richard
          Thanks - that was the syntax I was after; I couldn't see anything like i in the RQL syntax: https://cubicweb.readthedocs.io/en/3.26/book/annexes/rql/language/#rql
          Is there somewhere that I can read about this??
          Also I note that in my nested repeats, this will work, and display all the relevant info for a single point:
          <ma-json-store xid="sitesDataXID" value="sites"></ma-json-store>
          <div style="border:2px solid blue;" ng-repeat="site in sites.sites">
              <!-- show me everything -->
              <div style="color: white;background-color:black; border: 1px solid red;">--{{ site.name }}--<pre>{{ points }}</pre>--</div>
          Yet if I change the tag.SiteName to {{site.name}} thus:
              <ma-point-query query="'eq(tags.SiteName,{{site.name}})&eq(tags.Display,Customer Load)'" points="points" ></ma-point-query>
          I'm getting this:
          Although the browsers (Firefox) code inspector displays the code as it should:
          So - should that work as I have it, or does Angular not allow variable substitution in this manner? I al;so tried to do it with ' + {{site.name}} + ' and a few variations (but clearly not the right one!)
          My apologies - I left this in with changing the page so much ...
          Thanks for that - I'm looking into how that all works ...
          Richard
            @richard-mortimer said in maJsonStore (JSON store):
            Yikes, you're repeating your queries multiple times and calling the same data. We may need to start moving you into angularJS component territory.
            However, if you're after that site name, you need to do this:
                <ma-point-query query="'eq(tags.SiteName,'+site.name+')&eq(tags.Display,Customer Load)'" points="points[site.name]" ></ma-point-query>
                <!-- show me everything in this point! -->
                <div style="color: white;background-color:black; border: 1px solid red;">--{{ site.name }}--<pre>{{ points[site.name] }}</pre>--</div>
            if you have points="points" being used every time for each of your ma-point-query items, they'll continue to be updated and overwrite one another as they all share the same scope.
            Storing them in an object using the site name as the key makes it a bit easier.
            or alternatively!
            <div style="border:2px solid blue;" ng-repeat="(index,site) in sites.sites">
                <ma-point-query query="'eq(tags.SiteName,'+site.name+')&eq(tags.Display,Customer Load)'" points="points[index]" ></ma-point-query>
                <div style="color: white;background-color:black; border: 1px solid red;">--{{ site.name }}--<pre>{{ points[index] }}</pre>--</div>
            This will map everything by the index in your JSON store.
            Let me know how you go.
              I agree with Mattfox and I think Richard will be more familiar since you can code pure javascript functions in the component controller to manipulate your data. instead of pseudo angular/javascript
              I believe you are safe to use points="points" unless points is initiated somewhere else in the ng-repeats parent scope. As ng-repeat creates a scope for each iteration but will first look in the parent scope for points
                richard.mortimer
                Sorry to drag up an old subject, but I've got a curious thing happening within my repeats - and I'm not sure if it's an Angular issue, or I've done something to upset it ...
                My code used two ng-if statements to determine if the value is output value is in watts or kilowatts, thus:
                <span ng-repeat="point in points[site.name]"><!-- Load -->
                    <ma-get-point-value point-xid="{{ point.xid }}" point="output"></ma-get-point-value>
                    <div ng-if="output.value > 1000">{{ (output.value / 1000) | number:1 }}kW</div>
                    <div ng-if="output.value <= 1000">{{ output.value | number:0 }}W</div>
                </span><!-- end Load -->
                The problem is - I'm sometimes getting two values returned, (for example 984W and 1kW) - if I directyly print the value on the screen via {{ output.value }} I'm seeing what I would expect to see (mostly integers, a couple of float types for some points).
                Am I doing something wrong here, or is there a better way to do this?
                [edit] Here's one I managed to catch as it happened:0_1559714978372_output_error.jpg
                Richard
                  Evening Richard!
                  Are your points numeric types or alphanumeric?
                  I say keep it simple and just do
                      <div ng-if="parseInt(output.value) > 1000">{{  parseFloat(output.value / 1000).toFixed(1) }}kW</div>
                      <div ng-if="parseInt(output.value) <= 1000">{{ Number(output.value)}}W</div>
                  You don't have to use what I put int the div inner HTML. But as far as the ng-if is concerned at least you'd have a consistent read with your values.
                    richard.mortimer @MattFox
                    @mattfox said in maJsonStore (JSON store):
                    Evening Richard!
                    I believed they were simply numeric - but whern I add the parseInt(output.value) everything disappears (as in - neither ng-if statement is true), similarly the same with the Number and parseFloat functions ...
                    If I do: <script>console.log(typeof {{output.value}});</script> I get:
                    Richard
                      I'll just have a quick look in the mango dash to see fi I can run some tests.
                      As for typeof you want: note javascript generally has a numeric. doesn't have ints or floats like compiled languages.
                      {{ typeof output.value }} //although i'm not confident if it will work...
                        Nope, that didn't work ... :(
                          Ok, I can't replicate it. Let's go back to how you had it.
                          But make it this for your ng-ifs
                              <div ng-if="output.value < 1001">{{ output.value | number:0 }}W</div></span><!-- end Load -->
                          Just humour me please.
                          EDIT: Could you also please give me a copy of the {{output}} for the problem one?
                            richard.mortimer
                            {{output}} is:
                               "id":2986,
                               "xid":"S2.DP_HOD-002_827990",
                               "name":"Customer Load - Active Power",
                               "enabled":true,
                               "deviceName":"H02 - B-30",
                               "readPermission":"RO, user",
                               "setPermission":"",
                               "pointFolderId":387,
                               "purgeOverride":false,
                               "unit":"W",
                               "useIntegralUnit":false,
                               "useRenderedUnit":false,
                               "pointLocator":{
                                  "dataType":"NUMERIC",
                                  "settable":false,
                                  "modelType":"PL.PERSISTENT",
                                  "relinquishable":false
                               "chartColour":"black",
                               "plotType":"SPLINE",
                               "loggingProperties":{
                                  "loggingType":"ALL",
                                  "tolerance":0,
                                  "discardExtremeValues":false,
                                  "cacheSize":1
                               "textRenderer":{
                                  "useUnitAsSuffix":true,
                                  "unit":"W",
                                  "renderedUnit":"W",
                                  "format":"####.##",
                                  "suffix":"",
                                  "type":"textRendererAnalog"
                               "chartRenderer":{
                                  "timePeriod":{
                                     "periods":1,
                                     "type":"DAYS"
                                  "type":"chartRendererImage"
                               "rollup":"NONE",
                               "simplifyType":"NONE",
                               "simplifyTolerance":10,
                               "simplifyTarget":5000,
                               "templateXid":null,
                               "dataSourceId":116,
                               "dataSourceXid":"DS_Central_T_E01",
                               "dataSourceName":"Central-T-E01",
                               "dataSourceTypeName":"PERSISTENT",
                               "tags":{
                                  "SiteName":"S002",
                                  "Display":"Customer Load"
                               "lastPayload":{
                                  "xid":"SPS002.DP_HOD-002_827990",
                                  "event":"UPDATE",
                                  "value":{
                                     "value":118,
                                     "timestamp":1559717556655,
                                     "annotation":null
                                  "renderedValue":"118 W",
                                  "convertedValue":118,
                                  "enabled":true,
                                  "attributes":{
                                     "UNRELIABLE":false
                               "value":118,
                               "time":1559717556655,
                               "unreliable":false
                            Richard
                              Sorry Richard, I'm not seeing anything sticking out here. The only thoughts I have is echoing out {{output}} inbetween both of the ng-if divs. Seeing how you're having two appear in one area makes me wonder if there's some sort of overlap or something stupid. Your values are definitely numeric.
                              The next best idea Ive got is checking your console after doing a page load to see if any angular errors crop up..
                              Otherwise I'm gonna have to call on Jared or Phil to help here. Sorry I cannot be of any further assistance. Either that or I'm just simply half asleep and it's staring me in the face!
                                That's cool - I'm kinda glad it wasn't something glaringly obvious, and I appreciate your help!!
                                Getting a couple of errors, but I'm not sure they are related:
                                Richard
                                  CraigWeb @richard.mortimer
                                  @richard-mortimer Hi
                                  I don't think you need to user parseInt etc as javascript will evaluate it as a number when there is a comparator.
                                  I tested this out with this code and got the desirable outcome
                                  <div class="ma-designer-root" id="ad15c8a3-1798-45ab-9771-535bb550b828" style="width: 1366px; height: 768px; position: relative;" ng-init="points=[
                                      {xid:'DP_3414e074-39ae-4179-b3e7-0775e7cabc54'},
                                      {xid:'DP_a7485f76-5c52-4c42-b49a-f17b3276a2f8'}]">
                                  <span ng-repeat="point in points">
                                      <div ng-if="output.value > 999">{{ (output.value / 1000) }}kW</div>
                                      <div ng-if="output.value < 1000">{{ (output.value)}}W</div>
                                  If you look at your screen shot where the 'error" happens , 1.4kW is from the previous ng-repeat itteration.
                                  We can't see the rest of your code but by the looks of it, you have a table with nested repeats. I think you should refactor your code using ng-repeat-start and ng-repeat-end for all you nested repeats just to make sure the browser does not get confused.
                                  Edit:
                                  Another way to skin this cat would be to use a ternary expression.
                                      <div>{{output.value >1000? output.value/1000:output.value}}{{output.value >1000?'kW':'W'}}</div>
                                    @richard-mortimer I'm taking a guess at what is happening, but I'm pretty confident that this will fix it -
                                    <span ng-repeat="point in points[site.name] track by point.xid"><!-- Load -->
                                        <ma-get-point-value point="point"></ma-get-point-value>
                                        <div ng-if="point.value > 1000">{{ (point.value / 1000) | number:1 }}kW</div>
                                        <div ng-if="point.value <= 1000">{{ point.value | number:0 }}W</div>
                                    Two things -
                                    • Use track by in your ng-repeat expression so that Angular can correlate which points correspond to each span element when the points change.
                                    • Just pass the point to the <ma-get-point-value> component instead of retrieving it by XID again
                                    richard.mortimerR 1 Reply Last reply Reply Quote 1
                                      richard.mortimer @Jared Wiltshire
                                      @jared-wiltshire said in maJsonStore (JSON store):
                                      Two things -
                                      Thanks for that - I've made the changes and will keep an eye on it; unfortunately it only seems to happen at random times which makes it one of those "fun" bugs to iron out ... but I'm pretty confident that if you're pretty confident, it will probably be the right solution! :)
                                      Cheers!!
                                      Richard
                                        Sorry, I missed this reply - you are correct it's inside a larger loop, which iterates through each device - I'm going to try the ternary operator and see how that goes ...
                                        Any idea how to put the number filter in there? The kW was to one decimal place, and the W was to 0 ...
                                        Richard
                                        MattFoxM Jared WiltshireJ 2 Replies Last reply Reply Quote 0
                                          MattFox @richard.mortimer
                                          @richard-mortimer I believe when you did | number:1 and | number:0 was more than sufficient. alternatively just use point.value.toFixed(1) and point.value.toFixed() repectively
                                            Jared Wiltshire @richard.mortimer
                                            You would need another ternary operator. IMO the way you had it in the first place is easier to read.
                                            If you use this pattern often, consider adding an AngularJS filter to a user module. You could then use it just like
                                            <span ng-bind="point.value | formatPower"></span>