    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
    Radix IoT Website Mango 4 Documentation Website Mango 5 Documentation Website Radix IoT LinkedIn
    Server Time out
    Scheduled Pinned Locked Moved User help
    15 Posts 4 Posters 5.4k Views 4 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • J Offline
      JAST
      Hello,
      I am having issues when I click on Datasources. It shows the server timeout error.0_1541604159082_Screenshot_3.png .I have a log file and it shows bunch of errors I couldn't understand.I would appreciate guidance in this problem,
      1 Reply Last reply Reply Quote 0
      • Jared WiltshireJ Offline
        Jared Wiltshire
        @gquiroz I sometimes get that message too, mainly when I have a lot of data points. Do you actually have any data sources set up? Please post the relevant section of your log file which shows the errors and let us know your version numbers.
        https://help.infiniteautomation.com/reporting-bugs/
        Developer at Radix IoT
        • J Offline
          JAST
          we are using v2.8
          We originally had 6 data sources and roughly over 100 datapoints. They were uploaded and everything was working fine. We recently show that error occurrence starting with a java server dll file reference, this has been resolved.
          [link text](link url)Here is the link for the log file. I am not able to figure out which part is relevant. https://drive.google.com/file/d/1pSpX5Q-H73QFa1PGrFStUWVmvoltVbKl/view?usp=sharing
          • CraigWebC Offline
            CraigWeb
            I get this often when working on a cloud server. Haven't seen it when working on a localhost like you are experiencing.
            • phildunlapP Offline
              phildunlap
              Hi gquiroz,
              There are many exceptions in the file, all could suggest things to improve.
              Starting at the bottom and working backwards,
              ERROR 2018-11-07 11:19:41,446 (com.serotonin.m2m2.Main.main:119) - Error during initialization
              java.lang.RuntimeException: java.net.BindException: Address already in use: bind
              	at com.serotonin.m2m2.Lifecycle.webServerInitialize(Lifecycle.java:810)
              	at com.serotonin.m2m2.Lifecycle.initialize(Lifecycle.java:223)
              	at com.serotonin.m2m2.Main.main(Main.java:115)
              Caused by: java.net.BindException: Address already in use: bind
              	at sun.nio.ch.Net.bind0(Native Method)
              	at sun.nio.ch.Net.bind(Unknown Source)
              	at sun.nio.ch.ServerSocketChannelImpl.bind(Unknown Source)
              	at sun.nio.ch.ServerSocketAdaptor.bind(Unknown Source)
              	at org.eclipse.jetty.server.ServerConnector.open(ServerConnector.java:321)
              	at org.eclipse.jetty.server.AbstractNetworkConnector.doStart(AbstractNetworkConnector.java:80)
              	at org.eclipse.jetty.server.ServerConnector.doStart(ServerConnector.java:236)
              	at org.eclipse.jetty.util.component.AbstractLifeCycle.start(AbstractLifeCycle.java:68)
              	at org.eclipse.jetty.server.Server.doStart(Server.java:366)
              	at com.serotonin.m2m2.Lifecycle.webServerInitialize(Lifecycle.java:807)
              	... 2 more
              Suggests the previous launch of Mango is still running. Usually if you close the command prompt Window that it was launched in, Mango will have stopped, but, you may need to kill Java in your Task Manager.
              FATAL 2018-11-07 10:18:30,555 (com.serotonin.m2m2.util.timeout.RejectedRunnableEventGenerator.rejectedExecution:51) - Task com.serotonin.ma.bacnet.BACnetDataSourceRT$1@19e4bfd rejected from com.serotonin.timer.OrderedThreadPoolExecutor@997126[Running, pool size = 100, active threads = 100, queued tasks = 0, completed tasks = 996]
              java.util.concurrent.RejectedExecutionException: Task com.serotonin.ma.bacnet.BACnetDataSourceRT$1@19e4bfd rejected from com.serotonin.timer.OrderedThreadPoolExecutor@997126[Running, pool size = 100, active threads = 100, queued tasks = 0, completed tasks = 996]
              	at com.serotonin.m2m2.util.timeout.RejectedRunnableEventGenerator.rejectedExecution(RejectedRunnableEventGenerator.java:50)
              	at com.serotonin.timer.OrderedThreadPoolExecutor.rejectedExecution(OrderedThreadPoolExecutor.java:215)
              	at java.util.concurrent.ThreadPoolExecutor.reject(Unknown Source)
              	at java.util.concurrent.ThreadPoolExecutor.execute(Unknown Source)
              	at com.serotonin.timer.TimerThread.execute(TimerThread.java:53)
              	at com.serotonin.timer.RealTimeTimer.execute(RealTimeTimer.java:86)
              	at com.serotonin.ma.bacnet.BACnetDataSourceRT.iAmReceived(BACnetDataSourceRT.java:531)
              	at com.serotonin.bacnet4j.event.DeviceEventHandler.fireIAmReceived(DeviceEventHandler.java:99)
              	at com.serotonin.bacnet4j.service.unconfirmed.IAmRequest.handle(IAmRequest.java:95)
              	at com.serotonin.bacnet4j.transport.DefaultTransport.receiveAPDU(DefaultTransport.java:539)
              	at com.serotonin.bacnet4j.transport.DefaultTransport.receiveImpl(DefaultTransport.java:463)
              	at com.serotonin.bacnet4j.transport.DefaultTransport.run(DefaultTransport.java:404)
              	at java.lang.Thread.run(Unknown Source)
              In 2.x BACnet could get pretty thread hungry. It was best practice to combine BACnet data sources together whenever possible. You could also increase your maximum high priority thread pool limit.
              FATAL 2018-11-07 10:15:20,063 (com.serotonin.timer.TimerThread.run:41) - TimerThread failed
              org.springframework.jdbc.CannotGetJdbcConnectionException: Could not get JDBC Connection; nested exception is org.h2.jdbc.JdbcSQLException: Out of memory. [90108-181]
              	at org.springframework.jdbc.datasource.DataSourceUtils.getConnection(DataSourceUtils.java:80)
              	at org.springframework.jdbc.core.JdbcTemplate.execute(JdbcTemplate.java:615)
              	at org.springframework.jdbc.core.JdbcTemplate.query(JdbcTemplate.java:680)
              	at org.springframework.jdbc.core.JdbcTemplate.query(JdbcTemplate.java:712)
              	at org.springframework.jdbc.core.JdbcTemplate.query(JdbcTemplate.java:722)
              	at org.springframework.jdbc.core.JdbcTemplate.query(JdbcTemplate.java:772)
              	at com.serotonin.db.DaoUtils.query(DaoUtils.java:308)
              	at com.serotonin.m2m2.db.dao.EventHandlerDao.getEventHandlers(EventHandlerDao.java:155)
              	at com.serotonin.m2m2.db.dao.EventHandlerDao.getEventHandlers(EventHandlerDao.java:125)
              	at com.serotonin.m2m2.rt.EventManager.setHandlers(EventManager.java:804)
              	at com.serotonin.m2m2.rt.EventManager.raiseEvent(EventManager.java:111)
              	at com.serotonin.m2m2.rt.event.type.SystemEventType.raiseEvent(SystemEventType.java:99)
              	at com.serotonin.m2m2.util.timeout.RejectedRunnableEventGenerator.rejectedExecution(RejectedRunnableEventGenerator.java:58)
              	at com.serotonin.timer.OrderedThreadPoolExecutor.execute(OrderedThreadPoolExecutor.java:179)
              	at com.serotonin.timer.OrderedTimerThread.executeTask(OrderedTimerThread.java:28)
              	at com.serotonin.timer.TimerThread.mainLoop(TimerThread.java:127)
              	at com.serotonin.timer.TimerThread.run(TimerThread.java:38)
              Caused by: org.h2.jdbc.JdbcSQLException: Out of memory. [90108-181]
              	at org.h2.message.DbException.getJdbcSQLException(DbException.java:345)
              	at org.h2.message.DbException.get(DbException.java:168)
              	at org.h2.message.DbException.convert(DbException.java:289)
              	at org.h2.engine.Database.openDatabase(Database.java:297)
              	at org.h2.engine.Database.<init>(Database.java:260)
              	at org.h2.engine.Engine.openSession(Engine.java:60)
              	at org.h2.engine.Engine.openSession(Engine.java:167)
              	at org.h2.engine.Engine.createSessionAndValidate(Engine.java:145)
              	at org.h2.engine.Engine.createSession(Engine.java:128)
              	at org.h2.engine.Engine.createSession(Engine.java:26)
              	at org.h2.engine.SessionRemote.connectEmbeddedOrServer(SessionRemote.java:347)
              	at org.h2.jdbc.JdbcConnection.<init>(JdbcConnection.java:108)
              	at org.h2.jdbc.JdbcConnection.<init>(JdbcConnection.java:92)
              	at org.h2.Driver.connect(Driver.java:72)
              	at org.h2.jdbcx.JdbcDataSource.getJdbcConnection(JdbcDataSource.java:190)
              	at org.h2.jdbcx.JdbcDataSource.getXAConnection(JdbcDataSource.java:353)
              	at org.h2.jdbcx.JdbcDataSource.getPooledConnection(JdbcDataSource.java:385)
              	at org.h2.jdbcx.JdbcConnectionPool.getConnectionNow(JdbcConnectionPool.java:227)
              	at org.h2.jdbcx.JdbcConnectionPool.getConnection(JdbcConnectionPool.java:199)
              	at org.springframework.jdbc.datasource.DataSourceUtils.doGetConnection(DataSourceUtils.java:111)
              	at org.springframework.jdbc.datasource.DataSourceUtils.getConnection(DataSourceUtils.java:77)
              	... 19 more
              That's the killer for sure. Once the TimerThread is cancelled, you need to restart Mango. I wonder if your Mango/databases/mah2.h2.db file has grown, and that is why you're seeing memory issues now where you did not before. You can find many threads with instructions on shrinking the H2 database, but in short it's a SQL backup / restore. You may also need to purge your events, userEvents, and audit tables, as well as the pointValues table since from your logs I can see you are not using the NoSQL module.
              ERROR 2018-11-07 10:14:06,918 (org.apache.taglibs.log.LoggerTag.doStartTag:97) - org.springframework.jdbc.CannotGetJdbcConnectionException: Could not get JDBC Connection; nested exception is org.h2.jdbc.JdbcSQLException: The database has been closed [90098-181]
              	at com.serotonin.db.spring.ExtendedJdbcTemplate.queryForObject(ExtendedJdbcTemplate.java:39)
              	at com.serotonin.db.spring.ExtendedJdbcTemplate.queryForObject(ExtendedJdbcTemplate.java:63)
              	at com.serotonin.db.DaoUtils.queryForObject(DaoUtils.java:336)
              	at com.serotonin.m2m2.db.dao.SystemSettingsDao.getValue(SystemSettingsDao.java:158)
              	at com.serotonin.m2m2.db.dao.SystemSettingsDao.getValue(SystemSettingsDao.java:151)
              	at com.serotonin.m2m2.db.dao.SystemSettingsDao.getColour(SystemSettingsDao.java:283)
              	at com.serotonin.m2m2.util.chart.ImageChartUtils.writeChart(ImageChartUtils.java:74)
              	at com.serotonin.m2m2.util.chart.ImageChartUtils.getChartData(ImageChartUtils.java:63)
              	at com.serotonin.m2m2.util.chart.ImageChartUtils.getChartData(ImageChartUtils.java:55)
              	at com.serotonin.m2m2.web.servlet.ImageChartServlet.getImageData(ImageChartServlet.java:233)
              	at com.serotonin.m2m2.web.servlet.ImageChartServlet.doGet(ImageChartServlet.java:73)
              	at javax.servlet.http.HttpServlet.service(HttpServlet.java:687)
              	at javax.servlet.http.HttpServlet.service(HttpServlet.java:790)
              	at org.eclipse.jetty.servlet.ServletHolder.handle(ServletHolder.java:808)
              	at org.eclipse.jetty.servlet.ServletHandler$CachedChain.doFilter(ServletHandler.java:1669)
              	at org.eclipse.jetty.servlets.UserAgentFilter.doFilter(UserAgentFilter.java:83)
              	at org.eclipse.jetty.servlets.GzipFilter.doFilter(GzipFilter.java:364)
              	at org.eclipse.jetty.servlet.ServletHandler$CachedChain.doFilter(ServletHandler.java:1652)
              	at org.springframework.web.filter.ShallowEtagHeaderFilter.doFilterInternal(ShallowEtagHeaderFilter.java:87)
              	at com.serotonin.m2m2.web.filter.MangoShallowEtagHeaderFilter.doFilterInternal(MangoShallowEtagHeaderFilter.java:47)
              	at org.springframework.web.filter.OncePerRequestFilter.doFilter(OncePerRequestFilter.java:107)
              	at org.eclipse.jetty.servlet.ServletHandler.doHandle(ServletHandler.java:585)
              	at org.eclipse.jetty.server.handler.ScopedHandler.handle(ScopedHandler.java:143)
              	at org.eclipse.jetty.security.SecurityHandler.handle(SecurityHandler.java:577)
              	at org.eclipse.jetty.server.session.SessionHandler.doHandle(SessionHandler.java:223)
              	at org.eclipse.jetty.server.handler.ContextHandler.doHandle(ContextHandler.java:1127)
              	at org.eclipse.jetty.servlet.ServletHandler.doScope(ServletHandler.java:515)
              	at org.eclipse.jetty.server.session.SessionHandler.doScope(SessionHandler.java:185)
              	at org.eclipse.jetty.server.handler.ContextHandler.doScope(ContextHandler.java:1061)
              	at org.eclipse.jetty.server.handler.ScopedHandler.handle(ScopedHandler.java:141)
              	at org.eclipse.jetty.server.handler.ContextHandlerCollection.handle(ContextHandlerCollection.java:215)
              	at org.eclipse.jetty.server.handler.HandlerWrapper.handle(HandlerWrapper.java:97)
              	at org.eclipse.jetty.server.Server.handle(Server.java:499)
              	at org.eclipse.jetty.server.HttpChannel.handle(HttpChannel.java:310)
              	at org.eclipse.jetty.server.HttpConnection.onFillable(HttpConnection.java:257)
              	at org.eclipse.jetty.io.AbstractConnection$2.run(AbstractConnection.java:540)
              	at org.eclipse.jetty.util.thread.QueuedThreadPool.runJob(QueuedThreadPool.java:635)
              	at org.eclipse.jetty.util.thread.QueuedThreadPool$3.run(QueuedThreadPool.java:555)
              Caused by: org.h2.jdbc.JdbcSQLException: The database has been closed [90098-181]
              	at org.h2.message.DbException.get(DbException.java:179)
              	at org.h2.message.DbException.get(DbException.java:155)
              	at org.h2.message.DbException.get(DbException.java:144)
              	at org.h2.engine.Database.checkPowerOff(Database.java:496)
              	at org.h2.command.Command.executeUpdate(Command.java:274)
              	at org.h2.jdbc.JdbcConnection.rollbackInternal(JdbcConnection.java:1501)
              	at org.h2.jdbc.JdbcConnection.rollback(JdbcConnection.java:489)
              	at org.h2.jdbcx.JdbcXAConnection.getConnection(JdbcXAConnection.java:107)
              	at org.h2.jdbcx.JdbcConnectionPool.getConnectionNow(JdbcConnectionPool.java:229)
              	... 44 more
              Likely caused by a memory error that occurred before this log starts. After all, there's a lot of spam in there from the BACnet data sources consuming all the threads.
              • J Offline
                JAST
                Hello Phil I tried all the things except the sql backup and restore thing because when I logged in mysql there was no sql database.So what can I do in this situation?
                  phildunlap
                  Did you get Mango restarted? It's all from the memory error. With SQL the database expansion can be managed just by keeping the tables mentioned in check (which you could do at the command line). It's not necessary to do a dump/restore - I assumed you were using the H2 database.
                  • J Offline
                    JAST
                    Yes I restarted the mango but it is same issue.I think there is something wrong with database. Beacuse when I removed the database file and started mango again it was working fine and it also created new h2database file.
                      phildunlap
                      It would not switch database types....
                      Do you have a Mango/databases/mah2.h2.db file and how big is it?
                      If you are using H2 then the MySQL command line program won't be of use to us.
                      • J Offline
                        JAST
                        It's size is 1.58Gb
                          phildunlap
                          You can use the /system_settings.shtm page to create a SQL backup (SQL Backup section), then stop Mango, move the existing database so that Mango starts on a new database, start Mango, and then restore the SQL backup in the same section on the /system_settings.shtm page. There's other information here: https://forum.infiniteautomation.com/topic/2748/how-to-restore-a-database-backup Having a smaller H2 database may help some, generally.
                          Which issue? The memory is instantly running out or there is a bind exception because something is already running on the port you are trying to launch Mango on?
                          • J Offline
                            JAST
                            memory is running out .
                              phildunlap
                              You can
                              1. Use Mango/bin/h2-web-console script (bat or sh) to connect to the H2 database without running Mango. This would allow you to delete from the events, userEvents, audit, or pointValues tables. I would guess you need to purge events and userEvents at the very least, like DELETE FROM events; DELETE FROM userEvents; Mango needs to be stopped.
                              2. Start in SAFE mode. This will start will all data sources disabled, if for some reason they're the source of the memory loss.
                              3. Start on a clean database and restore an existing backup using the SQL backup configuration section of the /system_settings.shtm page.
                              4. Ensure a proper amount of memory has been allocated to Mango in a Mango/bin/ext-enabled script.
                              • J Offline
                                JAST
                                I tried connecting to h2 databse via console after stopping mango.i got this error.
                                "IO Exception: "C:/Users/DCU/test outside C:/Mango" [90028-181] 90028/90028 (Help)
                                org.h2.jdbc.JdbcSQLException: IO Exception: "C:/Users/DCU/test outside C:/Mango" [90028-181]
                                at org.h2.engine.ConnectionInfo.setBaseDir(ConnectionInfo.java:182)
                                at org.h2.jdbc.JdbcConnection.<init>(JdbcConnection.java:104)
                                at org.h2.server.web.WebServer.getConnection(WebServer.java:750)
                                at org.h2.server.web.WebApp.login(WebApp.java:957)
                                at org.h2.server.web.WebApp.process(WebApp.java:211)
                                at org.h2.server.web.WebApp.processRequest(WebApp.java:170)
                                at org.h2.server.web.WebThread.process(WebThread.java:137)
                                at org.h2.server.web.WebThread.run(WebThread.java:93)
                                at java.lang.Thread.run(Unknown Source) "
                                  phildunlap
                                  The webserver cannot try to open a database URL outside its Mango directory. You're probably looking for a URL of jdbc:h2:C:/Mango/databases/mah2
                                  Hello! It looks like you're interested in this conversation, but you don't have an account yet.
                                  Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.