    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
    Radix IoT Website Mango 4 Documentation Website Mango 5 Documentation Website Radix IoT LinkedIn
    Modbus "active source point has no value"
    Scheduled Pinned Locked Moved User help
    6 Posts 4 Posters 2.5k Views 3 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • P Offline
      Pedro
      I created a new Modbus/TCP datasource with a 1-second update period, like many other Modbus datasources that are working fine. However, this new Modbus source reports "active source point has no value" for some datapoints, even though they worked when performing a "Point locator test" on the datasource page. On the graphical view, these points report "point value may not be reliable" and display "(n/a)" rather than a numerical value. The event page filled up with "Illegal data value" datasource alarms.
      Why would the "Point locator test" work, but not the point it created?
      Shouldn't the Modbus I/O log file report I/O originated from the Modbus read/write tools on the Datasource page?
      The following is pasted from the Modules page:
      core 2.8.8 build 635 - paid
      modbus 1.8.0 - paid
      Thanks
      1 Reply Last reply Reply Quote 0
      • JoelHaggarJ Offline
        JoelHaggar
        I would suggest reducing the "Max read register count" value and/or checking the "Contiguous batches only" box. When you use the Point Locator tool it's just a single request but when you turn on the whole Data Source the default request might be too large for the device so you could get a partial response.
        • P Offline
          Pedro
          "Contigous batches only" solved the problem. Thanks.
          Shouldn't the IO log file also log the individual read/write I/O operations (i.e. shouldn't it log ALL I/O)?
          • phildunlapP Offline
            phildunlap
            Yes it should have logged the IO.
            Very likely there was a register that was requested based on the read register size settings coupled with your register spacing that was illegal, and you were seeing illegal data address, not value. "Contiguous batches only" will never request a register you haven't configured it to get data from, where otherwise it may request holding registers 0-150 (depending on your read settings) just to read 0 and 150. Let's say 75 is configured to be a private register, this would cause what you're seeing.
            • N Offline
              Nikospps
              Hello everyone!
              I also created a post about this, but i will make my request available (also) here.
              I try to connect to an (external) modbus device, but after my system scanned it in my local networks, doesn't allow me to verify "next step" button and establish the connection.
              Any idea?
              Thank you!
                phildunlap
                Hi Nikospps,
                I responded in your thread, but I'm not sure I understand what you mean "verify next step button." Can you post a screenshot?
                Hello! It looks like you're interested in this conversation, but you don't have an account yet.
                Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.