    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    Program devices via ControlCore using Mango as a Modbus Gateway

    User help
    2
    8
    2.2k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • M
      mihairosu
      last edited by

      I am trying to use ControlCore to program devices. See my settings:

      0_1469118372830_cc settings.png

      However, I get this error:

      0_1469118412238_cc error.png

      Control Core is v4.09. The module says it only supports Control Core v 2.7

      0_1469118473921_cc module.png

      I assume the module starts up with mango, so there is no need to manually start it. Any suggestions?

      Also there are no firewall issues as it's within the same subnet.

      1 Reply Last reply Reply Quote 0
      • JoelHaggarJ
        JoelHaggar
        last edited by

        It will show up in the Data Source drop down list. You need to add it as a data source and configure the port and serial port. Then you have to disable what ever data source is using the serial port before you enable it. Once you do all that it should work fine. We use it with the latest version of Control Core.

        1 Reply Last reply Reply Quote 0
        • M
          mihairosu
          last edited by

          Ah, that's unfortunate, as I cannot disable the modbus data source. It's pulling data from other devices regularly. In that case I will have to manually update the device locally, while it's disconnected from the network.

          Thanks Joel.

          1 Reply Last reply Reply Quote 0
          • JoelHaggarJ
            JoelHaggar
            last edited by

            Only one Data Source can talk on a serial port at a time and you can't mix different protocols on the same RS-485 network at the same time so there isn't really any way to make that work. In most cases you only have to turn off the device polling for a minute or less while you update the program. Your best option might be to run a separate RS-485 network and plug in a USB to RS-485 to your MangoES.

            1 Reply Last reply Reply Quote 0
            • M
              mihairosu
              last edited by

              That's not a bad idea. If I ever get a bunch more of these devices, that might be a route worth taking.

              1 Reply Last reply Reply Quote 0
              • M
                mihairosu
                last edited by

                Hey Joel,

                My first attempt has been to use the same serial network, and turning off the device polling, but no luck:

                Control Core Settings:

                0_1477664091150_CC settings.png

                Mango Settings:

                0_1477664100384_CC mango settings.png

                Mango Errors:

                0_1477664112289_CC error on mango.png

                CC Error:

                0_1477664132097_CC error.png

                Any thoughts?

                1 Reply Last reply Reply Quote 0
                • JoelHaggarJ
                  JoelHaggar
                  last edited by

                  I have a few things. On the Control Core Data Source it should be 19,200 baud. I would set the Receiving port to 8502.

                  In Control Core use the TCP/IP Server Gateway rather than the Modbus Gateway. Leave the username and password blank. Make sure no other data sources are enabled using the same serial port and it should work.

                  0_1477670773144_upload-9137370a-832c-4f90-b990-4033627e7b01

                  0_1477670844461_upload-485555bf-7c3a-4872-87c7-f46790eb00a2

                  1 Reply Last reply Reply Quote 0
                  • M
                    mihairosu
                    last edited by

                    Thank you Joel I got it to work.

                    The only thing I had to change was the Bit rate back to 9600, which is what our modbus network runs at.

                    1 Reply Last reply Reply Quote 0