    28 Posts 3 Posters 35.2k Views 3 Watching
      Hi Dave,
      This is done through a meta point.
      Something like....
      var changeThreshhold = 5 //5 units per minute, let's say
      var data = p.past(MINUTE, 5)
      if( data.count == 0 ) {
        //Handle no data in period condition, raise event?
        return true;
      } else if ( data.count == 1 ) {
        //Handle only one piece of data in our range by getting another value
        var lv = p.lastValue(1);
        if ( lv == null ) //Only one data point, no cause for alarm. We may not need to check this
           return false
        return changeThreshhold > ( data.lastValue - lv.value )/((data.lastTime - lv.time)/60000);
      } else {
        return changeThreshhold > ( data.lastValue - data.firstValue )/((data.lastTime - data.firstTime)/60000);
      Then having a state detector on the meta point checking for a "true" state. This isn't its own detector because the shrewd observer may see data sets where this logic is deeply flawed (specifically, data that isn't monotonic). For situations where your data varies in both directions, you may be more interested in changing the logic to sum the differences as you iterate the list, and alarm if you cross the threshhold, more like....
      var data = p.pointValuesSince(new Date().getTime() - 5*60*1000) //Five minutes in milliseconds
         return false
      var sum = 0;
      var changeThreshhold = 5; //so, this would mean that if any point in the period it is more than
      for( var k = 0; k < data.length-1; k+=1 ) {
        sum += (data[k+1].value - data[k].value);
        if( sum < changeThreshhold || sum > changeThreshhold )
          return true;
      return false;
      So, what it means to have changed over time can be funky depending on your data set. That second version should be equivalent to seeing if any values in a range are outside the acceptable rate of change... like,
         return false
      var firstValue = data[0];
        if( firstValue.value - data[k].value > changeThreshhold || firstValue.value - data[k].value < changeThreshhold )
          return true;
      return false;
      But this could still be flawed. If data[0].value == 0, data[1].value == -3, and data[2].value == 3, then none of these detectors would alarm, even though we experienced a change of 6 at one point. One would expect the next run of the point will have data[0] == -3, but having uniform data in time is an assumption we shouldn't rest our logic on!
      • V Offline
        v8dave
        Thanks Phil, once I figure out where the meta script is input I'll give this a go. I have the module loaded but can't see where to input this script. :)
        • V Offline
          v8dave
          OK. I found how to create a meta script. It's actually a data source. I'll give your code a try out. Thanks again.
            Data will be coming from it, won't it? :D
            A solution some people use for noisy data, to avoid what I was talking about, is to just use averages from time periods to compare instead of raw data, so,
            var period = 300000 //5*60*1000 Five minutes
            var now = new Date();
            var start = now.getTime() - period;
            var middle = now.getTime() - period/2;
            if( Math.abs( p.getStats(middle, now).average - p.getStats(start, middle).average ) > 5 ) //Threshhold
              return true;
            return false;
            Depending on your needs or thoughts on your data.
            • V Offline
              v8dave
              Just trying this now and when I input the script and then click save, I get this error at the bottom.
              invalid return
              at line -1
              I've selected a suitable data point and set its name to p for this test.
                Are you using the scripts as posted or as they arrived in an email notification?
                I am able to run all of these with a numeric point for p. That looks like a syntax error, which I think I would get regardless of the code path.
                • V Offline
                  v8dave
                  Hi Phil, I am using a numerical data point. Here is the screen capture. I modified the script as I only need to detect a falling trend.!!
                    it looks like you are using the scripting data source, instead of a meta data source and putting these scripting in a meta data point.
                    Scripts are intended for a multiple-output control loop. Scripting data source scripts don't contain return statements, they set a point's value with p.set(value, time) or just p.set(value) for the current time.
                    This kind of thing, where we're producing a single answer from perhaps multiple inputs, should be a meta point.
                    • V Offline
                      v8dave
                      Ah yes, so I was. Just trying it now but there is an error about a null value on line 4 which seems strange because it would not get to this line unless there was data.
                         return false;
                          return true;
                      return false;
                        That is odd....
                        I would put print(data) at line 2 to investigate.
                        • V Offline
                          v8dave
                          I've added that but where do I see the output from this?
                            It would be below the script window, if it ran, where you saw the error. If it didn't, I wonder if you have a global script declared? The global scripts page is this icon: 0_1469746987325_script-globe.png
                            • V Offline
                              v8dave
                              I don't have that icon. Is this a module I need to install or a setting somewhere?
                              • V Offline
                                v8dave
                                I found the module and installed it and the icon is now present. My scripts still don't seem the be running as there is no output from the print(data) statement.
                                  No, I was curious if that's where the error was occurring, not telling you that you needed to install it.
                                  Do you get the same error from a very simple script, perhaps just...
                                  return false;
                                  Are you sure your point is in the context as bbl1 (b - b - lower case L - numeral 1)?
                                  • V Offline
                                    v8dave
                                      print("bbl1:");
                                      print(bbl1);
                                      print("data:");
                                      print(data);
                                         return false;
                                          return true;
                                      return false;
                                      • V Offline
                                        v8dave
                                          return false;
                                          • V Offline
                                            v8dave
                                            Looking at the log file, it is still failing at this line.
                                            ERROR 2016-07-29 07:39:00,004 (com.serotonin.m2m2.meta.JavaScriptPointLocatorRT.executeImpl:54) - sun.org.mozilla.javascript.EvaluatorException: Java class "java.util.ArrayList" has no public instance field or method named "0". (<Unknown Source>#9) in <Unknown Source> at line number 9 in <Unknown Source> at line number 9
                                            I export and send you the file.