    Problems Creating Datasource Modbus RTU
    6 Posts 2 Posters 4.5k Views 1 Watching
      mtapia_vmt
      Hi, This is my problem, Modbus nodo scan is "ok", more, Modbus read Data "No response from slave 1". need help please, thank you very much
        There could be many different causes of this issue including bad wiring, baud rate, etc.
        Note that the Modbus Node Scan only works with certain devices. Did the scan find any slaves on the network. Maybe send a screenshot of your configuration.
          mtapia_vmt
          ![upload-a66a6138-6609-4eaf-9b90-1d4744bcf360](uploading 100%)
          thank you very much Joel:
          Attached image, I also confirm that communication is correct
          Thanks for your answer.
            mtapia_vmt
              You are testing reading 100 registers starting at 0. Try reading 1 or 10 and make sure you are using a register you know has a value in it. Every Modbus device is different so you need to look at the documentation on the device.
                mtapia_vmt
                I tried to create a connection in scadaBR and works perfect, attached image.