Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
Modbus RTU
-
Hi,
Have MangoES supported Modbus RTU ?
If this, how can I enable it. -
- Make a Modbus serial data source
- select Modbus RTU in the dropdown
- use the device '/dev/ttyUSB0' as the port and
- connect your Modbus RTU device to the RS-485 port on the MangoES.
-
Jeremyh,
Thank you for kindly reply.
And my device is Modbus RTU over TCP/IP.Any suggestion?
-
Mango has two modbus data sources. Modbus RTU and Modbus IP. Just use the one that is appropriate for your connection type. RTU is for serial ports and IP is for Ethernet based devices.
-
What is your device?
"Modbus TCP" and "Modbus RTU over TCP" are actually two different things.