Actually I just realised that I assumed you were using BACnet4J with MangoM2M. If you are just using the BACnet4J stack then my answer will be of no help to you.
Posts made by SteveV
-
RE: How to get the objects in the remote device?
-
RE: How to get the objects in the remote device?
After you click on Whois, you get a list of remote devices. Next to each device there is a small triangle - you can click on this to see the objects (you may have to wait a few minutes) then click on each object to add the point to the datasource.
-
RE: Editing graphical views from remote Web Browser
Just tested with Firefox remotely. works fine so it must be a IE problem. Sorry for the noise on the forum, hopefully this post helps someone.
-
Editing graphical views from remote Web Browser
I am working on a remote web browser, a web browser that is not running on the same PC as the Mango software.
When I add a point to a graphic view, I cannot edit the graphical renderer, I get an error of "unknown runtime error". However if I use a browser which is on the same PC as the Mango software I do not have this problem.
Any idea of what the problem could be. Actually I have to say I am using IE8, and Firefox on the PC where the MAngo Software is running so maybe it is an IE8 problem. I will run some tests and advise.
-
RE: Editing graphical views from remote Web Browser
I am working on a remote web browser, a web browser that is not running on the same PC as the Mango software.
When I add a point to a graphic view, I cannot edit the graphical renderer, I get an error of "unknown runtime error". However if I use a browser which is on the same PC as the Mango software I do not have this problem.
Any idea of what the problem could be. Actually I have to say I am using IE8, and Firefox on the PC where the MAngo Software is running so maybe it is an IE8 problem. I will run some tests and advise.
-
RE: BACnet Relinquish
Thank you Matthew.
I have spent some more time with the Mango M2M and I am VERY impressed, you have doe a great job.
I have some further suggestions with regard to "Relinquish" and BACnet priority setting in general.
- Write Priority, can Mango have 2 levels of priority, user selectable but say: Events to be written at priority 10. So if Mango is writing a point due to a scheduled time the priority is 10.
When the user writes a value to a point say from a graphic view or a watchlist, the point is written at priority 8.
This means that an operator can permanently override a scheduled event if desired.
-
This brings up the second point which is what priority to relinquish to. I think Mango should always relinguish the point at the same priority as it was set so if the point is written at priority 8 then it should be priority 8 that is relinquished. I expect you already had this in mind.
-
Would it be possible to add something to the graphical renderers that made it obvious that a point was at the overwritten priority, in my example if the point was at priority 8 could a hand symbol pop up to signify the point is no longer automatically controlled?
-
When a BACnet point is logged is a change in priority logged as well?
-
BACnet Relinquish
Hi,
I'm very new to the Mango M2M. I'm very impressed with what is available, and I wna tto send out a big thank you to those that have made it possible :D.
My question is about Reqlinquish. Is it possible to relinquish the priority of BACnet points from Mango.
For example if I have an AO point which is connected to a heating valve I want to be able to override the valve say to 100% from Mango and when I have finished Relinquish it back to automatic control.
In my system the BACnet priority for automatic control is 12, while the BACnet priority for override is 8.
Regards
Steve
-
RE: BACnet Relinquish
Hi,
I'm very new to the Mango M2M. I'm very impressed with what is available, and I wna tto send out a big thank you to those that have made it possible :D.
My question is about Reqlinquish. Is it possible to relinquish the priority of BACnet points from Mango.
For example if I have an AO point which is connected to a heating valve I want to be able to override the valve say to 100% from Mango and when I have finished Relinquish it back to automatic control.
In my system the BACnet priority for automatic control is 12, while the BACnet priority for override is 8.
Regards
Steve