Hi,
I would like to see support for modbus rtu over tcp/ip. I dont know how common it is to use this type of modbus. There is a nice 4-port converter from moxa that i use quite often and its name is "NPort 5430".
/Tomas
Support for modbus rtu over tcp/ip
Hi,
I would like to see support for modbus rtu over tcp/ip. I dont know how common it is to use this type of modbus. There is a nice 4-port converter from moxa that i use quite often and its name is "NPort 5430".
/Tomas
Hello Tomas,
Mango already supports Modbus RTU over TCP and UDP.
Aha, thats great. I must have missed that part =). I will take a look at it.
Thanks alot for the info.
/Tomas R
@mlohbihler said:
Hello Tomas,
Mango already supports Modbus RTU over TCP and UDP.
I try to configure a gen-set controller without success.
Testing with modpoll using "Encapsulated Modbus RTU over TCP" works fine, but i can't do it with Mango.
AFAIK, RTU over TCP uses a header different than Modbus/TCP. I need a new data source type? I try with Modbus IP without sucess.
Best regards,
David Parra
How do you configure Modbus RTU over tcp? I do not see a setting for it.
@jmalkoff said:
How do you configure Modbus RTU over tcp? I do not see a setting for it.
I found it, you have to create datasource Modbus IP and check Encapsulate field. It works fine.