      My mango ES is stuck in a reboot cycle. It get stuck at 88% and then reboots. I get this error over and over. This happened yesterday and after about 10 restarts it sorted itself out. today the error has returned.
      ERROR 2018-04-26T15:26:46,239 (com.serotonin.m2m2.meta.JavaScriptPointLocatorRT.executeImpl:88) - Rim WTW Battery - Volts : ReferenceError: "raw" is not defined in at line number 7 in at line number 7
      javax.script.ScriptException: ReferenceError: "raw" is not defined in at line number 7 in at line number 7
      at com.serotonin.m2m2.rt.script.ScriptExecutor.prettyScriptMessage(ScriptExecutor.java:181) ~[mango-3.3.4.jar:?]
      at com.serotonin.m2m2.rt.script.CompiledScriptExecutor.execute(CompiledScriptExecutor.java:92) ~[mango-3.3.4.jar:?]
      at com.serotonin.m2m2.meta.JavaScriptPointLocatorRT.executeImpl(JavaScriptPointLocatorRT.java:84) [meta-ds-3.3.2.jar:?]
      at com.serotonin.m2m2.meta.MetaPointLocatorRT.execute(MetaPointLocatorRT.java:310) [meta-ds-3.3.2.jar:?]
      at com.serotonin.m2m2.meta.MetaPointLocatorRT.contextPointUpdated(MetaPointLocatorRT.java:181) [meta-ds-3.3.2.jar:?]
      at com.serotonin.m2m2.meta.MetaPointLocatorRT.contextPointUpdated(MetaPointLocatorRT.java:166) [meta-ds-3.3.2.jar:?]
      at com.serotonin.m2m2.meta.MetaPointListener.pointUpdated(MetaPointListener.java:53) [meta-ds-3.3.2.jar:?]
      at com.serotonin.m2m2.rt.dataImage.DataPointRT$EventNotifyWorkItem.execute(DataPointRT.java:731) [mango-3.3.4.jar:?]
      at com.serotonin.m2m2.rt.maint.BackgroundProcessingImpl$RejectableWorkItemRunnable.run(BackgroundProcessingImpl.java:630) [mango-3.3.4.jar:?]
      at com.serotonin.timer.Task.runTask(Task.java:179) [mango-3.3.4.jar:?]
      at com.serotonin.timer.TaskWrapper.run(TaskWrapper.java:23) [mango-3.3.4.jar:?]
      at com.serotonin.timer.OrderedThreadPoolExecutor$OrderedTaskCollection.run(OrderedThreadPoolExecutor.java:317) [mango-3.3.4.jar:?]
      at java.util.concurrent.ThreadPoolExecutor.runWorker(ThreadPoolExecutor.java:1142) [?:1.8.0_131]
      at java.util.concurrent.ThreadPoolExecutor$Worker.run(ThreadPoolExecutor.java:617) [?:1.8.0_131]
      at java.lang.Thread.run(Thread.java:748) [?:1.8.0_131]
      WARN 2018-04-26T15:26:47,013 (org.springframework.web.servlet.handler.SimpleUrlHandlerMapping.registerHandlers:114) - Neither 'urlMap' nor 'mappings' set on SimpleUrlHandlerMapping
      • CraigWeb
        Mango ES is running 3.3.4
        i managed to disable the meta data source then rebooted the server.
        Still getting stuck on 88% and then rebooting.
        • phildunlap
          phildunlap last edited by
          Hi CraigWeb,
          Taking it's time at 88% sounds like you probably have swagger.enabled=true in your env.properties. The error you have shared doesn't seem like it caused anything. Are there other messages of interest in there? I would start looking at things like dmesg or /var/log/ files to resolve why it is rebooting. Unless you have configured Mango to reboot the system, Mango does not reboot the system. Can you check that your power supply is adequate (from the MangoES FAQ: you can use any power supply that is 12-24 VDC with a minimum of 20 watts (12vdc @ 2 amps or 24vdc @ 1 amp minimum)) and not at fault?
          • CraigWeb
            I will have a look at the power supply and let you know. It was running off a UPS for the last day. So there have been power issues.
            thank you
            These are the 2 errors that show when it hangs:
            WARN 2018-04-26T18:15:29,501 (org.springframework.web.servlet.handler.SimpleUrlHandlerMapping.registerHandlers:114) - Neither 'urlMap' nor 'mappings' set on SimpleUrlHandlerMapping
            ERROR 2018-04-26T18:15:37,698 (com.infiniteautomation.nosql.MangoNoSqlBatchWriteBehindManager$StatusProvider.scheduleTimeout:738) - 1 BWB Task Failures, first is: Task Queue Full
            • CraigWeb
              Everything seems to be back to normal. Looks like when the UPS got its mains supply back. it sorted the problem out. Thank you it was very helpful to know that mango cant restart the unit.
              • phildunlap
                phildunlap last edited by phildunlap
                Certainly! Thanks for sharing the resolution. I always feel like I'm on a ledge when I tell people it's the other equipment or the wire. Nice to know when I'm [probably] right and wrong!
                Doesn't restart the unit* you mean. You can certainly have a process event handler reboot the system, if you've given the user that launches Mango sufficient privileges to do so.
                • CraigWeb
                  Started getting this problem again. Replaced the power supply and it booted right up.