Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
More than one BACnet data source
-
Hi,
I'm trying to create more than one BACnet data source. When I try it I get the following error:
'CDI2-Test': Initialization error: Address already in use
Is this by design or am I doing something wrong?
Thanks in advance,
JoseP.S. The idea behind more than one BACnet point it to group them for easiest management. In this way I will group each data source and its points like in the building is a correspondent given zone or area. In total there are about 1500 points.
-
Hi jmatos,
Are your multiple BACnet data sources using the same local device (they should be, I suspect you made a local device for each?)? Local devices can be configured on the System Settings page.
-
It's also possible that you have another tool open on the computer, already bound the port that the local device is trying to bind to (0xBAC0, 47808). In which case none of your data sources on that local device would be working.
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.