    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    SMA Cluster Controller

    Hardware
    2
    5
    3.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • D
      Dominic.Irl
      last edited by

      I am trying to communicate via the SMA cluster controller to additional inverters in the network.

      I can communicate with the cluster controller directly no problem.
      My issue is with ascertaining the unit ID's of the other inverters. I am unsure if this a Mango query or a query for SMA.
      I have strangely enough found one of the inverters @ slave ID 255. I thought the range was 0-240!!

      Are there any trick to polling the slaves to find them?

      Any insight into this would be greatly appreciated.

      Thanks in advance

      1 Reply Last reply Reply Quote 0
      • jeremyhJ
        jeremyh
        last edited by

        @Dominic.Irl said:

        My issue is with ascertaining the unit ID's of the other inverters. I am unsure if this a Mango query or a query for SMA.

        Hello,

        This is a SMA query, but I will save you some time.

        The basic steps are that you must go into the Cluster Controller > 'Update and Save' page > Modbus > 'Save automatically generated plant configuration'. This will download a XML file which you can open in a text editor and set the modbus address of each inverter. Then upload it via the 'Update user-defined plant configuration (*.xml)' button.

        You can find all this information in the SMA Cluster Controller user manual, but it is quite poorly explained. It took me a little while to work out too.

        Cheers
        Jeremy

        1 Reply Last reply Reply Quote 0
        • D
          Dominic.Irl
          last edited by

          Hi Jeremy,

          You are a star!!
          You are right, it is poorly explained in the SMA manual - regardless you saved the day!

          Thanks,

          D

          1 Reply Last reply Reply Quote 0
          • jeremyhJ
            jeremyh
            last edited by

            No problem, thanks for following up. Glad you had a win.