Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
Exception from modbus master: No error in nativeavailable
-
This alarm message came out from a modbus serial data source, what's the meaning of this alarm message?
Today the data source can't work any more. A new alarm message came out.
'COM8': com.serotonin.modbus4j.exception.ModbusTransportException: com.serotonin.messaging.TimeoutException: request=com.serotonin.modbus4j.serial.rtu.RtuMessageRequest@f64ef8
Not any manual change on the data source before the alarm came out.
-
Looks to me like the request timed out. The slave didn't respond within your time out setting. If you get this a lot you may want to try increasing your time out setting.
Joel.
-
An unexpected failure leads to that sensors connecting to COM8 can't be reached.
Turning off power and turn on then, those sensors can be reached again.
thanks Joel.