    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    BACNet MSTP communicate with FieldServer problem

    User help
    2
    8
    3.1k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • R
      ray
      last edited by

      I am testing out the Mango BACNet (v. 2.1.0) MSTP running against FieldServer. I got an error message when I tried to discover device objects. Please see the error message in the attachment. For BACNet IP, I can easily communicate with the FieldServer without any problem. The FieldServer works as a Modbus RTU to BACnet MSTP gateway. I can collect data by CAS BACNet Explorer through BACNet MSTP protocol.

      Attachment: download link

      1 Reply Last reply Reply Quote 0
      • terrypackerT
        terrypacker
        last edited by

        Ray,

        Can you post an excerpt from your log file around that time? That will help us in identifying where the problem is.

        1 Reply Last reply Reply Quote 0
        • R
          ray
          last edited by

          I got anther error message when I try to get the object list. Please check the attachment. Thanks !

          Attachment: download link

          1 Reply Last reply Reply Quote 0
          • terrypackerT
            terrypacker
            last edited by

            Ray,

            I'm not very familiar with BacNet but from what you've posted it appears that the module is expecting the Link service station value to be an octet string of the form:

            x.x.x.x:yyyy where the :yyyy part is optional.

            My guess is that this code is specific for the BACnet I/P system and is somehow getting confused when you are sending in the 3 or in the first case nothing at all. I found the section of code that is failing and changed it to work with MSTP addresses.

            The changes will be included in the next release of the module (2.1.3). What version of Mango are you using? I may be able to compile the changes into a module that would be compatible with your core.

            Thanks for letting us know about this,
            Terry

            1 Reply Last reply Reply Quote 0
            • R
              ray
              last edited by

              I tested on Mango 2.4.0. I ran the same test with DGBox BACNet MSTP has no problem at all.

              1 Reply Last reply Reply Quote 0
              • terrypackerT
                terrypacker
                last edited by

                Ray,

                This bug fix will be included in the 2.5.0 release.

                1 Reply Last reply Reply Quote 0
                • R
                  ray
                  last edited by

                  Thanks !

                  1 Reply Last reply Reply Quote 0