Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
Who know how can connect rs232 or rs485 device ?
- 
 Now want to use mango received the data . Devicehave connect the computer via rs232(serial). what protocol and data source will be choosen? 
- 
 What protocol is the device you want to connect to? If you know that then you know what Protocol to use in Mango. There is also a general serial data source that you can use regex to parse values out of the serial stream. See the end of this thread to download the latest module. http://forum.infiniteautomation.com/forum/posts/list/15/1813.page 
- 
 I find the EQUIPMENT use RS232 communication and the TCPIP .SO what protocol will be choose for receiving data ? 
- 
 You need to find out what protocol your device uses. RS232 or TCPIP are not protocols they are only methods of communication. You need to find documentation on your equipment that will tell you what protocol or language they speak. 
- 
 yes. 
 The equipment can output:-ASCII comma separated data with RS232, RS422 or RS485 levels. SDI-12 format data. Modbus ASCII or RTU data with RS232 or RS485 levels. But now the equipment directly the computer via serial port(rs232). what should I do ? whether use modbus serial is supported? if it not support it whether I must use modbus tcp/ip? Configuring equipment for MODBUS 
 equipment Supported Modbus Specification
 MODBUS RTU or ASCII.
 Baud Rate 9600 or 19200 Baud.
 COMMS RS232 point to point only, RS485 2 wire networkable.
 Modbus Parameters ASCII or RTU.
 Parameter Modbus ASCII Modbus RTU
 Character ASCII 0 to 9 and A to F (Hex) Binary 0 to 255
 Error Check Longitudinal Redundancy Check (LRC) Cyclic Redundancy Check (CRC)
 Frame Start Character ':' (3A Hex) 3.5 Characters Silence
 Frame End Characters CR/LF (0D/0A Hex) 3.5 Characters Silence
 Gaps in Message 1 Second 1.5 Times Character Length
 Start Bit 1 1
 Data Bits 7 8
 Parity Even/Odd None Even/Odd None
 Stop Bits 1 2 1 2
 Requires:-
 with version 2346-4.00 firmware and onwards.
 version 2.02-02 and onwards.
 Connect equipment to a PC COM port (default communication is RS232).
 Open Software.
 Click on Connect and Read to reach the Editing Pages as shown below.
 Configuration
 Click on the MODBUS Page
 Mode: Choose between RTU and ASCII, in this case RTU.
 Address: Choose a MetPak Address number to be between 1 to 247.
 Data Bits: Choose 7 for Modbus ASCII and 8 for Modbus RTU.
 Stop Bits: Choose 1 for Even/Odd Parity or 2 for No Parity (None).
 Parity: Choose Even/Odd or None.
 Termination Char ASCII code: Choose between 0-255.
 Inter Char Timeout (ms): Choose between 500ms to 10000ms.
 Operation
 Select the COMMS Page
 Protocol: Select MODBUS
 Interface: Default is RS232. Select RS232 or RS4852W. RS232 will only
 allow a single point to point non multi drop network connection. RS485 2 wire will
 allow networking with up to 32 connected devices.
 Baud Rate: Default is 19200. Select required Baud rate (9600 or 19200
 supported).
 Node ID: Default is Q. Not used for MODBUS.
 Output Rate: Default is 1Hz. Set update rate for Data (0.25Hz
 to 1Hz).
 Message Mode: Default is CONT. Select POLL mode and equipment will
 only make and output a measurement (set by the output rate) on demand from the
 Modbus Master. In CONTinuous mode the MetPak continuously makes
 measurements set by output rate (0.25Hz to 1Hz) and only outputs a result when
 demanded from the Modbus Master.
 When required settings have been selected click on Save Settings to Device
 Click on Yes and OK.
 Power down the and apply power back to the MetPak to complete setting
 changes.
 Note: now that the unit is in MODBUS mode if any further changes need to be
 made use the SAFE MODE connection and method to re-establish communication
 with equipment
 METPAK MODBUS NOTES- All registers are 16bit.
- The first byte is high order and the second is low.
- Each measurement is comprised of two 16bit registers.
- The registers are arranged High Word/ Low Word.
- Registers start at address 40001.
- Holding registers available in the order of the MetPak data string (which can be
 established by the REPORT command in non-Modbus ASCII Mode).
 MetPak Pro MODBUS Default Data String Field Encoding:
 Node 4-byte character string Registers 40001-2.
 Direction: 32 Bit Floating point value Registers 40003-4.
 Speed: 32 Bit Floating point value Registers 40005-6.
 Pressure: 32 Bit Floating point value Registers 40007-8.
 Temperature: 32 Bit Floating point value Registers 40009-10.
 Relative Humidity: 32 Bit Floating point value Registers 400011-12.
 Dewpoint: 32 Bit Floating point value Registers 400013-14.
 PRT: 32 Bit Floating point value Registers 400015-16.
 AN1: 32 Bit Floating point value Registers 400017-18.
 AN2: 32 Bit Floating point value Registers 400019-20.
 DIG1: 32 Bit Floating point value Registers 400021-22.
 Supply Voltage: 32 Bit Floating point value Registers 400023-24.
 Status: 32 bit Unsigned Integer (UINT) Registers 400025-26.
 See Simply Modbus program reading example MODBUS Data as
 follows:- please refer the attachment.
 Attachment: download link 
- 
 HI, 
 I try to connect use modbus serial .but I setting COM1 (it is really COM1 port) and scan modbus node and it is not sucessful.in data point display " Point value may not be reliable ".
 I donot know how to setting make modbus serial can connect mango system. but I use hyperterminal it is very easy to connect COM1 port as show attahment.any idea? BR Attachment: download link 
- 
 yes. 
 The equipment can output:-ASCII comma separated data with RS232, RS422 or RS485 levels. SDI-12 format data. Modbus ASCII or RTU data with RS232 or RS485 levels. But now the equipment directly the computer via serial port(rs232). what should I do ? whether use modbus serial is supported? if it not support it whether I must use modbus tcp/ip? Configuring equipment for MODBUS 
 equipment Supported Modbus Specification
 MODBUS RTU or ASCII.
 Baud Rate 9600 or 19200 Baud.
 COMMS RS232 point to point only, RS485 2 wire networkable.
 Modbus Parameters ASCII or RTU.
 Parameter Modbus ASCII Modbus RTU
 Character ASCII 0 to 9 and A to F (Hex) Binary 0 to 255
 Error Check Longitudinal Redundancy Check (LRC) Cyclic Redundancy Check (CRC)
 Frame Start Character ':' (3A Hex) 3.5 Characters Silence
 Frame End Characters CR/LF (0D/0A Hex) 3.5 Characters Silence
 Gaps in Message 1 Second 1.5 Times Character Length
 Start Bit 1 1
 Data Bits 7 8
 Parity Even/Odd None Even/Odd None
 Stop Bits 1 2 1 2
 Requires:-
 with version 2346-4.00 firmware and onwards.
 version 2.02-02 and onwards.
 Connect equipment to a PC COM port (default communication is RS232).
 Open Software.
 Click on Connect and Read to reach the Editing Pages as shown below.
 Configuration
 Click on the MODBUS Page
 Mode: Choose between RTU and ASCII, in this case RTU.
 Address: Choose a MetPak Address number to be between 1 to 247.
 Data Bits: Choose 7 for Modbus ASCII and 8 for Modbus RTU.
 Stop Bits: Choose 1 for Even/Odd Parity or 2 for No Parity (None).
 Parity: Choose Even/Odd or None.
 Termination Char ASCII code: Choose between 0-255.
 Inter Char Timeout (ms): Choose between 500ms to 10000ms.
 Operation
 Select the COMMS Page
 Protocol: Select MODBUS
 Interface: Default is RS232. Select RS232 or RS4852W. RS232 will only
 allow a single point to point non multi drop network connection. RS485 2 wire will
 allow networking with up to 32 connected devices.
 Baud Rate: Default is 19200. Select required Baud rate (9600 or 19200
 supported).
 Node ID: Default is Q. Not used for MODBUS.
 Output Rate: Default is 1Hz. Set update rate for Data (0.25Hz
 to 1Hz).
 Message Mode: Default is CONT. Select POLL mode and equipment will
 only make and output a measurement (set by the output rate) on demand from the
 Modbus Master. In CONTinuous mode the MetPak continuously makes
 measurements set by output rate (0.25Hz to 1Hz) and only outputs a result when
 demanded from the Modbus Master.
 When required settings have been selected click on Save Settings to Device
 Click on Yes and OK.
 Power down the and apply power back to the MetPak to complete setting
 changes.
 Note: now that the unit is in MODBUS mode if any further changes need to be
 made use the SAFE MODE connection and method to re-establish communication
 with equipment
 METPAK MODBUS NOTES- All registers are 16bit.
- The first byte is high order and the second is low.
- Each measurement is comprised of two 16bit registers.
- The registers are arranged High Word/ Low Word.
- Registers start at address 40001.
- Holding registers available in the order of the MetPak data string (which can be
 established by the REPORT command in non-Modbus ASCII Mode).
 MetPak Pro MODBUS Default Data String Field Encoding:
 Node 4-byte character string Registers 40001-2.
 Direction: 32 Bit Floating point value Registers 40003-4.
 Speed: 32 Bit Floating point value Registers 40005-6.
 Pressure: 32 Bit Floating point value Registers 40007-8.
 Temperature: 32 Bit Floating point value Registers 40009-10.
 Relative Humidity: 32 Bit Floating point value Registers 400011-12.
 Dewpoint: 32 Bit Floating point value Registers 400013-14.
 PRT: 32 Bit Floating point value Registers 400015-16.
 AN1: 32 Bit Floating point value Registers 400017-18.
 AN2: 32 Bit Floating point value Registers 400019-20.
 DIG1: 32 Bit Floating point value Registers 400021-22.
 Supply Voltage: 32 Bit Floating point value Registers 400023-24.
 Status: 32 bit Unsigned Integer (UINT) Registers 400025-26.
 See Simply Modbus program reading example MODBUS Data as
 follows:
 
- 
 Have not answer? 
- 
 When I in Port find "dev/ttys0" and "dev/ttys1", When I choose "/dev/ttyS0", In "point locator test" test and display "There was a problem testing the locator. (com.serotonin.io.serial.SerialPortException: Port In Use: /dev/ttyS0)" ,when I choose "/dev/ttyS1", In "point locator test" test and display “Main equipment malfunction:1”, Any suggestion? BR 