    Little endian
    11 Posts 2 Posters 4.1k Views 1 Watching
      alberto
      Hi All,
      how to set the data format "little endian" in mango?
      I must put the variable in a meta data source?
      If yes, what script should I enter?
      thanks
        What do you want to have be LE? Data storage, transmission, a particular comm protocol? And why?
          alberto
          the registers are transmitted as words of 16 bits, LSByte first, followed by MSByte.
          How to do the reverse in mango?
          thank you
            To be clear, i assume you are talking about Modbus. The implementation currently does not have an endian flag.
              alberto
              Yes,
              the protocol is Modbus.
              So there is no chance?
              I use the latest version of m2m mango.
              If not, think that in future there will be?
              thanks
                Seems unlikely at the moment. The Modbus spec - such as it is - is clear on byte ordering as i recall, and honestly, you're the first to ask for little endian. Why do you need it?
                  alberto
                  I use that because the slave provides the data in this format.
                  The specifications of the device indicate that the protocol is Modbus RTU.
                  Very strange.
                  thanks
                    Yes, strange. Is this a relatively new model? I wonder if they're also swapping things like the CRC.
                      alberto
                      I really need to reverse the byte order of a variable.
                      I can do meta data source with a command like the following?
                      unsigned short int Endian_Word_Conversion(unsigned short int word) {
                      return ((word>>8)&0x00FF) | ((word<<8)&0xFF00) ;
                      where 'word' is, for example, p241.value or p241.other
                      any ideas?
                      thanks
                        Sure, you can do something like that.
