    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    Modbus exception...

    User help
    2
    6
    3.1k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • P
      Phil
      last edited by

      Hi everybody, since a couple of day, I have the message below when I start MANGO application (after a cold start and manual MANGO starting) :
      <<com.serotonin.modbus4j.exception.ModbusInitException: com.serotonin.io.messaging.Send.TimeOutException>>
      I'm not sure for all the words, but seems to be the correct...
      Someone can help me ?

      Phil

      1 Reply Last reply Reply Quote 0
      • M
        mlohbihler
        last edited by

        The data source appears to be trying to send a message to the modbus equipment, and is not getting a response.

        Best regards,
        Matthew

        1 Reply Last reply Reply Quote 0
        • P
          Phil
          last edited by

          m@,

          Following the last message, now I've the message :
          com.serotonin.modbus4j.exception.ModbusTransportException: com.serotonin.io.messaging.SendTimeoutException

          I've check the slave, and with another application, it works...
          Any idea ?

          Phil

          1 Reply Last reply Reply Quote 0
          • P
            Phil
            last edited by

            m@,

            I've found why this error appears.
            In fact, it's due to a strange mapping of modbus registers.
            Now all is clear, I'll modify my data points in order to retreive values.
            You were right in your previous reply !!!

            Thanks again,

            Phil

            1 Reply Last reply Reply Quote 0
            • M
              mlohbihler
              last edited by

              Good to hear. Thanks for following up.

              Best regards,
              Matthew

              1 Reply Last reply Reply Quote 0