    ES version bacnet module 3.6.0 issue compare ver. 3.5.2
    33 Posts 5 Posters 51.5k Views 6 Watching
      You would have to use Mango 3.5.x to use a 3.5.x version of BACnet. Database downgrades aren't supported, so you'll either need to restore a database backup from 3.5 to 3.5, or you can export the JSON from the 3.6 instance and import it into 3.5 . But, you must already have 3.5 to have given me those captures, yes?
      As I told you earlier - we noticed some controller unable to discover on bacnet version 3.6.0
      Your capture doesn't indicate that using 3.6 is the cause from my understanding presented in the last post.
      • F Offline
        frankalton
        Hi Philips,
        The MANGO ES upgraded every time there is upgrade available , I didn't take action to backup any older version unless the ES has a auto backup "If yes - do tell me how to restore"
        The scan result on earlier post was performed on MANGO PC (free version) - that we have 3.5 and 3.6.
        Can you elaborate in details steps how shall we rescue MANGO ES now
        My main concern is MANGO ES.
        regards,
        Frank
          If you had it configured to make backups, you would perhaps still have a backup like core-database-H2-date.zip in the /opt/mango/backup directory. If you have one from before the upgrade (which is checked by default, but if you backup task doesn't backup the database that wouldn't happen), you could restore that into 3.5
          • T Offline
            techalton @phildunlap
            Dear Philips,
            Hi, I'm Eswaran, we now we are having two issues that we unable to solve
            • First issue we unable to scan some brand controller in BACnet version 3.6.0 on pc version (windows 7)
              • First attempt with BACnet version 3.6.0 on pc version (windows 7)
              • Second attempt with BACnet version 3.6.0 on pc version (windows 7)
              • Third attempt with BACnet version 3.6.0 on pc version (windows 7)
              • First attempt with BACnet version 3.5.2 on pc version (windows 7)
              • Second attempt with BACnet version 3.5.2 on pc version (windows 7)
              • Third attempt with BACnet version 3.5.2 on pc version (windows 7)
              As you can see ..... why Dev 1003 unable to scan in Bacnet version 3.6.0 (the latest version)
            The Second issue was we unable to scan the DDC properly BACnet IP on mango ES
            Pls refer to the link below for Wireshark file together with the mango host file :
            https://files.mycloud.com/home.php?brand=webfiles&seuuid=ec51add0c5fe1adc5cc3e5a6d5627780&name=Mango_forum_Post_230819
              Please email the wireshark logs to support@infiniteautomation.com
              • T Offline
                @phildunlap Please check your email. thank you
                • T Offline
                  techalton @techalton
                  @techalton said in ES version bacnet module 3.6.0 issue compare ver. 3.5.2:
                  Did u receive my email?
                    Yes, I did. They all show the same devices reporting IAms this time, but I do see that the 3.5 version is making solicitations in your captures for WhoIs specific device numbers, but there is no response in the captures where these devices are discovered so it's hard to say the significance of that. Perhaps different sets of points are enabled on the two Mango instances?
                    In all six submitted captures devices 10000, 1001, 1002, 1003 and 1004 responded to the initial discovery request and no other devices did.
                    And once again all the actual BACnet/IP protocol WhoIS discovery request bytes and the TCP/IP addressing is exactly the same in all six captures, leading once again to suggest it is not a Mango issue.
                      Also I notice we only see one bind address for any of these discoveries. While I wouldn't expect that to be the issue 1003 isn't in your images from 3.6 despite it being in the wireshark responding in exactly the same manner as it did in 3.5 . Can you confirm the local device configuration is the same in both versions? Can you try using a bind address of 0.0.0.0 ?
                      • T Offline
                        techalton
                        @phildunlap said in ES version BACnet module 3.6.0 issue compare ver. 3.5.2:
                        can we arrange a remote view session via Teamviewer to our pc...please let us know the time and date? when u are free. thank you
                          Were the wireshark captures provided from the same discovery attempts as the six images posted here?
                          Perhaps you can modify your Mango/classes/log4j2.xml file to log BACnet4J at trace level for the course of the test, and then send in the Mango/logs/ma.log file and wireshark from an attempted discovery in 3.6
                          Add near similar tags close to the bottom of log4j2.xml:
                          <AsyncLogger includeLocation="true" name="com.serotonin.bacnet4j" level="trace"/>
                          You can then either restart Mango or reload them on the /ui/administration/log4j-reset page, if the Log4J reset module is installed.
                          Until I have reason to suspect Mango as the cause of these discovery issues, we would assess an hourly support fee for any direct assistance.
                          T 2 Replies Last reply Reply Quote 0
                          • cwangvC Offline
                            cwangv
                            I am having similar issue running Bacnet Module 3.6.1. I can only discover some of the bacnet/ip devices, however other bacnet/ip devices can see Mango points (via bacnet/ip).
                            Other bacnet/ip devices on the network can see each other with no issues.
                            Using the legacy UI yields the same problem.
                            Let me know If I need to check anything to help out.
                            thanks.
                            • cwangvC Offline
                              cwangv
                              Hi, Guys
                              I figured it out the issue (at least for me).
                              It is to do with the broadcast address. For me, I needed to change it from 255.255.255.255 to 192.168.69.255 (which is my subnet host ip range).
                              after doing that, all is well.
                              @techalton - give it try.
                              thanks.
                                Thanks for sharing what you saw on your network cwangv!
                                I would encourage @techalton to try the bind address is 0.0.0.0 . From the wiresharks emailed in, I believe they're broadcasting on 255.255.255.255 already, but we can see in one screenshot the local device's bind address is the IPv4 address.
                                • cwangvC Offline
                                  cwangv
                                  Phil
                                  some bacnet/ip devices won't respond to broadcast of 255.255.255.255. They only respond to local subnet broadcast request. Hence the need to change the broadcast address to 192.168.69.255.
                                  I hope the above would help @techalton
                                  • T Offline
                                    @phildunlap said in ES version bacnet module 3.6.0 issue compare ver. 3.5.2:
                                    hello Phillip
                                    sorry for the late reply I have tried bind address 0.0.0.0 and still I'm unable to scan device 1003
                                    thanks.
                                    • T Offline
                                      hello Phillip
                                      On Wireshark and ma.log I'm able to see device 1003 but on the mango UI I'm unable to see the device.i have emailed the ma.log and Wireshark file to you
                                      thanks.
                                      • T Offline
                                        techalton @cwangv
                                        @cwangv said in ES version BACnet module 3.6.0 issue compare ver. 3.5.2:
                                        Phil
                                        some BACnet/IP devices won't respond to broadcast of 255.255.255.255. They only respond to local subnet broadcast requests. Hence the need to change the broadcast address to 192.168.69.255.
                                        Thanks for sharing @cwangv. when I change the broadcast address to 192.168.69.255.im unable to scan any device at all
                                        • cwangvC Offline
                                          cwangv @techalton
                                          @techalton
                                          You need to change the first three parts of the IP address to match you ip range.
                                          I am having different BACnetIP issue. In your case, most likely it is down to mango since only thing that has been changed is the mango version of software. Your field controllers would have still be the same.
                                          I have sent in my wireshark captures and am waiting for updates.
                                            Thanks for being persistent, techalton, we are examining the files and information you submitted.