    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    Rollup Value Calculations and No Values for 15m intervals

    User help
    3
    13
    1.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • cbyrneC
      cbyrne
      last edited by

      I've got a question in two parts. From looking at some delta data, there seems to be some discrepancy with rollups. This may be a misunderstanding on my part to how the deltas/rollups are calculated. I'm also getting no graph for 15m intervals.


      Part 1

      Sample data for a power usage accumulator:

      timestamp               value
      21/8/2019 05:30:00 	2724.95 kW·h
      21/8/2019 05:15:00 	2722.89 kW·h
      21/8/2019 05:00:00 	2720.82 kW·h
      21/8/2019 04:45:00 	2718.79 kW·h
      21/8/2019 04:30:00 	2717.55 kW·h
      21/8/2019 04:15:00 	2716.30 kW·h
      21/8/2019 04:00:00 	2715.06 kW·h
      21/8/2019 03:45:00 	2713.82 kW·h
      21/8/2019 03:30:00 	2712.57 kW·h
      21/8/2019 03:15:00 	2711.34 kW·h
      21/8/2019 03:00:00 	2710.09 kW·h
      21/8/2019 02:45:00 	2708.84 kW·h
      21/8/2019 02:30:00 	2707.59 kW·h
      21/8/2019 02:15:00 	2706.36 kW·h
      21/8/2019 02:00:00 	2704.24 kW·h
      21/8/2019 01:45:00 	2702.09 kW·h
      21/8/2019 01:30:00 	2699.94 kW·h
      

      If we set the rollup interval to 15m (or 900 seconds) and rollup type to delta, the graph on the data point details page goes blank:

      0_1566482536018_Screenshot_2019-08-22 Data point details - Mango v3.png

      Bug or expected behaviour?


      Part 2:

      For a 30 minute rollup and 60 minute rollup the graphs are as follows:
      1_1566482779667_Screenshot_2019-08-22 Data point details - Mango v3_60.png

      0_1566482779666_Screenshot_2019-08-22 Data point details - Mango v3_30.png

      and the transcribed values are:

      time 30 mins 60 mins
      02:00 2.12 4.6
      02:30 1.25
      03:00 1.24 3.73
      03:30 1.25
      04:00 1.24 3.73
      04:30 1.24

      I would have assumed that the 1 hour delta is the assume as the combined 30 minute deltas but it seems not to be the case.

      Software Developer for GLAS Energy Technology, Ireland

      cwangvC 1 Reply Last reply Reply Quote 0
      • phildunlapP
        phildunlap
        last edited by

        Hi cbyrne,

        I would expect most of this is being caused by the precision of everything occurring exactly on the milliseconds of the 15 minute intervals. Mango statistics are computed with an inclusive period start time, but an exclusive period end time. So, with the fifteen minute data, or really any of the rollups you are trying that are multiples of that, can have this behavior in the delta. As far as the statistics are concerned, the 15 minutes started with a real value, then no other values occurred in the next 15 minutes, so the delta is zero.

        In the 30 minute example, there are two values in the period, so the delta can be computed, but because the period ends exactly when the next value is recorded, the delta between those two values is not accounted for in either period's delta.

        Try offsetting your periods by a millisecond - except be aware that doing rollups via the datebar will automatically align the data period to fit an integer number of rollup periods inside the data period by expanding start and end times to period boundaries. With REST requests this can be controlled via setting the truncate parameter false.

        cbyrneC 1 Reply Last reply Reply Quote 0
        • cbyrneC
          cbyrne
          last edited by cbyrne

          Hi @phildunlap, thanks for the info, however I think this way of calculating deltas is flawed for anyone doing metered readings. These happen at regular intervals like above and currently the delta value for an hour does not show the user their usage for one hour and this is the critical issue.

          The way the delta is being calculated effectively drops one reading per rollup period and gives a misleading result. The normal approach for metered data at regular intervals is to only allow rollups that are a multiple of the reading interval and to calculate the delta based on the difference between the first reading of each rollup period i.e. for 15 minute readings, an hourly rollup would take the first reading of hour 2 and subtract the first reading of hour 1.

          Ofsetting by 1 ms does not cure the problem as it forces the last reading in the period into the next period so it still gets missed.

          One solution might be to add a "consumption" delta option to use this method? We're trying to push Mango to our customers right now for energy monitoring and this is the behaviour they need and expect. Similarly, would you consider adding a last_value-first value to the mango statistics object? Again, for energy monitoring, this delta is the key piece of information as it's their usage in the time period.

          Software Developer for GLAS Energy Technology, Ireland

          1 Reply Last reply Reply Quote 0
          • cwangvC
            cwangv @cbyrne
            last edited by

            @cbyrne
            I am just wondering what the polling intervals you have got for your points? I can imaging if the polling interval is the same as history interval, you may run
            into such issues.

            1 Reply Last reply Reply Quote 0
            • cbyrneC
              cbyrne
              last edited by

              @cwangv Yeah our polling interval is every 15 minutes.

              Software Developer for GLAS Energy Technology, Ireland

              cwangvC 1 Reply Last reply Reply Quote 0
              • cwangvC
                cwangv @cbyrne
                last edited by cwangv

                @cbyrne
                that may well be the cause of your issue. Due to polling delay, the data will not come in at exact 15 minutes intervals.
                you need to have shorter poll interval period (which is different to your history log interval), eg, 5 minutes, then over 15 minutes period you will have 3 samples in the poll, when history log kicks in, there will always be data there to collect even it is maybe from 5 minutes ago.
                Give it a try.

                cbyrneC 1 Reply Last reply Reply Quote 0
                • cbyrneC
                  cbyrne @cwangv
                  last edited by

                  @cwangv
                  We import our data from CSV files that are timestamp,value_1...value_n in fomat.
                  Maybe I'm misunderstanding but I don't see polling times affecting it.

                  Software Developer for GLAS Energy Technology, Ireland

                  cwangvC 1 Reply Last reply Reply Quote 0
                  • phildunlapP
                    phildunlap
                    last edited by phildunlap

                    cwangv

                    that may well be the cause of your issue. Due to polling delay, the data will not come in at exact 15 minutes intervals.

                    Not so! Mango is somewhat deceptive in terms or recorded timestamps in polls, which is why we discourage collecting highly time-precise data directly via Mango.

                    Mango will schedule a poll for a data source at a certain time, and all data will report that timestamp for the poll, even if the poll took quite some time to run. That's not true for every type of data source, since some transmit the timestamps with the data, but for protocols like BACnet and Modbus all points sampled in the poll will have the poll as the timestamp of the value.

                    The problem is somewhat more readily evident even with those sources now, since "Quantize" became an option on all data sources, which will align the period along the millisecond boundary of the polling period, so it is easy to collect data with these timestamps.

                    cbyrne

                    Hi @phildunlap, thanks for the info, however I think this way of calculating deltas is flawed for anyone doing metered readings. These happen at regular intervals like above and currently the delta value for an hour does not show the user their usage for one hour and this is the critical issue.

                    I can see your argument. I will raise it with others and see their perspective. The reason the ending timestamp is exclusive is that otherwise values on the period boundary could be counted twice in separate periods, causing the sum, average, and integral to have issues when comparing to the whole period. But, as you are noting, the delta has that behavior.

                    Ofsetting by 1 ms does not cure the problem as it forces the last reading in the period into the next period so it still gets missed.

                    Offsetting the values by 1 ms backward would solve the display issue of those rollups, I would expect. Or one could offset the period 1 ms forward if not using the datebar and truncate is false.

                    Similarly, would you consider adding a last_value-first value to the mango statistics object?

                    There already are the values Start, First, and Last in terms of values. They are formally defined here: https://help.infiniteautomation.com/mango-rollups-and-statistics

                    1 Reply Last reply Reply Quote 0
                    • cwangvC
                      cwangv @cbyrne
                      last edited by

                      @cbyrne
                      I didn't know that your data was imported. That all make sense now together with how Mango handles the data that falls on the boundary time.
                      This is definitely a scenario I need to watch out for.
                      thanks.

                      1 Reply Last reply Reply Quote 0
                      • cbyrneC
                        cbyrne @phildunlap
                        last edited by

                        @phildunlap Thanks Phil, much appreciated!

                        Similarly, would you consider adding a last_value-first value to the mango statistics object?

                        There already are the values Start, First, and Last in terms of values. They are formally defined here: https://help.infiniteautomation.com/mango-rollups-and-statistics

                        I should have been more specific on what I meant, I mean could the statistics object include a value which is equal to the last value minus the start value for the time period, essentially, the consumption or delta in my terms. For example, on the point details page in the point statistics card, it would be great to have one more value, the delta/consumption. But this is minor to the original issue.

                        Software Developer for GLAS Energy Technology, Ireland

                        1 Reply Last reply Reply Quote 0
                        • phildunlapP
                          phildunlap
                          last edited by

                          The last value is the the value at the period end time, since that is exclusive.

                          I think what will probably happen is that the delta will be computed with an inclusive period end time, while all the other statistics will remain computed with an exclusive period end time, but I haven't collected that consensus yet.

                          cbyrneC 1 Reply Last reply Reply Quote 0
                          • cbyrneC
                            cbyrne @phildunlap
                            last edited by

                            @phildunlap Cool cool cool, sounds like a nice solution. Thanks for keeping us in the loop!

                            Software Developer for GLAS Energy Technology, Ireland

                            1 Reply Last reply Reply Quote 0
                            • phildunlapP
                              phildunlap
                              last edited by

                              We had a discussion and this is the git issue: https://github.com/infiniteautomation/ma-core-public/issues/1480

                              We decided that it was a better solution to include the value prior to the period start time for computing the delta, since the same at the period start would be the instant of change, not the period where the prior value was held.

                              1 Reply Last reply Reply Quote 0