    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
    Radix IoT Website Mango Documentation Radix IoT LinkedIn
    MODBUS JAVA agent for data acquisition
    Scheduled Pinned Locked Moved Modbus4J general discussion
    4 Posts 3 Posters 7.8k Views 3 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • V Offline
      vijay chelliah
      I want to develop a JAVA code using MODBUS4J which should discover and read data from modbus controllers present in its network.
      Is there a feature like autodiscovery in modbus like that of bacnet?
      I have a doubt if my code should be a master or slave?
      if master can a network have multiple masters? for network might have a plc or a master modbus controller.
      if a slave can a slave communicate with a master to get all data?
      1 Reply Last reply Reply Quote 0
      • CraigWebC Offline
        CraigWeb
        These seem to be Modbus protocol-specific questions.
        Modbus does not have an auto-discovery like BACnet. You can make your own by polling each slave and see if there is any response.
        Modbus can only have one master on a network.
        Slaves cannot initiate a message they can only respond to a master.
        1 Reply Last reply Reply Quote 2
        • phildunlapP Offline
          phildunlap
          Hi vijay, welcome to the forum!
          As Craig said, the slave cannot initiate the communication. But, if the request is encoded in the registers (ProcessImage in Modbus4J speak), and the response is written back from the master, one could say the slave has some control of the communication at the application layer.
          @craigweb said in MODBUS JAVA agent for data acquisition:
          This only applies to serial communication lines. If it's Modbus IP there is no restriction and devices often support concurrent connections. Even on a serial line it is possible to have more than one device acting as a master, but there is no token passing like BACnet to avoid collisions on the wire, so generally there's only one device acting as a master on a serial line.
          V 1 Reply Last reply Reply Quote 1
          • V Offline
            vijay chelliah @phildunlap
            @phildunlap thanks a lot.
            Hello! It looks like you're interested in this conversation, but you don't have an account yet.
            Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.