    Event Handler Setting Meta Point Failing
    24 Posts 3 Posters 22.6k Views 3 Watching
      mihairosu
      Mango Enterprise Core 3.3.4
      We are trying to set a meta point based on an Event Trigger.
      if temperature is greater than 150 on point X, set point Y to 1
      if temperature is less than 120 on point X, set point Y to 2
      On return to normal of point X, set point Y to 0
      Here's the point event detector:
      Here's the meta point we are trying to change:
      Here's the event handler:
      To test the event, I changed the limit numbers to trigger the event:
      Here's email proof that the alarm triggered:
      The meta point was not changed:
        Hi Mihai,
        Hmm. You would have gotten an event if the set point handler had run and had an issue.
        As an aside, your event detector isn't going to do what you want. A reset limit means that the event stays active until the value gets on the appropriate side of the reset limit. So, you detector means "Raise the alarm if the value exceeds 190 for two seconds and leave it active until the value falls below 120." So we've got some issues. For one, 190 != 150. Secondly, the reset limit is not the same as a low limit detector to handle the logic of setting Y to 2.
        From the images, I would think the high limit being 190 is why the image of the watchlist values doesn't have the target point getting the value 2.
          rshah
          Hi @phildunlap ,
          I can chime in a little as Mihai is gone for the day.
          We actually do want it to reset, what we were thinking we'd do for low limit is just setup another event detector, so we'd have:
          Event Detector 1: If boiler temperature is greater than 160, set point Y to 2, when boiler temperature returns to less than 160, set point Y to 0 (I know the screenshot does not reflect this)
          Event Detector 2: If boiler temp is less than 120, set point Y to 1, when boiler temp returns to greater than 120, set point Y to 0. (I know the screenshot does not reflect this)
          I hope that is more clear. The screenshots were just some random numbers we had thrown in. It doesn't work even if there are more accurate numbers
          As far as the 190 != 150, we actually had it set to 150 initially, and then increased it (to cancel the event) prior to taking the screenshot -- so it was at one point 150, which tripped the email, but it did not set the point. The numbers are just for testing purposes, we wanted some numbers that would for sure trip (150) and some that would never trip (190)
          Thanks!
            mihairosu
            Hi Phil,
            As Ronak said, the screenshots are a bit deceptive. What we did to test the event is to reduce the event detector threshold to 130, then raise it again.
              There are two issues that were handled recently that come to mind. If you go to the /internal/queueStats.shtm page do you see a large number of medium priority items queuing up, perhaps never decreasing?
              That you say it tripped the email but didn't set the point is interesting. I would have expected you to get a log message but this issue could be related: https://github.com/infiniteautomation/ma-core-public/issues/1235
              Both of those should go away in 3.4, which is beta released currently (pick your release channel in the system settings) and will probably be fully released next week.
              Does the behavior persist a restart? I am fairly confident in the event handler being able to set a meta point to a static value.
                rshah
                Hey Phil,
                Here's some info:
                Here is the accurate screenshot of our event handler:
                Here is the watchlist showing the event is active, but the meta point isn't getting set:
                Here is the /internal/queueStats.shtm page
                Is it possible we did not configure the metapoint correctly when we created it?
                We weren't sure if multistate was the right option, or what we should put in 'script'
                Here are the metapoint settings:
                  rshah
                  Update:
                  I tried 'multistate' instead of numeric, got this error:
                  Here are the event handler settings:
                    The second image you provided, of the /internal/queueStats.shtm page, makes me certain it is the first issue I referred to. If you update to 3.4 I would expect that issue to go away. If you restart I would expect it to be temporarily relieved.
                      rshah
                      Sounds good -- we will wait for 3.4 to be officially released and then upgrade and report back.
                      Thank you again for all of your help!
                        rshah
                        Hi @phildunlap ,
                        Still no luck. We upgraded to 3.4 today and now we're getting this error when trying to create an event handler to set a point:
                        For reference, here is the event handler we are trying to create:
                          Post the error in its entirety from your Mango/logs/ma.log file.
                            rshah
                            @phildunlap said in Event Handler Setting Meta Point Failing:
                            ERROR 2018-05-02T09:55:50,957 (com.serotonin.m2m2.web.dwr.util.ExceptionDetectionFilter.doFilter:38) - DWR invocation exception
                            org.springframework.jdbc.BadSqlGrammarException: PreparedStatementCallback; bad SQL grammar [INSERT INTO eventHandlersMapping (eventHandlerId, eventTypeName, eventTypeRef1, eventTypeRef2) values (?, ?, ?, ?) ON DUPLICATE KEY IGNORE]; nested exception is com.mysql.jdbc.exceptions.jdbc4.MySQLSyntaxErrorException: You have an error in your SQL syntax; check the manual that corresponds to your MySQL server version for the right syntax to use near 'IGNORE' at line 1
                            	at org.springframework.jdbc.support.SQLErrorCodeSQLExceptionTranslator.doTranslate(SQLErrorCodeSQLExceptionTranslator.java:231) ~[spring-jdbc-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at org.springframework.jdbc.support.AbstractFallbackSQLExceptionTranslator.translate(AbstractFallbackSQLExceptionTranslator.java:73) ~[spring-jdbc-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at org.springframework.jdbc.core.JdbcTemplate.execute(JdbcTemplate.java:655) ~[spring-jdbc-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at org.springframework.jdbc.core.JdbcTemplate.update(JdbcTemplate.java:876) ~[spring-jdbc-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at org.springframework.jdbc.core.JdbcTemplate.update(JdbcTemplate.java:937) ~[spring-jdbc-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at com.serotonin.db.spring.ExtendedJdbcTemplate.update(ExtendedJdbcTemplate.java:83) ~[mango-3.4.0.jar:?]
                            	at com.serotonin.m2m2.db.dao.EventHandlerDao.addEventHandlerMappingIfMissing(EventHandlerDao.java:241) ~[mango-3.4.0.jar:?]
                            	at com.serotonin.m2m2.db.dao.EventHandlerDao.saveRelationalData(EventHandlerDao.java:210) ~[mango-3.4.0.jar:?]
                            	at com.serotonin.m2m2.db.dao.EventHandlerDao.saveRelationalData(EventHandlerDao.java:37) ~[mango-3.4.0.jar:?]
                            	at com.serotonin.m2m2.db.dao.AbstractBasicDao.lambda$saveFull$0(AbstractBasicDao.java:552) ~[mango-3.4.0.jar:?]
                            	at org.springframework.transaction.support.TransactionTemplate.execute(TransactionTemplate.java:133) ~[spring-tx-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at com.serotonin.m2m2.db.dao.AbstractBasicDao.saveFull(AbstractBasicDao.java:548) ~[mango-3.4.0.jar:?]
                            	at com.serotonin.m2m2.db.dao.AbstractBasicDao.saveFull(AbstractBasicDao.java:539) ~[mango-3.4.0.jar:?]
                            	at com.serotonin.m2m2.web.dwr.EventHandlersDwr.save(EventHandlersDwr.java:333) ~[mango-3.4.0.jar:?]
                            	at com.serotonin.m2m2.web.dwr.EventHandlersDwr.saveSetPointEventHandler(EventHandlersDwr.java:272) ~[mango-3.4.0.jar:?]
                            	at sun.reflect.NativeMethodAccessorImpl.invoke0(Native Method) ~[?:1.8.0_162]
                            	at sun.reflect.NativeMethodAccessorImpl.invoke(NativeMethodAccessorImpl.java:62) ~[?:1.8.0_162]
                            	at sun.reflect.DelegatingMethodAccessorImpl.invoke(DelegatingMethodAccessorImpl.java:43) ~[?:1.8.0_162]
                            	at java.lang.reflect.Method.invoke(Method.java:498) ~[?:1.8.0_162]
                            	at org.directwebremoting.impl.ExecuteAjaxFilter.doFilter(ExecuteAjaxFilter.java:34) ~[dwr-2.0.11.jar:?]
                            	at org.directwebremoting.impl.DefaultRemoter$1.doFilter(DefaultRemoter.java:428) ~[dwr-2.0.11.jar:?]
                            	at com.serotonin.m2m2.web.dwr.util.TranslationsFilter.doFilter(TranslationsFilter.java:37) ~[mango-3.4.0.jar:?]
                            	at com.serotonin.m2m2.web.dwr.util.ExceptionDetectionFilter.doFilter(ExceptionDetectionFilter.java:26) [mango-3.4.0.jar:?]
                            	at org.directwebremoting.impl.DefaultRemoter$1.doFilter(DefaultRemoter.java:428) [dwr-2.0.11.jar:?]
                            	at com.serotonin.m2m2.web.dwr.util.DwrPermissionFilter.doFilter(DwrPermissionFilter.java:46) [mango-3.4.0.jar:?]
                            	at org.directwebremoting.impl.DefaultRemoter.execute(DefaultRemoter.java:431) [dwr-2.0.11.jar:?]
                            	at org.directwebremoting.impl.DefaultRemoter.execute(DefaultRemoter.java:283) [dwr-2.0.11.jar:?]
                            	at org.directwebremoting.servlet.PlainCallHandler.handle(PlainCallHandler.java:52) [dwr-2.0.11.jar:?]
                            	at org.directwebremoting.servlet.UrlProcessor.handle(UrlProcessor.java:101) [dwr-2.0.11.jar:?]
                            	at org.directwebremoting.servlet.DwrServlet.doPost(DwrServlet.java:146) [dwr-2.0.11.jar:?]
                            	at javax.servlet.http.HttpServlet.service(HttpServlet.java:707) [javax.servlet-api-3.1.0.jar:3.1.0]
                            	at javax.servlet.http.HttpServlet.service(HttpServlet.java:790) [javax.servlet-api-3.1.0.jar:3.1.0]
                            	at org.eclipse.jetty.servlet.ServletHolder.handle(ServletHolder.java:848) [jetty-servlet-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.servlet.ServletHandler$CachedChain.doFilter(ServletHandler.java:1772) [jetty-servlet-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.springframework.web.filter.ShallowEtagHeaderFilter.doFilterInternal(ShallowEtagHeaderFilter.java:110) [spring-web-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at com.serotonin.m2m2.web.filter.MangoShallowEtagHeaderFilter.doFilterInternal(MangoShallowEtagHeaderFilter.java:90) [mango-3.4.0.jar:?]
                            	at org.springframework.web.filter.OncePerRequestFilter.doFilter(OncePerRequestFilter.java:107) [spring-web-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at org.eclipse.jetty.servlet.ServletHandler$CachedChain.doFilter(ServletHandler.java:1759) [jetty-servlet-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.springframework.security.web.FilterChainProxy$VirtualFilterChain.doFilter(FilterChainProxy.java:317) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.access.intercept.FilterSecurityInterceptor.invoke(FilterSecurityInterceptor.java:127) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.access.intercept.FilterSecurityInterceptor.doFilter(FilterSecurityInterceptor.java:91) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.FilterChainProxy$VirtualFilterChain.doFilter(FilterChainProxy.java:331) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at com.serotonin.m2m2.web.mvc.spring.security.PermissionExceptionFilter.doFilter(PermissionExceptionFilter.java:32) [mango-3.4.0.jar:?]
                            	at org.springframework.security.web.access.ExceptionTranslationFilter.doFilter(ExceptionTranslationFilter.java:114) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.session.SessionManagementFilter.doFilter(SessionManagementFilter.java:137) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.authentication.AnonymousAuthenticationFilter.doFilter(AnonymousAuthenticationFilter.java:111) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.servletapi.SecurityContextHolderAwareRequestFilter.doFilter(SecurityContextHolderAwareRequestFilter.java:170) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.savedrequest.RequestCacheAwareFilter.doFilter(RequestCacheAwareFilter.java:63) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.session.ConcurrentSessionFilter.doFilter(ConcurrentSessionFilter.java:155) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.authentication.AbstractAuthenticationProcessingFilter.doFilter(AbstractAuthenticationProcessingFilter.java:200) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.authentication.logout.LogoutFilter.doFilter(LogoutFilter.java:116) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.csrf.CsrfFilter.doFilterInternal(CsrfFilter.java:100) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.header.HeaderWriterFilter.doFilterInternal(HeaderWriterFilter.java:66) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.context.SecurityContextPersistenceFilter.doFilter(SecurityContextPersistenceFilter.java:105) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.context.request.async.WebAsyncManagerIntegrationFilter.doFilterInternal(WebAsyncManagerIntegrationFilter.java:56) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.FilterChainProxy.doFilterInternal(FilterChainProxy.java:214) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.security.web.FilterChainProxy.doFilter(FilterChainProxy.java:177) [spring-security-web-4.2.5.RELEASE.jar:4.2.5.RELEASE]
                            	at org.springframework.web.filter.DelegatingFilterProxy.invokeDelegate(DelegatingFilterProxy.java:347) [spring-web-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at org.springframework.web.filter.DelegatingFilterProxy.doFilter(DelegatingFilterProxy.java:263) [spring-web-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at org.eclipse.jetty.servlet.ServletHandler$CachedChain.doFilter(ServletHandler.java:1751) [jetty-servlet-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.servlet.ServletHandler.doHandle(ServletHandler.java:582) [jetty-servlet-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.handler.ScopedHandler.handle(ScopedHandler.java:143) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.security.SecurityHandler.handle(SecurityHandler.java:548) [jetty-security-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.session.SessionHandler.doHandle(SessionHandler.java:226) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.handler.ContextHandler.doHandle(ContextHandler.java:1180) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.servlet.ServletHandler.doScope(ServletHandler.java:512) [jetty-servlet-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.session.SessionHandler.doScope(SessionHandler.java:185) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.handler.ContextHandler.doScope(ContextHandler.java:1112) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.handler.ScopedHandler.handle(ScopedHandler.java:141) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.handler.ContextHandlerCollection.handle(ContextHandlerCollection.java:213) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.handler.gzip.GzipHandler.handle(GzipHandler.java:493) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.handler.HandlerWrapper.handle(HandlerWrapper.java:134) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.Server.handle(Server.java:539) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.HttpChannel.handle(HttpChannel.java:333) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.server.HttpConnection.onFillable(HttpConnection.java:251) [jetty-server-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.io.AbstractConnection$ReadCallback.succeeded(AbstractConnection.java:283) [jetty-io-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.io.FillInterest.fillable(FillInterest.java:108) [jetty-io-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.io.SelectChannelEndPoint$2.run(SelectChannelEndPoint.java:93) [jetty-io-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.util.thread.strategy.ExecuteProduceConsume.executeProduceConsume(ExecuteProduceConsume.java:303) [jetty-util-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.util.thread.strategy.ExecuteProduceConsume.produceConsume(ExecuteProduceConsume.java:148) [jetty-util-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.util.thread.strategy.ExecuteProduceConsume.run(ExecuteProduceConsume.java:136) [jetty-util-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.util.thread.QueuedThreadPool.runJob(QueuedThreadPool.java:671) [jetty-util-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at org.eclipse.jetty.util.thread.QueuedThreadPool$2.run(QueuedThreadPool.java:589) [jetty-util-9.3.23.v20180228.jar:9.3.23.v20180228]
                            	at java.lang.Thread.run(Thread.java:748) [?:1.8.0_162]
                            Caused by: com.mysql.jdbc.exceptions.jdbc4.MySQLSyntaxErrorException: You have an error in your SQL syntax; check the manual that corresponds to your MySQL server version for the right syntax to use near 'IGNORE' at line 1
                            	at sun.reflect.NativeConstructorAccessorImpl.newInstance0(Native Method) ~[?:1.8.0_162]
                            	at sun.reflect.NativeConstructorAccessorImpl.newInstance(NativeConstructorAccessorImpl.java:62) ~[?:1.8.0_162]
                            	at sun.reflect.DelegatingConstructorAccessorImpl.newInstance(DelegatingConstructorAccessorImpl.java:45) ~[?:1.8.0_162]
                            	at java.lang.reflect.Constructor.newInstance(Constructor.java:423) ~[?:1.8.0_162]
                            	at com.mysql.jdbc.Util.handleNewInstance(Util.java:411) ~[mysql-connector-java-5.1.26.jar:?]
                            	at com.mysql.jdbc.Util.getInstance(Util.java:386) ~[mysql-connector-java-5.1.26.jar:?]
                            	at com.mysql.jdbc.SQLError.createSQLException(SQLError.java:1054) ~[mysql-connector-java-5.1.26.jar:?]
                            	at com.mysql.jdbc.MysqlIO.checkErrorPacket(MysqlIO.java:4190) ~[mysql-connector-java-5.1.26.jar:?]
                            	at com.mysql.jdbc.MysqlIO.checkErrorPacket(MysqlIO.java:4122) ~[mysql-connector-java-5.1.26.jar:?]
                            	at com.mysql.jdbc.MysqlIO.sendCommand(MysqlIO.java:2570) ~[mysql-connector-java-5.1.26.jar:?]
                            	at com.mysql.jdbc.MysqlIO.sqlQueryDirect(MysqlIO.java:2731) ~[mysql-connector-java-5.1.26.jar:?]
                            	at com.mysql.jdbc.ConnectionImpl.execSQL(ConnectionImpl.java:2818) ~[mysql-connector-java-5.1.26.jar:?]
                            	at com.mysql.jdbc.PreparedStatement.executeInternal(PreparedStatement.java:2157) ~[mysql-connector-java-5.1.26.jar:?]
                            	at com.mysql.jdbc.PreparedStatement.executeUpdate(PreparedStatement.java:2460) ~[mysql-connector-java-5.1.26.jar:?]
                            	at com.mysql.jdbc.PreparedStatement.executeUpdate(PreparedStatement.java:2377) ~[mysql-connector-java-5.1.26.jar:?]
                            	at com.mysql.jdbc.PreparedStatement.executeUpdate(PreparedStatement.java:2361) ~[mysql-connector-java-5.1.26.jar:?]
                            	at org.apache.commons.dbcp.DelegatingPreparedStatement.executeUpdate(DelegatingPreparedStatement.java:105) ~[commons-dbcp-1.4.jar:1.4]
                            	at org.springframework.jdbc.core.JdbcTemplate$2.doInPreparedStatement(JdbcTemplate.java:883) ~[spring-jdbc-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at org.springframework.jdbc.core.JdbcTemplate$2.doInPreparedStatement(JdbcTemplate.java:876) ~[spring-jdbc-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	at org.springframework.jdbc.core.JdbcTemplate.execute(JdbcTemplate.java:639) ~[spring-jdbc-4.3.16.RELEASE.jar:4.3.16.RELEASE]
                            	... 99 more
                              Whoa, that's not good. I have committed a fix and we'll be releasing core 3.4.1 to address this. Thanks for bringing it to our attention.
                                rshah
                                Glad to hear it was discovered early :)
                                Any workarounds until 3.4.1?
                                  We'll be releasing 3.4.1 today.
                                    rshah @phildunlap
                                    @phildunlap
                                    Thanks!
                                    Thanks for the quick fix as well.
                                      3.4.1 is released.
                                        rshah
                                        Thanks @phildunlap
                                        Upgrade went smooth and what we were trying to do kind of worked, but still not working as expected.
                                        I am now able to create an event handler to set a point to a static value if an event is triggered -- and that works just fine. However, the point we are setting almost instantly goes back to 0, despite the event still being active.
                                        Screenshots:
                                        Event Detector:
                                        Proof that the event is still active:
                                        Event Handler:
                                        History of the point we are trying to set, note it goes active, and then 8 seconds later inactive for some reason (even though we never came close to hiting the reset limit of <60)
                                          We can see in the annotation that it wasn't the inactive event doing it. So, what could trigger that meta point to recompute itself? Is 0 the value it would get if it executed?
                                            rshah
                                            Sorry -- unsure what you mean by if "...it was executed"
                                            Nothing else changes that point except the event handler.
                                            Here's a screeenshot of the metapoint details: