      rshah
      Of course it works fine now.
      Magic.
      I'm curious though if anyone thinks it would be better to use
      'now' | maMoment:'subtract':12:'hours'
      instead of:
      <ma-now update-interval="1 minutes" output="to"></ma-now>
      <ma-calc input="to | maMoment:'subtract':12:'hours'" output="from"></ma-calc>
      Not sure if that would work for us or not.
        The second form is probably the preferred form. In the preceding form, it will be updated every digest cycle regardless of what triggered that digest update (the default timer, some other modeled object, etc) while the latter will only update on the update interval, even if other things change in the digest.
          rshah
          Hi @phildunlap
          Thanks!
          Is ma-point-values the best way to get all this data to show on a chart? We are using ma-point-values to retrieve 12 hours of values for 12 or so points, and it really feels like it is slowing down the entire page significantly
            Jared Wiltshire @rshah
            @rshah said in Retrieve last 12 hours of data:
            How often are you retrieving point values? If you have a timer (ma-now) and are updating the query for point values too regularly you will definitely cause the system to bog down.
              rshah
              @jared-wiltshire said in Retrieve last 12 hours of data:
              Jared, we are retrieving once per minute.
              Am I correct in this assumption:
              Calling ma-point-values fetches all 12 hours (for example) of data every single time you call it?
              Or, does it only fetch the latest data?
              If the former, is there a better way of doing this? I can probably create an array and call ma-get-point to get the latest point and push to the array rather than getting 12 hours worth of data every minute for 8+ points.
              Thanks!
                Correct. Although saying "calling" is a little confusing, its not a function, its an Angular component. It will fetch all 12 hours when its attributes change (e.g. when the time period changes).
                Are you talking about point values rather than points?
                This is essentially what the <ma-point-values> component does if you set the latest="x" attribute.
                Are you sure that you don't have some other error in your console (e.g. infinite digest error) which could be causing the page to bog down?
                  rshah
                  Hi, yes no error.
                  How would we use latest if we wanted 12 hours worth of data (point values) for ma-serial-chart?
                  I thought about using latest initially but as there is only a way to limit the scope of latest via NUMBER of points rather than time-duration, I moved away from it.
                  My end goal is to populate ma-serial-chart with 12 hours of point values for multiple datapoints. I can send you the code I am using to do that now if it would help.
                    You would have to know the sample/poll period of the data points.
                    What rollup are you using? Have you opened your chrome developer tools and checked the network requests that are going out? Check they aren't occurring more frequently than you intended and that they aren't taking too long to complete.
                    You can post up your code if you would like, sure.
                      Here's how I would accomplish what you are doing:
                      <ma-watch-list-get ng-model="designer.watchList" parameters="designer.parameters" on-points-change="designer.points = $points" id="d01a1ce8-d4d7-43b3-831c-9c619fb4bace" watch-list-xid="WL_ac76beaa-10f4-40f0-b714-d0fda1c1e801"></ma-watch-list-get>
                      <div class="ma-designer-root" id="4a3435f4-e428-4ee2-8ba8-1cf4511aa999" style="width: 1366px; height: 768px; position: relative;">
                          <ma-point-values id="5a8730ae-18bc-443c-8bad-e9ef83ccf104" points="designer.points" rollup-interval="15 minutes" rollup="FIRST" to="designer.time" from="designer.time | maMoment:'subtract':12:'hours'" style="position: absolute; left: 27px; top: 0px;" values="designer.values"></ma-point-values>
                          <ma-serial-chart id="2796c91b-75b7-4759-9228-60d2e840b90f" style="position: absolute; width: 854px; height: 541px; left: 29px; top: 93px;" points="designer.points" values="designer.values" legend="true"></ma-serial-chart>
                          <ma-now id="2269ccdd-6d99-4732-81a4-3d607e73dbb8" style="position: absolute; left: 210px; top: 0px;" update-interval="1 minute" output="designer.time"></ma-now>
                        rshah
                        Here is what we are doing now -- I am not very familiar with Angular, my experience is largely with React -- can you advise if this is a bad way to do this?
                        <!DOCTYPE html>
                        <html lang="en">
                            <head>
                                <meta charset="utf-8">
                                <title>Boiler 2 Screen</title>
                                <meta name="viewport" content="width=device-width, height=device-height, initial-scale=1">
                                <link rel="stylesheet" href="/modules/mangoUI/web/vendor/angular/angular-csp.css"></link>
                                <link rel="stylesheet" href="/modules/mangoUI/web/vendor/angular-material/angular-material.css">
                                <link rel="stylesheet" href="/modules/mangoUI/web/vendor/material-design-icons/iconfont/material-icons.css">
                                <link rel="stylesheet" href="/modules/mangoUI/web/vendor/md-pickers/mdPickers.css">
                            </head>
                            <body layout="column">
                                <!-- We only want to obtain last 12 hours of data, so use Angular Moment Library to do figure out what last 12 hours are-->
                                <!-- Obtain 12 hours of point values based on point XID, average them per minute  store them in an array (object) (param = values) -->
                                <!-- Boiler DHW information -->
                                <!-- Member 1 Information (DHW Mode only) -->
                                <ma-point-values
                                    point-xid="member1DhwTankTemp"
                                    rendered="true"
                                    values="m1TankValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                    rollup-interval="1 minutes">
                                </ma-point-values>
                                <ma-point-values
                                    point-xid="DP_member1FiringRateDHW"
                                    rendered="true"
                                    values="m1FireDHWValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <ma-point-values
                                    point-xid="member1OutletTemp"
                                    rendered="true"
                                    values="m1OutletTempValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <!-- Member 3 Information (DHW Mode only) -->
                                <ma-point-values
                                    point-xid="member3DhwTankTemp"
                                    rendered="true"
                                    values="m3TankValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <ma-point-values
                                    point-xid="DP_member3FiringRateDHW"
                                    rendered="true"
                                    values="m3FireDHWValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <ma-point-values
                                    point-xid="member3OutletTemp"
                                    rendered="true"
                                    values="m3OutletTempValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <!-- DHW Flow Data -->
                                <ma-point-values
                                    point-xid="DHWSupplyRate"
                                    rendered="true"
                                    values="dhwSupplyRateValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <ma-point-values
                                    point-xid="DHW11ReturnRate"
                                    rendered="true"
                                    values="dhw11SupplyRateValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <ma-point-values
                                    point-xid="DP_DhwConsumedRate"
                                    rendered="true"
                                    values="dhwConsumedRateValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <ma-point-values
                                    point-xid="IoM322DHWBsmntReturnTemp"
                                    rendered="true"
                                    values="returnBasementTemperatureValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <ma-point-values
                                    point-xid="IoM3DHWSupTemp"
                                    rendered="true"
                                    values="DHW22SupplyTemperatureValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <ma-point-values
                                    point-xid="IoM322DHW11ReturnTemp"
                                    rendered="true"
                                    values="return11TemperatureValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <ma-point-values
                                    point-xid="DHWBsmntReturnRate"
                                    rendered="true"
                                    values="basementReturnRateValues"
                                    from="from"
                                    to="to"
                                    rollup="AVERAGE"
                                </ma-point-values>
                                <!-- Displays only if the app is still loading -->
                                <div ng-if="appLoading">
                                    <span>App is loading..</span>
                                <!-- Actual content of page once loaded -->
                                <div ng-cloak layout="column" flex>
                                    <h3 class="centerText">DHW Tanks and Boilers</h3>
                                    <div layout="row">
                                        <md-card flex="75">
                                            <md-card-content layout="column">
                                                <ma-serial-chart
                                                style="height: 490px; width: 100%"
                                                series-1-values="m1FireDHWValues"
                                                series-1-title="Member 1 DHW Firing Rate"
                                                series-1-color="red"
                                                series-1-axis="left"
                                                series-1-type="smoothedLine"
                                                series-2-values="m3FireDHWValues"
                                                series-2-title="Member 3 DHW Firing Rate"
                                                series-2-color="green"
                                                series-2-axis="left"
                                                series-2-type="smoothedLine"
                                                series-3-values="m1TankValues"
                                                series-3-title="Member 1 Tank Temp"
                                                series-3-color="blue"
                                                series-3-axis="right"
                                                series-3-type="smoothedLine"
                                                series-4-values="m3TankValues"
                                                series-4-title="Member 3 Tank Temp"
                                                series-4-color="yellow"
                                                series-4-axis="right"
                                                series-4-type="smoothedLine"
                                                legend="true"
                                                options="{
                                                    valueAxes:[
                                                            axisColor:'white',
                                                            color:'white',
                                                            title: 'Firing Rate (%)',
                                                            titleColor: 'white',
                                                            fontSize:26,
                                                            titleFontSize:26,
                                                            minimum:0,
                                                            maximum:100
                                                            axisColor:'white',
                                                            color:'white',
                                                            title: 'Temperature (ºF)',
                                                            fontSize:26,
                                                            titleFontSize:26,
                                                            minimum:0,
                                                            maximum:180
                                                </ma-serial-chart>
                                            </md-card-content>
                                        </md-card>
                                        <md-card flex="25">
                                                <div layout="row">
                                                    <md-card flex="50">
                                                        <md-card-title>
                                                            <md-card-title-text>
        Member 1 Firing Rate (DHW)
                                                            </md-card-title-text>
                                                        </md-card-title>
                                                            <h4 id="testing">{{m1FireDHWValues[m1FireDHWValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                                    <md-card flex="50">
                                                        <md-card-title>
        Member 3 Firing Rate (DHW)
                                                        </md-card-title>
                                                            <h4 id="testing">{{m3FireDHWValues[m3FireDHWValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                                <div layout="row">
                                                    <md-card flex="50">
                                                        <md-card-title>
        Member 1 DHW Outlet Temp
                                                        </md-card-title>
                                                            <h4 id="testing">{{m1OutletTempValues[m1OutletTempValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                                    <md-card flex="50">
                                                        <md-card-title>
        Member 3 DHW Outlet Temp
                                                        </md-card-title>
                                                            <h4 id="testing">{{m3OutletTempValues[m3OutletTempValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                                <div layout="row">
                                                    <md-card flex="50">
                                                        <md-card-title>
        Member 1 DHW Tank Temperature
                                                        </md-card-title>
                                                            <h4 id="testing">{{m1TankValues[m1TankValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                                    <md-card flex="50">
                                                        <md-card-title>
        Member 3 DHW Tank Temperature
                                                        </md-card-title>
                                                            <h4 id="testing">{{m3TankValues[m3TankValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                            </md-card-content>
                                        </md-card>
                                    <h3 class="centerText">DHW Flow and Temperature</h3>
                                    <div layout="row">
                                        <md-card flex="75">
                                                <ma-serial-chart
                                                series-1-values="dhwSupplyRateValues"
                                                series-1-title="DHW Supply Rate"
                                                series-2-values="dhwConsumedRateValues"
                                                series-2-title="DHW Consumed Rate"
                                                series-3-values="DHW22SupplyTemperatureValues"
                                                series-3-title="DHW Supply Temperature"
                                                legend="true"
                                                options="{
                                                    valueAxes:[
                                                            axisColor:'black',
                                                            color:'black',
                                                            title: 'Flow Rate (Gal / Min)',
                                                            titleColor: 'black',
                                                            fontSize:26,
                                                            titleFontSize:26,
                                                            minimum:0,
                                                            maximum:100
                                                            axisColor:'black',
                                                            color:'black',
                                                            fontSize:26,
                                                            titleFontSize:26,
                                                            minimum:0,
                                                            maximum:180
                                                </ma-serial-chart>
                                            </md-card-content>
                                        </md-card>
                                        <md-card flex="25">
                                                <div layout="row">
                                                    <md-card flex="50">
                                                        <md-card-title>
        DHW Supply Flow Rate
                                                        </md-card-title>
                                                            <h4 id="testing">{{dhwSupplyRateValues[dhwSupplyRateValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                                    <md-card flex="50">
                                                        <md-card-title>
        22 DHW Supply Temperature
                                                        </md-card-title>
                                                            <h4 id="testing">{{DHW22SupplyTemperatureValues[DHW22SupplyTemperatureValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                                <div layout="row">
                                                    <md-card flex="50">
                                                        <md-card-title>
        11th Flr DHW Return Flow Rate
                                                        </md-card-title>
                                                            <h4 id="testing">{{dhw11SupplyRateValues[dhw11SupplyRateValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                                    <md-card flex="50">
                                                        <md-card-title>
        22 DHW Bsmt Return Temperature
                                                        </md-card-title>
                                                            <h4 id="testing">{{returnBasementTemperatureValues[returnBasementTemperatureValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                                <div layout="row">
                                                    <md-card flex="50">
                                                        <md-card-title>
        DHW Consumed Flow Rate
                                                        </md-card-title>
                                                            <h4 id="testing">{{dhwConsumedRateValues[dhwConsumedRateValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                                    <md-card flex="50">
                                                        <md-card-title>
        22 DHW 11th Flr Return Temp
                                                        </md-card-title>
                                                            <h4 id="testing">{{return11TemperatureValues[return11TemperatureValues.length - 1].rendered}}</h4>
                                                        </md-card-content>
                                                    </md-card>
                                            </md-card-content>
                                        </md-card>
                                <script src="/modules/mangoUI/web/vendor/requirejs/require.js"></script>
                                <script src="/modules/mangoUI/web/loaderConfig.js"></script>
                                <script>require(['ngMango/bootstrap']);</script>
                            </body>
                        </html>
                          @rshah two things
                          a) I would strongly suggest moving your page into a custom / dashboard designer page inside the UI module. I can tell you that the above page will break upon installation of Mango 3.4
                          To make the page full screen / no menu and toolbar, see here - https://forum.infiniteautomation.com/topic/3297/deploying-custom-page/3
                          b) Don't get every point and its values individually. Use a watch list as I posted above. You can use multiple watch lists if you want multiple charts. This also lets you dynamically add/remove points from the watchlist and you wont have to change your page markup.
                            rshah
                            Thanks a lot!
                            We will do that.